PTX10008 Power Planning for JNP10008-SF3 Switch Fabric

Use this information to calculate the power consumption for the PTX10008 running the JNP10008-SF3 switch fabric and plan your configuration’s power requirements.

Power Requirements for PTX10008 Components in a JNP10008-SF3 Fabric

Table 1 lists the power requirements for the PTX10008 router running the JNP10008-SF3 under typical voltage conditions and optics.

Note:

The power management considers the values in the column titled 'Default Power Considered' in Table 1 to determine the power requirement when a new component is installed. You can disable the default power management by using the no-power-budget command.

Table 1: Power Consumption JNP10008-SF3 Fabric Systems Running 14.4 Tbps Line Cards

Component

Description

At 25° C

At 40° C

Default Power Considered

JNP10008-SF3

PTX10008 Switch Interface Board

700 W

750 W

680 W

JNP10008-FAN2

PTX10008 fan tray

600 W

1280 W

1265 W

JNP10K-RE1-E

PTX10008 Routing Control Board for Junos OS Evolved systems

100 W

150 W

200 W

PTX10K-LC1201-36CD

PTX10008 36-port QSFP56-DD line card (without optical transceivers)

If the router has Junos OS Evolved Release 21.4 or earlier installed in it

2360 W

976 W

1008 W

If the router has Junos OS Evolved Release 22.1 or later installed in it

918 W

948 W

PTX10K-LC1202-36MR

PTX10008 line card with thirty-two QSFP28 ports and four QSFP56-DD ports (without optical transceivers)

740 W

750 W

1150 W

CAUTION:

To ensure adequate power and to avoid raising a power alarm, we recommend that you maintain n +1 power supplies in your router at all times. Replace failed power supplies immediately to prevent unexpected failures.

If a new line card is installed in an operational router, power management does not power on the line card if the increased power demand exceeds the total available power, including redundant power. If redundant power is used to power on the line card, a minor alarm is raised, which becomes a major alarm in five minutes if the condition is not corrected.

You can view the total power provided to the chassis, the power required to operate the chassis and the components installed in it, and the balance power available in the chassis by using the show chassis power detail command.

JNP10K-PWR-AC2 Power Specifications

The JNP10K-PWR-AC2 power supply supports AC, HVAC, and HVDC. You can run the JNP10K-PWR-AC2 power supply in either JNP10008-SF or in JNP10008-SF3 fabric systems. However, if you are upgrading a JNP10008-SF system to use JNP10K-PWR-AC2 power supplies, also upgrade your fans and fan tray controllers to ensure the proper airflow. JNP10K-PWR-AC2 power supplies require JNP10008-FAN2 and JNP10008-FTC2 cooling systems.

Table 2 lists the power specifications for the AC power supply (JNP10K-PWR-AC2) used in a PTX10008 chassis.

Table 2: Power Specifications for a JNP10K-PWR-AC2 Power Supply

Item

Specifications

AC input voltage

180–305 VAC

DC input voltage

190–410  VDC

Input current rating

28.5 A

DC output power

5500 W with dual feed and 5000 W with single feed

Table 3 shows the physical specifications for a JNP10K-PWR-AC2 power supply.

Table 3: Physical Specifications for a JNP10K-PWR-AC2 Power Supply

Specification

Value

Height

3.5 in. (8.89 cm)

Width

3.6 in. (9.14 cm)

Depth

15.1 in. (38.35 cm)

Weight

11.4 lb (5.17 kg)

JNP10K-PWR-AC2 Power Cable Specifications

Most sites distribute power through a main conduit that leads to frame-mounted power distribution panels, one of which can be located at the top of the rack that houses the router. An AC power cord connects each power supply to the power distribution panel.

Note:

In North America, AC power cords must not exceed 15 feet (approximately 4.5 meters) in length, to comply with National Electrical Code (NEC) Sections 400-8 (NFPA 75, 5-2.2) and 210-52 and Canadian Electrical Code (CEC) Section 4-010(3). The cords shipped with the router to North America and Canada are in compliance.

PTX10008 AC, high-voltage alternating current (HVAC), and high-voltage direct current (HVDC) power supplies have specific cord requirements. Use the following sections to determine the cable requirements based on the model of your power supply and any mode settings:

JNP10K-PWR-AC2 Power Cable Specifications

When the JNP10K-PWR-AC2 power supply is operating in 20-A mode, it has an output of 2700-W with a single feed and 3000-W with dual feeds. Table 4 shows the cables appropriate for 20-A input. Table 5 shows the cable appropriate for HVAC input. One end of the cable has a type SAF-D-GRID Series (3-5958P4) Anderson APP-400 connector, rated 30A/400V/105C. An example of the connector is shown in Figure 1.

Warning:

Do not run JNP10K-PWR-AC2 power supplies using 16-A or 20-A cables if connected to 30-A input.

CAUTION:

You can prevent AC power cables from being exposed to hot air exhaust by always routing the power cables away from the fan trays and power supplies.

CAUTION:

It is important to connect both input feeds of the JNP10K-PWR-AC2 power supply to AC mains before loading the system with power.

Note:

The cables that we ship are 4.5 m long and come with AWG or mm² wire size depending on your country or region.

Table 4: JNP10K-PWR-AC2 Power Cable Specifications for 20-A Input

Locale

Cord Set Rating

Plug Standards

Spare Juniper Model Number

Graphic

Argentina

16 A, 250 VAC

IRAM 2073 Type RA/3

CBL-JNP-SG4-AR

Australia and New Zealand

15 A, 250  VAC

AS/NZS 3112

CBL-JNP-SG4-AU

Brazil

16 A, 250 VAC

NBR 14136 Type BR/3

CBL-JNP-SG4-BR

China

16 A, 250 VAC

GB2099

CBL-JNP-SG4-CH

China, Europe, and Japan

16 A, 250 VAC

C20 to Anderson 3-5958p4

CBL-JNP-SG4-C20-CH

Europe (except Italy, Switzerland, and United Kingdom)

20 A, 250 VAC

CEE 7/7

CBL-JNP-SG4-EU

Great Britain

13 A, 250 VAC,

BS1363

CBL-JNP-SG4-UK

India

16 A, 250 VAC

SANS 164/1

CBL-JNP-SG4-SA

Israel

16 A, RA, 250 VAC

SI 32/1971 Type IL/3C

CBL-JNP-SG4-IL

Italy

16 A, 250 VAC

CEI 23-50

CBL-JNP-SG4-IT

North America

20 A, 250 VAC

3-5958P4 to IEC 60320 C20

CBL-JNP-SG4-C20

16 A, 250 VAC

Locking NEMA L6-20P

CBL-JNP-SG4-US-L

NEMA 6-20P

CBL-JNP-SG4-US

South Africa

16 A, 250 VAC

SANS 164/1

CBL-JNP-SG4-SA

Switzerland

16 A, 250 VAC

CEI 23-50

CBL-JNP-SG4-SZ

Figure 1: Bare Cable with Anderson Connector Bare Cable with Anderson Connector
Table 5: JNP10K-PWR-AC2 Power Cable Specifications for HVAC Input

Locale

Cord Set Rating

Plug Standard

Spare Juniper Model Number

Graphic

North America

16 A, 277 V

NEMA L7-20P

CBL-JNP-SG4-HVAC

JNP10K-PWR-AC2 Power Cable Specifications for 30-A Input

The JNP10K-PWR-AC2 AC or HVDC power supply require a high voltage cable assembly when set for 30-A input. One end of the cable has a type SAF-D-GRID Series (3-5958P4) Anderson APP-400 connector, rated 30A/400V/105C, while the other end of the cable is bare wire. See Figure 2 and Table 6. These cables are separately orderable and are not shipped automatically with JNP10K-PWR-AC2 orders. An example of the right-angle cable and connector is shown in Figure 4.

For connection to AC systems, Juniper provides a cable with either a NEMA 30-A connector (Figure 2) or an IEC 330P6W connector (Figure 3).

Figure 2: NEMA 30-A Connector NEMA 30-A Connector
Figure 3: IEC 330P6W Connector IEC 330P6W Connector
Table 6: 30-A Cabling Options

Description

Locale

Cord Set Rating

Plug Standards

Connector

Spare Juniper Model Number

AC/HVDC power cord

Any

30-A, 400 VAC

UL 950 and IEC 60950

Anderson/straight to bare wire

CBL-PWR2-BARE

30-A, 400 VAC

UL 950 and IEC 60950

Anderson/right-angle to bare wire

CBL-PWR2-BARE-RA

AC power cord

Continental Europe

30-A 250 VAC

UL 950 and IEC332P6

Anderson/right-angle to IEC 332P6

CBL-PWR2-332P6W-RA

30-A 250 VAC

UL 950 and IEC332P6

Anderson/straight to IEC332P6

CBL-PWR2-332P6W

North America

30-A 250 VAC

IEC330P6

Anderson/right-angle to IEC 330P6

CBL-PWR2-330P6W-RA

30-A 250 VAC

IEC330P6

Anderson/straight to IEC 330P6

CBL-PWR2-330P6W

30-A 250 VAC

UL 498, CSA

Anderson/right-angle to L6-30P (NEMA-30A)

CBL-PWR2-L6-30P-RA

30-A 250 VAC

UL 498, IEC5958P4

Anderson/straight to L6-30P (NEMA-30A)

CBL-PWR2-L6-30P

Figure 4: Right-Angle, Bare Cable with Anderson Connector Right-Angle, Bare Cable with Anderson Connector
  1

Black wire – “+” or “-“ for HVDC and “Hot or neutral” for AC

  3

White wire – “+” or “-“ for HVDC and “Hot or neutral” for AC

  2

Green wire - Ground

 

JNP10K-PWR-DC2 Power Specifications

If you are upgrading a JNP10008-SF system to use JNP10K-PWR-DC2 power supplies, also upgrade your fans and fan tray controllers to ensure the proper airflow. JNP10K-PWR-DC2 power supplies require JNP10008-FAN2 and JNP10008-FTC2 cooling systems.Table 7 lists the power specifications for the dual DC power supply used in a PTX10008 chassis.

Table 7: Power Specifications for the JNP10K-PWR-DC2 Power Supply

Item

Specifications

DC input voltage

  • Minimum operating voltage: –40 VDC

  • Nominal operating voltage: –48 VDC

  • Operating voltage range: –40 VDC through –72 VDC

DC input current rating

  • 76-A maximum at minimum operating voltage (-40 VDC) with 80-A DIP switch setting and 5500-W output load

  • 64-A maximum at nominal operating voltage (–48 VDC) with 80-A DIP switch setting and 5500-W output load

  • 60-A maximum at minimum operating voltage (-40 VDC) with 60-A DIP switch setting and 4400-W output load

  • 50-A maximum at nominal operating voltage (-48 VDC) with 60-A DIP switch setting and 4400-W output load

Output power

2200 W for low input (60-A) single feed

4400 W for low input (60-A) dual feed

2750 W for high input (80-A) single feed

5500 W for high input (80-A) dual feed

Table 8 shows the physical specifications for a JNP10K-PWR-DC2 power supply.

Table 8: Physical Specifications of a JNP10K-PWR-DC2 Power Supply

Specification

Value

Height

3.5 in. (8.89 cm)

Width

3.6 in. (1.63 cm)

Depth

16.05 in. (40.77 cm)

Weight

8.1 lb (3.67 kg)