PTX10016 Power Planning

Use the information to calculate the power consumption for the PTX10016 and plan your configuration’s power requirements.

Power Requirements for PTX10016 Components

Table 1 lists the power requirements for different hardware components of a PTX10016 router running the JNP10016-SF under typical voltage conditions and optics.

Table 1: Power Requirements for PTX10016 Components Running the JNP10016-SF

Component

Description

Power Requirements (W)

At 25° C for all systems

At 40° C for systems running Junos OS Evolved

At 55° C for systems running standard Junos OS

JNP10016-SF

PTX10016 SIB

510

593

675

JNP10016-FAN

PTX10016 fan tray

475

975 at the maximum fan speed

JNP10K-RE0

PTX10016 standard RCB

50

75

100

JNP10K-RE1

PTX10016 enhanced RCB

100

138

175

PTX10K-LC1101

PTX10016 30-port QSFP28 line card

890

1020

1150

PTX10K-LC1102

PTX10016 36-port QSFP+ line card

520

598

675

PTX10K-LC1104

PTX10016 coherent DWDM line card

900

975

1050

PTX10K-LC1105

PTX10016 30-port MACsec QSSP28 line card

950

1100

1250

QFX10000-60S-6Q

PTX10016 60-port SFP+ and 6-port QSFP+ line card

365

410

465

Table 2 lists the power requirements for different hardware components of a PTX10016 router running the JNP10016-SF3 under typical voltage conditions and optics.

Note:

The power management considers the values in the column titled 'Default Power Considered' in Table 2 to determine the power requirement when a new component is installed. You can disable the default power management by using the no-power-budget command.

Table 2: Power Requirements for PTX10016 Components Running the JNP10016-SF3

Component

Description

Power Requirements (W)

At 25° C for all systems

At 40° C for systems running Junos OS Evolved

Default Power Considered

JNP10016-SF3

PTX10016 SIB that is supported on a PTX10016 router running Junos OS Evolved Release 21.2R2 and later.

1683

1763

680

JNP10016-FAN2

PTX10016 fan tray that is supported on a PTX10016 router running Junos OS Evolved Release 21.2R2 and later and has JNP10016-SF3 SIB installed in it.

2300

2300

2530

JNP10K-RE1-E

RCB for the PTX10016 router running Junos OS Evolved Release 21.2R2 and later and has JNP10016-SF3 SIB installed in it

100

150

200

PTX10KLC1201-36CD

PTX10016 line card with 36 QSFP56-DD ports that support 400-Gbps speed. You can channelize the ports to operate at 200-Gbps, 100-Gbps, 50-Gbps, 25-Gbps, or 10-Gbps speed by using breakout cables.

If the router has Junos OS Evolved Release 21.4 or earlier installed in it

2360

976

1008

If the router has Junos OS Evolved Release 22.1 or later installed in it

918

948

PTX10K-LC1202-36MR

PTX10016 line card with 32 QSFP28 ports and 4 QSFP56-DD ports (without optical transceivers)

740

750

1150

CAUTION:

To ensure adequate power and to avoid raising a power alarm, we recommend that you maintain n +1 power supplies in your router at all times. Replace failed power supplies immediately to prevent unexpected failures.

If a new line card is installed in an operational router, power management does not power on the line card if the increased power demand exceeds the total available power, including redundant power. If redundant power is used to power on the line card, a minor alarm is raised, which becomes a major alarm in five minutes if the condition is not corrected.

You can view the total power provided to the chassis, the power required to operate the chassis and the components installed in it, and the balance power available in the chassis by using the show chassis power detail command.

JNP10K-PWR-AC Power Specifications

PTX10008 and PTX10016 redundant-configuration routers can use either AC or DC power supplies; base-configuration routers are AC only. You can run the JNP10K-PWR-AC power supply only in routers in which you have installed the JNP10008-SF or JNP10016-SF switch fabric.

Table 3 lists the power specifications for the AC power supply (JNP10K-PWR-AC) used in a PTX10008 or PTX10016 chassis.

Table 3: Power Specifications for a JNP10K-PWR-AC Power Supply

Item

Specification

AC input voltage

Operating range: 200–240 VAC

AC input line frequency

50–60 Hz

AC input current rating

16 A

AC output power

2700 W

CAUTION:

Use a 2-pole circuit breaker rated at 25 A in the building installation and the system, or as per local electrical code.

Table 4 shows the physical specifications for an AC power supply.

Table 4: Physical Specifications for a JNP10K-PWR-AC Power Supply

Specification

Value

Height

3.4 in. (8.64 cm)

Width

3.6 in. (9.14 cm)

Depth

14.4 in. (36.58 cm)

Weight

6.8 lb (3.08 kg)

JNP10K-PWR-AC2 Power Specifications

PTX10008 and PTX10016 redundant configuration routers can use either AC or DC power supplies; base configuration routers can use AC power supplies only. The JNP10K-PWR-AC2 power supply supports AC, HVAC, and HVDC inputs.

Table 5 lists the power specifications for the JNP10K-PWR-AC2 power supply supported by the PTX10008 and PTX10016 routers.

Table 5: Power Specifications for a JNP10K-PWR-AC2 Power Supply

Item

Specification

AC input voltage

180–305 VAC

DC input voltage

190–410  VDC

Input current rating

28.5 A

DC output power

12.3 V, 5500 W with dual feed and 5000 W with single feed

Table 6 shows the physical specifications of the JNP10K-PWR-AC2 power supply.

Table 6: Physical Specifications of the JNP10K-PWR-AC2 Power Supply

Specification

Value

Height

3.4 in. (8.64 cm)

Width

3.6 in. (9.14 cm)

Depth

16.6 in. (42.16 cm)

Weight

11.4 lb (5.17 kg)

PTX10016 Power Cables Specifications

Most sites distribute power through a main conduit that leads to frame-mounted power distribution panels, one of which can be located at the top of the rack that houses the router. An AC power cord connects each power supply to the power distribution panel.

Note:

In North America, AC power cords must not exceed 15 feet (approximately 4.5 meters) in length, to comply with National Electrical Code (NEC) Sections 400-8 (NFPA 75, 5-2.2) and 210-52 and Canadian Electrical Code (CEC) Section 4-010(3). The cords shipped with the router to North America and Canada are in compliance.

PTX10016 AC, high-voltage alternating current (HVAC), and high-voltage direct current (HVDC) power supplies have specific cord requirements. Use the following sections to determine the cable requirements based on the model of your power supply and any mode settings:

JNP10K-PWR-AC Power Cable Specifications

Each JNP10K-PWR-AC power supply has two independent 16 A rated AC inlets on the faceplate.

Each detachable AC power cord for is 8 feet (approximately 2.5 meters) long. The coupler end of the appliance cord inserts into the AC appliance inlet on the faceplate of the AC power supply. The coupler type is C19 as described by the International Electrotechnical Commission (IEC) standard 60320. The plug end of the power cord fits into the power source outlet that is standard for your geographical location.

Table 7 lists the AC power cord specifications for JNP10K-PWR-AC for various countries and regions.

Table 7: AC Power Cord Specifications for JNP10K-PWR-AC Power Supplies

Country/Region

Electrical Specifications

Plug Standards

Juniper Model Number

Graphic

Argentina

250 VAC, 16 A, 50 Hz

IRAM Type RA/3/20

CBL-EX-PWR-C19-AR

Australia

250 VAC, 15 A, 50 Hz

AS/NZS 3112 Type SAA/3/15

CBL-EX-PWR-C19-AU

Brazil

250 VAC, 16 A, 50 Hz

NBR 14136: 2002 Type BR/3/20

CBL-EX-PWR-C19-BR

China

250 VAC, 16 A, 50 Hz

GB 1002 Type PRC/3/16

CBL-EX-PWR-C19-CH

Europe (except Italy, Switzerland, and United Kingdom)

250 VAC, 16 A, 50 Hz

CEE (7) VII Type VIIG

CBL-EX-PWR-C19-EU

India

250 AC, 16 A, 50 Hz

SABS 164/1:1992 Type ZA/3

CBL-EX-PWR-C19-SA

Israel

250 AC, 16 A, 50 Hz

SI 32/1971 Type IL/3

CBL-EX-PWR-C19-IL

Italy

250 VAC, 16 A, 50 Hz

CEI 23-16 Type I/3/16

CBL-EX-PWR-C19-IT

Japan

250 VAC, 16 A, 60 Hz

NEMA 6–20 Type N6/20

CBL-EX-PWR-C19-JP (default)

250 VAC, 16 A, 60 Hz

NEMA L6–20P Type NEMA Locking

CBL-EX-PWR-C19-JPL

Korea

250 VAC, 16 A, 50 Hz

CEE (7) VII Type VIIG

CBL-EX-PWR-C19-KR

North America

250 VAC, 16 A, 60 Hz

NEMA 6–20 Type N6/20

CBL-EX-PWR-C19-US (default)

250 VAC, 16 A, 60 Hz

NEMA L6–20P Type NEMA Locking

CBL-EX-PWR-C19-USL

South Africa

250 VAC, 16 A, 50 Hz

SABS 164/1:1992 Type ZA/3

CBL-EX-PWR-C19-SA

Switzerland

250 VAC, 16 A, 50 Hz

SEV 5934/2 Type 23G

CBL-EX-PWR-C19-SZ

United Kingdom

250 VAC, 13 A, 50 Hz

BS 1363/A Type BS89/13

CBL-EX-PWR-C19-UK

Worldwide (other)

250 VAC, 16 A, 50 Hz

EN 60320-2-2/1

CBL-EX-PWR-C19-C20

CAUTION:

It is important to connect both input feeds of the JNP10K-PWR-AC2 power supply to AC mains before loading the system with power.

CAUTION:

Use a 2-pole circuit breaker rated at 25 A in the building installation and the system, or as per local electrical code.

JNP10K-PWR-AC2 Power Cable Specifications

The JNP10K-PWR-AC2 power supply operates in two modes:

  • JNP10K-PWR-AC2 Power Cable Specifications for 30-A Input shows the cables and connectors for 30-A input with 5500-W output. One end of the cable has a type SAF-D-GRID Series (3-5958P4) Anderson APP-400 connector, rated 30A/400V/105C, while the other end of the cable is bare wire. An example of the connector is shown in Figure 1.

  • Table 8 shows the cables appropriate for 20-A input with 3000-W output. One end of the cable has a type SAF-D-GRID Series (3-5958P4) Anderson APP-400 connector, rated 30A/400V/105C.

  • Table 9 shows the cable appropriate for HVAC input with 3000-W output. One end of the cable has a type SAF-D-GRID Series (3-5958P4) Anderson APP-400 connector, rated 30A/400V/105C.

Warning:

Do not run JNP10K-PWR-AC2 power supplies using 16-A or 20-A cables if connected to 30-A input.

CAUTION:

You can prevent AC power cables from being exposed to hot air exhaust by always routing the power cables away from the fan trays and power supplies.

Note:

The cables that we ship are 4.5 m long and come with AWG or mm² wire size depending on your country or region.

Table 8: JNP10K-PWR-AC2 Power Cable Specifications for 20-A Input

Locale

Cord Set Rating

Plug Standards

Spare Juniper Model Number

Graphic

Argentina

16 A, 250 VAC

IRAM 2073 Type RA/3

CBL-JNP-SG4-AR

Australia and New Zealand

15 A, 250  VAC

AS/NZS 3112

CBL-JNP-SG4-AU

Brazil

16 A, 250 VAC

NBR 14136 Type BR/3

CBL-JNP-SG4-BR

China

16 A, 250 VAC

GB2099

CBL-JNP-SG4-CH

China, Europe, and Japan

16 A, 250 VAC

C20 to Anderson 3-5958p4

CBL-JNP-SG4-C20-CH

Europe (except Italy, Switzerland, and United Kingdom)

20 A, 250 VAC

CEE 7/7

CBL-JNP-SG4-EU

Great Britain

13 A, 250 VAC,

BS1363

CBL-JNP-SG4-UK

India

16 A, 250 VAC

SANS 164/1

CBL-JNP-SG4-SA

Israel

16 A, RA, 250 VAC

SI 32/1971 Type IL/3C

CBL-JNP-SG4-IL

Italy

16 A, 250 VAC

CEI 23-50

CBL-JNP-SG4-IT

North America

20 A, 250 VAC

3-5958P4 to IEC 60320 C20

CBL-JNP-SG4-C20

16 A, 250 VAC

Locking NEMA L6-20P

CBL-JNP-SG4-US-L

NEMA 6-20P

CBL-JNP-SG4-US

South Africa

16 A, 250 VAC

SANS 164/1

CBL-JNP-SG4-SA

Switzerland

16 A, 250 VAC

CEI 23-50

CBL-JNP-SG4-SZ

Table 9: JNP10K-PWR-AC2 Power Cable Specifications for HVAC Input

Locale

Cord Set Rating

Plug Standard

Spare Juniper Model Number

Graphic

North America

20 A, 277 V

NEMA L7-20P

CBL-JNP-SG4-HVAC

Figure 1: Bare Cable with Anderson Connector Bare Cable with Anderson Connector

JNP10K-PWR-AC2 Power Cable Specifications for 30-A Input

The JNP10K-PWR-AC2 AC or HVDC power supplies require a high voltage cable assembly when set for 30-A input. One end of the cable has a type SAF-D-GRID Series (3-5958P4) Anderson APP-400 connector, rated 30A/400V/105C, while the other end of the cable is bare wire. See Figure 2 and Table 10. These cables are separately orderable and are not shipped automatically with JNP10K-PWR-AC2 orders. An example of the right-angle cable and connector is shown in Figure 4.

For connection to AC systems, Juniper provides a cable with either a NEMA 30-A connector (Figure 2) or an IEC 330P6W connector (Figure 3).

Figure 2: NEMA 30-A Connector NEMA 30-A Connector
Figure 3: IEC 330P6W Connector IEC 330P6W Connector
Table 10: 30-A Cabling Options

Power Cord

Locale

Cord Set Rating

Plug Standards

Connector

Spare Juniper Model Number

AC/HVDC power cord

Any

30-A, 400 VAC

UL 950 and IEC 60950

Anderson/straight to bare wire

CBL-PWR2-BARE

30-A, 400 VAC

UL 950 and IEC 60950

Anderson/right-angle to bare wire

CBL-PWR2-BARE-RA

AC power cord

Continental Europe

30-A 250 VAC

UL 950 and IEC332P6

Anderson/right-angle to IEC 332P6

CBL-PWR2-332P6W-RA

30-A 250 VAC

UL 950 and IEC332P6

Anderson/straight to IEC332P6

CBL-PWR2-332P6W

North America

30-A 250 VAC

IEC330P6

Anderson/right-angle to IEC 330P6

CBL-PWR2-330P6W-RA

30-A 250 VAC

IEC330P6

Anderson/straight to IEC 330P6

CBL-PWR2-330P6W

30-A 250 VAC

UL 498, CSA

Anderson/right-angle to L6-30P (NEMA-30A)

CBL-PWR2-L6-30P-RA

30-A 250 VAC

UL 498, IEC5958P4

Anderson/straight to L6-30P (NEMA-30A)

CBL-PWR2-L6-30P

Figure 4: Right-Angle, Bare Cable with Anderson Connector Right-Angle, Bare Cable with Anderson Connector
  1

Black wire – Return (+)

  3

White wire – Neutral

  2

Green wire – Ground

 

JNP10K-PWR-DC Power Specifications

The DC power supply (JNP10K-PWR-DC) is supported only in routers in which you have installed the JNP10008-SF or JNP10016-SF switch fabric. Table 11 lists the power specifications for the JNP10K-PWR-DC power supply used in PTX10008 and PTX10016 routers.

Table 11: Power Specifications for the JNP10K-PWR-DC Power Supply

Item

Specifications

DC input voltage

  • Minimum operating voltage: –40 VDC

  • Nominal operating voltage: –48 VDC

  • Operating voltage range: –40 VDC through –72 VDC

DC input current rating

60 A maximum at nominal operating voltage (–48 VDC) for each input terminal

Output power

2500 W

Table 12 shows the physical specifications of the JNP10K-PWR-DC power supply.

Table 12: Physical Specifications of the JNP10K-PWR-DC Power Supply

Specification

Value

Height

3.4 in. (8.64 cm)

Width

3.6 in. (9.14 cm)

Depth

14.4 in. (36.58 cm)

Weight

6 lb (2.72 kg)

JNP10K-PWR-DC2 Power Specifications

HVDC power supplies (JNP10K-PWR-DC2) are supported in only the PTX10008 and PTX10016 redundant configurations. Table 13 lists the power specifications for the HVDC power supply used in PTX10008 and PTX10016 routers.

Table 13: Power Specifications for the JNP10K-PWR-DC2 Power Supply

Item

Specifications

DC input voltage

  • Minimum operating voltage: –40 VDC

  • Nominal operating voltage: –48 VDC

  • Operating voltage range: –40 VDC through –72 VDC

DC input current rating

  • 76-A maximum at minimum operating voltage (-40 VDC) with 80-A DIP switch setting and 5500-W output load.

  • 64-A maximum at nominal operating voltage (–48 VDC) with 80-A DIP switch setting and 5500-W output load.

  • 60-A maximum at minimum operating voltage (-40 VDC) with 60-A DIP switch setting and 4400-W output load.

  • 50-A maximum at nominal operating voltage (-48 VDC) with 60-A DIP switch setting and 4400-W output load.

Output power

2200 W for low input (60-A) single feed

4400 W for low input (60-A) dual feed

2750 W for high input (80-A) single feed

5500 W for high input (80-A) dual feed

Table 14 shows the physical specifications of the JNP10K-PWR-DC2 power supply.

Table 14: Physical Specifications of the JNP10K-PWR-DC2 Power Supply

Specification

Value

Height

3.4 in. (8.64 cm)

Width

3.6 in. (9.14 cm)

Depth

16.05 in. (40.77 cm)

Weight

8.6 lb (3.9 kg)

PTX10016 Grounding Cable and Lug Specifications

You must install the router in a restricted-access location. You must ensure that the router is adequately grounded at all times. Proper grounding ensures your router is operating correctly and that it meets safety and electromagnetic interference (EMI) requirements. The PTX10016 modular chassis has a 2-hole protective earthing terminal on the rear of the chassis beneath the power supplies for grounding.

For AC powered systems, you must also use the grounding wire in the AC power cord along with the 2-hole lug ground connection. This tested system meets or exceeds all applicable EMC regulatory requirements with the 2-hole protective earthing terminal.

Warning:

To comply with GR-1089 requirements, you must shield and ground all intrabuilding copper cabling used for SFP+, QSFP+, and QSFP28 ports at both ends.

CAUTION:

Before router installation begins, a licensed electrician must attach a cable lug to the grounding cables that you supply. See Connect the PTX10016 Router to Earth Ground. A cable with an incorrectly attached lug can damage the router.

Before connecting the router to earth ground, review the following information:

  • We provide two threaded inserts (PEM nuts) on the lower rear of the chassis for connecting the router to earth ground. The grounding points are spaced at 0.63 in. (16 mm) centers.

  • The grounding lug required is a Panduit LCD6-10A-L or equivalent (provided). The grounding lug accommodates 6 AWG (13.3 mm²) stranded wire. If you install one or more JNP10K-PWR-DC2 power supplies in the chassis and set for high input (80 A), use the Panduit LCD4-14A-L or equivalent (provided). This lug accommodates 4 AWG (21.1 mm²) stranded wire. The 4 AWG (21.1 mm²) stranded wire should be rated 90° C, or as permitted by local electrical code.

  • The grounding cable that you provide for a PTX10016 must be the same size or heavier than the input wire of each power supply. Minimum recommendations are 6 AWG (13.3 mm²) stranded copper wire, Class B; 90° C wire, or as permitted by local code.