Help us improve your experience.

Let us know what you think.

Do you have time for a two-minute survey?

 
 

PTX10004 Power System

PTX10004 routers support AC, DC, high-voltage alternating current (HVAC), and high-voltage direct current (HVDC) by offering the following power supplies:

  • JNP10K-PWR-AC3

  • JNP10K-PWR-AC2

  • JNP10K-PWR-DC2

You can install up to three power supplies in the slots labeled PSU0 through PSU2 (top to bottom) located in the rear of the chassis.

Note:

The JNP10K-PWR-AC2 and JNP10K-PWR-AC3 can share power proportionally in a mixed configuration, only when you are upgrading to JNP10K-PWR-AC3.

JNP10K-PWR-AC3 Power Supply

The JNP10K-PWR-AC3 power supply is a high-capacity model that is designed to support AC systems in a 15-A and 20-A mode; see Figure 1.

Figure 1: JNP10K-PWR-AC3 Power Supply JNP10K-PWR-AC3 Power Supply

Input—The power supply takes four single-phase AC (180-264 VAC) inputs (A0, A1, B0, and B1) at either 20 A or 15 A and provides a DC output of 12.3V. The input receptacle on the AC power supply unit (PSU) is IEC 320-C22. The mating connector on the power cord is IEC 320-C21.

Output—The power supply provides DC output of 12.3V at:

  • 7800 W (20-A input) with three or four active feeds, or
  • 6000 W (20-A input) with two active feeds (either A0 and A1 or B0 and B1), or
  • 3000 W (20-A input) with single active feed.
  • 7800 W (15-A input) with four active feeds, or

  • 7500 W (15-A input) with three active feeds, or

  • 5000 W (15-A input) with two active feeds, or

  • 2500 W (15-A input) with single active feed.

  • The operating input voltage range is 180 to 264 VAC for AC systems. The DC output is 12.3 VDC.

  • The number of power feeds and whether the power supplies provide high-output (20-A) or low-output (15-A) power are configured using a set of dual inline package (DIP) switches on the faceplate of the power supply. If one power supply in the chassis is set to low power, the power budget for the chassis is reduced to low power, regardless of their DIP switch settings or the output results in the CLI. This design safeguards against accidentally setting the power supply to 20 A in a facility that can provide only 15 A and tripping the facility circuit breaker. We recommend that you don’t mix DIP switch settings in your system. See Table 2 for information about the input and output voltages when you use the DIP switches.

  • The JNP10K-PWR-AC3 power supply has an ENABLE switch on the front panel to enable/disable the main 12.3 VDC output and +5.0 V_BIAS standby output as well. If the switch is in DISABLE position, the front-end PFC will be disabled to minimize power consumption. This switch has the highest priority over any other shutdown method.

  • The Power Factor Correction (PFC) is PF 0.98 kW minimum at full load. The maximum inrush current is 50 A for the active feed.

JNP10K-PWR-BLN3 or Active Blank

Juniper Networks offers an Active Blank Power Module (ABPM), JNP10K-PWR-BLN3. This helps in airflow and cooling in the chassis. You can have the following combination of ABPM, passive blank, and JNP10K-PWR-AC3 power supply units (PSU) in the router chassis:

  • Three PSUs

  • Two PSUs with one ABPM

  • One PSU with one ABPMs and one passive blank

  • One PSU with two ABPMs

  • Table 1: PSU, ABPM, Passive Blank Matrix

    JNP10K-PWR-AC3 PSU(s)

    ABPM (JNP10K-PWR-BLN3)

    Passive Blank

    3

    -

    -

    2

    1

    -

    1

    1

    1

    1

    2

    -

    Note:

    A minimum of one JNP10K-PWR-AC3 power supply unit (PSU) must be present in the router chassis.

The JNP10K-PWR-AC3 power supply has internal fans that contribute to chassis cooling. Three PSUs or two PSUs along with a ABPM must be present in a running chassis to have the adequate airflow. While the minimum power supplies are required to be present in the chassis, they all need not be necessarily connected to power source. If a power supply is installed in a slot but not connected to a power source, it draws power from the chassis to power the internal fans in the power supplies.

Warning:

Extreme burn danger—The JNP10K-PWR-AC3 can reach temperatures in the range of 158°F to 176°F (70°C to 80°C) under running conditions.

Warning:

The router is pluggable type A equipment installed in a restricted-access location. It has a separate protective earthing terminal on the chassis that must be connected to earth ground permanently to ground the chassis adequately and protect the operator from electrical hazards.

CAUTION:

Before you begin installing the router, ensure that a licensed electrician has attached an appropriate grounding lug to the grounding cable that you supply. Using a grounding cable with an incorrectly attached lug can damage the router.

CAUTION:

Use a 2-pole circuit breaker rated at 25 A in the building installation and the system, or as per local electrical code.

The JNP10K-PWR-AC3 Power Supplies have five dual position DIP switches (INP-A0, INP-A1, INP-B0, INP-B1, and DIP4) that are accessible from the front panel. DIP4 is the fifth DIP switch, which is used to indicate whether 20A or 15A input source is connected. See Figure 2 and Table 2 to know the layout of the DIP switches and the power output when the DIP switches are set in different combinations.

Figure 2: DIP Switches on NP10K-PWR-AC3 Power Supply DIP Switches on NP10K-PWR-AC3 Power Supply

1—LEDs corresponding to the DIP switches above it.

Table 2: DIP Switch Settings for JNP10K-PWR-AC3 Power Supply

INP-A0 (Switch 0)

INP-A1 (Switch 1)

INP-B0 (Switch 2)

INP-B1 (Switch 3)

Switch 4 (High Input 20 A/Low Input 15 A)

Output Power

15-A

Off

Off

Off

On

Off (15 A)

2500 W

Off

Off

On

Off

Off (15 A)

2500 W

Off

Off

On

On

Off (15 A)

5000 W

Off

On

Off

Off

Off (15 A)

2500 W

Off

On

Off

On

Off (15 A)

5000 W

Off

On

On

On

Off (15 A)

7500 W

Off

On

On

Off

Off (15 A)

5000 W

On

Off

Off

Off

Off (15 A)

2500 W

On

Off

Off

On

Off (15 A)

5000 W

On

Off

On

Off

Off (15 A)

5000 W

On

Off

On

On

Off (15 A)

7500 W

On

On

Off

Off

Off (15 A)

5000 W

On

On

Off

On

Off (15 A)

7500 W

On

On

On

Off

Off (15 A)

7500 W

On

On

On

On

Off (15 A)

7800 W

20-A

Off

Off

Off

On

On (20 A)

3000 W

Off

Off

On

Off

On (20 A)

3000 W

Off

Off

On

On

On (20 A)

6000 W

Off

On

Off

Off

On (20 A)

3000 W

Off

On

Off

On

On (20 A)

6000 W

Off

On

On

Off

On (20 A)

6000 W

Off

On

On

On

On (20 A)

7800 W

On

Off

Off

Off

On (20 A)

3000 W

On

Off

Off

On

On (20 A)

6000 W

On

Off

On

Off

On (20 A)

6000 W

On

Off

On

On

On (20 A)

7800 W

On

On

Off

Off

On (20 A)

6000 W

On

On

Off

On

On (20 A)

7800 W

On

On

On

Off

On (20 A)

7800 W

On

On

On

On

On (20 A)

7800 W

CAUTION:

It is important to connect the input feeds of the JNP10K-PWR-AC3 power supply to AC mains before powering-on the router.

JNP10K-PWR-AC3 Power Supply LEDs

The JNP10K-PWR-AC3 power supply has six LEDs on its faceplate: !, OK, A0, A1, B0, and B1. The numbered LEDs correspond to the four inputs (INP-A0, INP-A1, INP-B0, and INP-B1). Additionally, there are two more LEDs OK (Power OK) and !(Fault). These LEDs display information about the status of the power supply. See Figure 3.

Figure 3: LEDs on a JNP10K-PWR-AC3 Power Supply LEDs on a JNP10K-PWR-AC3 Power Supply

1—LEDs on the JNP10K-PWR-AC3 Power Supply denoting:

  • ! Fault

  • OK Power OK

  • A0 INP A0–Source input 1

  • A1 INP A1–Source input 2

  • B0 INP B0–Source input 3

  • B1 INP B1–Source input 4

Note:

Physical markings on the power supply are 1, 2, 3, and 4. These markings correspond to INP-A0, INP-A1, INP-B0, and INP-B1 in the show chassis power output (see Table 3).

Table 3: Physical Markings on AC3 Chassis Versus show chassis power Command

Physical Marking on JNP10K-PWR-AC3

show chassis power Command

INP A0

INP-A0

INP A1

INP-A1

INP B0

INP-B0

INP B1

INP-B1

Table 4 describes the LEDs on a JNP10K-PWR-AC3 power supply, color on the LED, state, and its meaning.

Table 4: JNP10K-PWR-AC3 LEDs on a PTX10004

LED

Color

State

Description

1 or (AO in CLI output)

Yellow

Solid

One of the following:

  • The power supply is switched off.

  • There is input voltage.

  • The input voltage is present, but a fault is detected.

Green

Solid

The power supply is functioning properly.

2 or (A1 in CLI output)

Yellow

Solid

One of the following:

  • The power supply is switched off.

  • There is input voltage.

  • The input voltage is present, but a fault is detected.

Green

Solid

The power supply is functioning properly.

3 or (B0 in CLI output)

Yellow

Solid

One of the following:

  • The power supply is switched off.

  • There is input voltage.

  • The input voltage is present, but a fault is detected.

Green

Solid

The power supply is functioning properly.

4 or (B1 in CLI output)

Yellow

Solid

One of the following:

  • The power supply is switched off.

  • There is input voltage.

  • The input voltage is present, but a fault is detected.

Green

Solid

The power supply is functioning properly.

OK (Power OK)

Green

Solid

The power supply is functioning properly.

Yellow

Blinking

The power supply output has detected a fault.

Unlit

Off

The power supply is switched off.

! (Fault)

Red

Solid

The power supply has failed and must be replaced.

Unlit

Off

The power supply is functioning normally.

JNP10K-PWR-AC2 Power Supply

The JNP10K-PWR-AC2 power supply is a high-capacity model that is designed to support AC, high-voltage AC (HVAC), or high-voltage DC (HVDC) systems in either a 20-A or a 30-A mode; see Figure 4. The power supply feeds AC input and provides DC output of 5000 W with a single feed and 5500 W with a dual feed. The operating input voltage range is 180 to 305 VAC for AC systems and 190 to 410 VDC for DC systems.

The number of power feeds and whether the power supplies provide high-output (30-A) or low-output (20-A) power are configured using a set of dual inline package (DIP) switches on the faceplate of the power supply. If one power supply in the chassis is set to low power, the power budget for the chassis is reduced to low power, regardless of their DIP switch settings or the output results in the CLI. This design safeguards against accidentally setting the power supply to 30 A in a facility that can provide only 20 A and tripping the facility circuit breaker. We recommend that you don’t mix DIP switch settings in your system. See Table 5 for information about the input and output voltages when you use the DIP switches.

Figure 4: JNP10K-PWR-AC2 Power Supply JNP10K-PWR-AC2 Power Supply
Warning:

Extreme burn danger—Do not handle an HVAC or HVDC power supply running in the chassis without heat protective gloves. The JNP10K-PWR-AC2 can reach temperatures in the range of 158°F to 176°F (70°C to 80°C) under running conditions.

Warning:

The router is pluggable type A equipment installed in a restricted-access location. It has a separate protective earthing terminal on the chassis that must be connected to earth ground permanently to ground the chassis adequately and protect the operator from electrical hazards.

CAUTION:

Before you begin installing the router, ensure that a licensed electrician has attached an appropriate grounding lug to the grounding cable that you supply. Using a grounding cable with an incorrectly attached lug can damage the router.

CAUTION:

Use a 2-pole circuit breaker rated at 25 A in the building installation and the system, or as per local electrical code.

Table 5: DIP Switch Settings for JNP10K-PWR-AC2 Power Supplies

INP0—PS 0(DIP Switch 1)

INP1—PS 1(DIP Switch 2)

H/L (High Input 30 A/Low Input 20 A)

Output Power

On

On

On (30 A)

5500 W

On

On

Off (20 A)

3000 W

On

Off

On (30 A)

5000 W

Off

On

On (30 A)

5000 W

On

Off

Off (20 A)

2700 W

Off

On

Off (20 A)

2700 W

Note:

If one of the DIP switches is in the on position and if the power switch is set to the off position, the system raises an alarm that the input feeds are missing. You can avoid this by setting both the DIP switches to off position.

Note:
  • IP1
    • INP1 in the CLI output for Junos OS Evolved Release 20.4R2 or later.
    • INP0 in the CLI output for releases earlier than Junos OS Evolved Release 20.4R2.
  • IP2
    • INP2 in the CLI output for Junos OS Evolved Release 20.4R2 or later.
    • INP1 in the CLI output for releases earlier than Junos OS Evolved Release 20.4R2.
CAUTION:

It is important to connect both input feeds of the JNP10K-PWR-AC2 power supply to AC mains before loading the system with power.

The power supplies have internal fans that contribute to chassis cooling. Therefore, all the power supplies must be present in a running chassis to have the adequate airflow. While all power supplies are required to be present in the chassis, they do not necessarily be connected to power. If a power supply is installed in a slot but is not connected to a power source, it draws power from the chassis to power the internal fans in the power supplies.

JNP10K-PWR-AC2 Power Supply LEDs

The JNP10K-PWR-AC2 power supply has four LEDs on its faceplate: !, OK, 2, and 1. These LEDs display information about the status of the power supply. See Figure 5.

Figure 5: LEDs on a JNP10K-PWR-AC2 Power Supply LEDs on a JNP10K-PWR-AC2 Power Supply
  1

! Fault

  3

2 INP2–Source input 1

  2

OK Power OK

  4

1 INP1–Source input 0

Note:

Physical markings on the power supply are 1 and 2. These markings correspond to INP0 and INP1 in the show chassis power output (see Table 6).

Table 6: Physical Markings on Chassis Versus show chassis power Command

Physical Marking on JNP10K-PWR-AC2

show chassis power Command

1

INP0

2

INP1

Table 7 describes the LEDs on a JNP10K-PWR-AC2 power supply.

Table 7: JNP10K-PWR-AC2 LEDs on a PTX10004

LED

Color

State

Description

1 (or INPO in CLI output)

Yellow

Solid

One of the following:

  • The power supply is switched off.

  • There is no input voltage.

  • The input voltage is present, but a fault is detected.

Green

Solid

The power supply is functioning properly.

2 (or INP1 in CLI output)

Yellow

Solid

One of the following:

  • The power supply is switched off.

  • There is no input voltage.

  • The input voltage is present, but a fault is detected.

Green

Solid

The power supply is functioning properly.

OK (Power OK)

Green

Solid

The power supply is functioning properly.

Yellow

Blinking

The power supply output has detected a fault.

Unlit

Off

The power supply is switched off.

! (Fault)

Red

Solid

The power supply has failed and must be replaced.

Unlit

Off

The power supply is functioning normally.

JNP10K-PWR-DC2 Power Supply

The JNP10K-PWR-DC2 power supply provides two power supplies in a single housing that accepts either 60 A or 80 A using four redundant input power feeds. See Figure 6.

Figure 6: JNP10K-PWR-DC2 Power Supply JNP10K-PWR-DC2 Power Supply

The two internal power supplies (PS 0 and PS 1) each have redundant input feeds: A0 and/or B0 provide power to PS 0 and A1 and/or B1 provide power to PS 1.The input feed A0 or B0 with the highest input voltage provides power to PS 0. Similarly, the input feed A1 or B1 with the highest input voltage provides power to PS 1. A0, B0, A1, and B1 share the power if the input voltage is the same. You configure the input using a set of three DIP switches on the power supply faceplate that sets the combined output power for both internal power supplies. The output depends on the settings of these DIP switches. See Table 8. The output of the PS 0 and PS 1 shares the output power.

Table 8: DIP Switch Settings for JNP10K-PWR-DC2 Power Supplies

INP0—PS 0(DIP Switch 1)

INP1—PS 1(DIP Switch 2)

H/L (High Input 80 A/Low Input 60 A)

Output Power

On

On

On (80 A)

5500 W

On

On

Off (60 A)

4400 W

On

Off

On (80 A)

2750 W

Off

On

On (80 A)

2750 W

On

Off

Off (60 A)

2200 W

Off

On

Off (60 A)

2200 W

A combined output of 5500 W with PS 0 and PS 1 active is available at 56 VDC or greater. If the input voltage is less than 56 VDC, the output power decreases linearly, keeping the input current a little below the default 60 A. However, the power supply supports 5500 W at lower input voltage if you provide 80 A and sets the power supply switch to 80 A setting.

A combined output of 2750 W with only PS 0 or PS 1 active is available at 56 VDC or greater. If the input voltage is less than 56 VDC, the output power decreases linearly, keeping the input current a little below the default 60 A. However, the power supply supports 2750 W at lower input voltage if you provide 80 A and sets the power supply switch to 80 A setting.

The JNP10K-PWR-DC2 power supply requires a dedicated circuit breaker for each input DC feed. You must use a circuit breaker that is rated for 80 A DC with medium delay.

The power supplies have internal fans that contribute to chassis cooling. Therefore, all the power supplies must be present in a running chassis to have the adequate airflow. While all power supplies are required to be present in the chassis, they do not necessarily be connected to power. If a power supply is installed in a slot but is not connected to a power source, it draws power from the chassis to power the internal fans in the power supplies.

Warning:

The router is pluggable type A equipment installed in a restricted-access location. It has a separate protective earthing terminal on the chassis that must be connected to earth ground permanently to ground the chassis adequately and protect the operator from electrical hazards.

CAUTION:

Before you begin installing the router, ensure that a licensed electrician has attached an appropriate grounding lug to the grounding cable that you supply. Using a grounding cable with an incorrectly attached lug can damage the router.

JNP10K-PWR-DC2 Power Supply LEDs

A JNP10K-PWR-DC2 power supply has four LEDs on its faceplate: 1, 2, OK, and the symbol for fault, !. These LEDs display information about the status of the power supply. See Figure 7.

Figure 7: LEDs on a JNP10K-PWR-DC2 Power Supply LEDs on a JNP10K-PWR-DC2 Power Supply
  1

! Fault

  3

2 Power source input 1

  2

OK Power OK

  4

1 Power source input 0

Table 9 describes the LEDs on a JNP10K-PWR-DC2 power supply.

Table 9: LEDs on a JNP10K-PWR-DC2 Power Supply

LED

Color

State

Description

1 (INP0 in CLI output) or 2 (INP1 in CLI output)

Green

Solid

The DC power is within normal operating range (—40 VDC to —72 VDC).

Yellow

Blinking

The DC power input voltage is not within normal operating range.

Unlit

Off

The power supply is switched off.

OK (Power OK)

Green

Solid

The DC power output is within normal operating range.

Yellow

Blinking

The power supply output is out of the power limits.

! (Fault)

Red

Solid

The power supply has failed and must be replaced.

Unlit

Off

The power supply is functioning normally. Or, only one input is powered and the enable switch for the input that is not powered is set to ON. See Install a JNP10K-PWR-DC2 Power Supply for more information about the enable switches.

Note:

If the 1 or 2 and the OK LED are unlit, the power cables are not installed properly or the power supply has failed.

If the 1 or 2 LED is lit green and the OK LED is unlit, the power supply is not installed properly or the power supply has an internal failure.

If the ! LED is blinking, add a power supply to balance the power demand and supply.