PTX10002-36QDD Power System

The router supports the following power supplies (PSUs):

  • 2200-W HVAC/HVDC

  • 2200-W DC

  • 3000-W HVAC/HVDC

  • 3000-W DC

The router supports 1+1 redundant, preinstalled PSUs. The PSUs are installed on the rear panel of the chassis in power supply slots labeled 0 and 1. The PSUs directly plug into the power distribution board and are located symmetrically on the left side of the rear panel of the chassis for better thermal management. The power distribution board distributes different output voltages produced by the PSUs to the router components, depending on their voltage requirements. Each PSU has a handle, an ejection lever, and a status LED. A minimum of one PSU is required for non-redundant operation. Both the PSUs must be present in the chassis for the normal operation of the router. If one PSU in a redundant configuration fails, the second PSU assumes the entire electrical load without interruption. The PSUs are hot-insertable and hot-removable, field-replaceable units (FRUs): You can remove and replace them without powering off the router or disrupting the router functions.

Each PSU is cooled by its own internal cooling system.

CAUTION:

You must not mix:

  • HVAC/HVDC and DC PSUs in the same chassis.

  • 2200-W and 3000-W PSUs in the same chassis

PTX10002-36QDD HVAC/HVDC Power Supply Units

The router supports 2200-W HVAC/HVDC and 3000-W HVAC/HVDC PSUs. The PSUs automatically detect whether there is HVAC or HVDC input voltage and manage the power accordingly.

Each HVAC/HVDC PSU weighs approximately 3 lb (1.36 kg) and consists of a handle, an ejector lever, an appliance inlet, a built-in fan, and an LED to monitor the status of the PSU. Each inlet requires a dedicated power feed and a dedicated customer-site circuit breaker.

  1

Handle

  3

LED

  2

Inlet plug

  4

Ejector lever

Table 1: LED on the HVAC/HVDC PSU

State

Color

Pattern

Description

On

Green

On steadily

The PSU is receiving power.

On

Green

Blinking

There is input power; however, the PSU is off.

On

Amber

On steadily

The PSU is not functioning normally and has a fault.

On

Amber

Blinking

The system software has shut down the PSU.

Off

The PSU is in off state.

The router operates within the HVAC/HVDC input voltage range listed in Table 2.

Table 2: PTX10002-36QDD HVAC/HVDC Power Specifications

Parameter

Minimum

Rated

Maximum

Input voltage—HVAC

180 VAC

200–277 VAC

305 VAC

Frequency for input—HVAC

47 Hz

50-60 Hz

63 Hz

Input voltage—HVDC

190 VDC

240–380 VDC

400 VDC

Table 3 lists the specifications of the HVAC power cord provided for each country or region.

Table 3: PTX10002-36QDD HVAC Power Cord Specifications

Locale

Cord Set Rating

Plug Standards

Spare Juniper Model Number

Graphic

Argentina

16 A, 277 VAC

IRAM 2073 Type RA/3

CBL-JNP-SG4-AR

Australia and New Zealand

16 A, 277  VAC

AS/NZS 4417

CBL-JNP-SG4-AU

Brazil

16 A, 277 VAC

NBR 14136 Type BR/3

CBL-JNP-SG4-BR

China

16 A, 277 VAC

GB2099

CBL-JNP-SG4-CH

China, Europe, and Japan

16 A, 277 VAC

C20 to Anderson 3-5958p4

CBL-JNP-SG4-C20-CH

Europe (except Italy, Switzerland, and United Kingdom)

16 A, 277 VAC

CEE 7/7 STRAIGHT

CBL-JNP-SG4-EU

Great Britain

16 A, 277 VAC,

BS1363

CBL-JNP-SG4-UK

India

16 A, 277 VAC

SANS 164/1

CBL-JNP-SG4-SA

Israel

16 A, RA, 277 VAC

SI 32/1971 Type IL/3G

CBL-JNP-SG4-IL

Italy

16 A, 277 VAC

CEI 23-16

CBL-JNP-SG4-IT

Japan

16 A, 277 VAC

Nema L-20

CBL-JNP-SG4-JPL

North America

20 A, 277 VAC

C20 to Anderson 3-5958p4

CBL-JNP-SG4-C20

North America

20 A, 277 VAC

Locking NEMA L6-20P

CBL-JNP-SG4-US-L

North America

20 A, 277 VAC

NEMA 6-20P

CBL-JNP-SG4-US

North America

20 A, 277 V

NEMA I7-20P

CBL-JNP-SG4-HVAC

South Africa

16 A, 277 VAC

SANS 164/1

CBL-JNP-SG4-SA

Switzerland

16 A, 277 VAC

CEI 23-50

CBL-JNP-SG4-SZ

Table 4 lists the specifications of the HVDC power cord.

Table 4: PTX10002-36QDD HVDC Power Cord Specifications

Cord Set Rating

Spare Juniper Model Number

16 A, 400 HVDC

CBL-PWR2-BARE

PTX10002-36QDD DC Power Supply Units

The router supports 2200-W DC and 3000-W DC PSUs. Each PSU has a single DC input and provides 12 VDC output with a standby voltage of 12 VDC.

Each DC PSU weighs approximately 3 lb (1.36 kg) and consists of a handle, an ejector lever, a terminal block that provides a single DC input (–48/–60 VDC and return), a built-in fan, and an LED to monitor the status of the PSU. The DC PSU requires a dedicated customer-site circuit breaker. We recommend that you use a dedicated customer-site circuit breaker rated for 80 A (125 VDC), or as required by the local code.

  1

Ejector lever

  4

Handle

  2

LED

  5

Terminal block

  3

DC input current selector (DIP) switch

 

The DIP switch is used to select the DC input current. The switch is active only in the 3000-W DC PSU.

Table 5: LED on the DC PSU

State

Color

Pattern

Description

On

Green

On steadily

The PSU is receiving power.

On

Green

Blinking

There is input power; however, the PSU is off.

On

Amber

On steadily

The PSU is not functioning normally and has a fault.

On

Amber

Blinking

The system software has shut down the PSU.

Off

The PSU is in off state.