MX104 Power System
MX104 Power Overview
The MX104 router uses either AC or DC power supplies (see Figure 1 and Figure 2). The power supplies are located in the front of the chassis and offer 1+1 redundancy. Each power supply has a handle, an ejection tab, and a status LED.
The router cannot be powered from AC and DC power supplies simultaneously.
When two power supplies are present, they share power almost equally within a fully populated system. If one power supply in a redundant configuration fails or is removed, the remaining power supply assumes the entire electrical load without interruption. A single power supply provides the maximum configuration with full power for as long as the router is operational. A second power supply can be installed for redundancy. Each power supply is cooled by its own internal cooling system.
Redundant power supplies are hot-removable and hot-insertable. When you remove a power supply from a router that uses only one power supply, the router might shut down depending on your configuration.
AC Power Supplies
Each AC power supply weighs approximately 2.5 lb (1.13 kg) and consists of a handle, a power cord retainer clip, an ejection latch, an AC appliance inlet, a fan, and an LED to monitor the status of the power supply. Figure 1 shows the power supply.
Each inlet requires a dedicated AC power feed and a dedicated customer site circuit breaker. We recommend that you use a dedicated customer site circuit breaker rated for 10 A (100 VAC), or as required by local code.

The router is pluggable type A equipment installed in a restricted-access location. It has a separate protective earthing terminal (sized for SAE 10-32 ground screws) provided on the chassis in addition to the grounding pin of the power supply cord. This separate protective earthing terminal must be permanently connected to earth.
DC Power Supplies
Each DC power supply weighs approximately 3 lb (1.36 kg) and consists of a handle, an ejection latch, a status LED, a grounding point, and a terminal block that provides a single DC input (24, –48, or –60 VDC and return) that requires a dedicated customer site circuit breaker. We recommend that you provide at least 40 A @ 24 VDC and use a facility circuit breaker. Figure 2 shows the power supply.

Power Supply LEDs
One LED labeled PS STATUS indicates the status of the power supply. Table 1 describes the system LED in more detail.
Label |
Color |
State |
Description |
---|---|---|---|
PS STATUS |
Green |
On steadily |
Power supply is functioning normally, and input voltage is within allowable operating range. |
Yellow |
On steadily |
Primary OTP |
|
Blinking |
Secondary OTP |
||
Red |
On steadily |
Power supply is receiving input voltage below the allowable operating range, but the redundant power supply is functioning normally. |
|
— |
Off |
Power supply is receiving input voltage below the allowable operating range and is not part of a redundant configuration. |
See Also
MX104 Power Consumption
The MX104 router supports installation of up to two AC or DC power supplies in slots labeled on the front of the router.
Table 2 lists the power consumed by the MX104 router.
The power consumption values are measured from the power source and are based on systems that contain redundant power supplies, redundant Routing Engines, a fan tray, and are fully loaded with MICs.
Description |
Value |
---|---|
Power consumed by the AC router (typical) |
600 W |
Power consumed by the DC router (typical) |
625 W |
Power consumed by the AC router without MICs (typical) |
325 W |
Power consumed by the DC router without MICs (typical) |
350 W |
See Also
MX104 AC Power Specifications
Table 3 lists the AC power electrical specifications.
Item |
Specification |
---|---|
Power Supplies | |
AC input voltage |
Operating range: 100 to 240 VAC |
AC input line frequency |
50 to 60 Hz (nominal) |
AC input current rating |
10 A maximum per inlet at 100 VAC |
Efficiency |
91% @ 800 W@ 230 V |
Maximum AC power supply output power |
800 W |
System | |
Maximum output power |
800 W |
We recommend that you use a facility circuit breaker rated for 10 A maximum per inlet at 100 VAC to 240 VAC. Doing so enables you to operate the router in any configuration without upgrading the power infrastructure, and allows the router to function at full capacity using multiple power supplies.
See Also
MX104 AC Power Cord Specifications
Each AC power supply has a single AC appliance inlet that requires a dedicated AC power feed. Most sites distribute power through a main conduit that leads to frame-mounted power distribution panels, one of which can be located at the top of the rack that houses the router. An AC power cord connects each power supply to the power distribution panel.
You can order detachable AC power cords, each approximately 8 ft (2.5 m) long that supply AC power to the router. The C15 appliance coupler at the socket end of the cord, as described by International Electrotechnical Commission (IEC) standard 60320, inserts into the AC appliance inlet coupler. The plug end of the power cord fits into the power source receptacle that is standard for your geographic location.
Table 4 provides specifications on the AC power cord provided for each country or region.
Country |
Model Number |
Electrical Specification |
Plug Type |
Design Standard |
---|---|---|---|---|
Argentina |
CBL-PWR-C15M-HITEMP-AR |
250 VAC, 10 A, 50 Hz |
RA/3 |
IRAM 2073 |
Australia |
CBL-PWR-C15M-HITEMP-AU |
250 VAC, 10 A, 50 Hz |
SAA/3 |
AS/NZZS 3112-2000 |
Brazil |
CBL-PWR-C15M-HITEMP-BR |
250 VAC, 10 A, 50 Hz |
BR/3 |
NBR 14136 |
China |
CBL-PWR-C15M-HITEMP-CH |
250 VAC, 10 A, 50 Hz |
PRC/3 |
GB2099, GB1002 |
Europe (except Italy, Switzerland, and United Kingdom) |
CBL-PWR-C15M-HITEMP-EU |
250 VAC, 10 A, 50 Hz |
VIIG |
CEE (7) VII |
India |
CBL-PWR-C15M-HITEMP-IN |
250 VAC, 10 A, 50 Hz |
ZA/3 |
SABS 164/1:1992 |
Israel |
CBL-PWR-C15M-HITEMP-IL |
250 VAC, 10 A, 50 Hz |
IL/3G |
SI 32 |
Italy |
CBL-PWR-C15M-HITEMP-IT |
250 VAC, 10 A, 50 Hz |
I/3G |
CEI 23–16 |
Japan |
CBL-PWR-C15M-HITEMP-JP |
125 VAC, 15 A, 50 Hz or 60 Hz |
498GJ |
JIS 8303 |
Korea |
CBL-PWR-C15M-HITEMP-KR |
250 VAC, 10 A, 50 Hz |
VIIG |
CEE (7) VII |
South Africa |
CBL-PWR-C15M-HITEMP-SA |
250 VAC, 10 A, 50 Hz |
ZA/3 |
SABS 164/1:1992 |
Switzerland |
CBL-PWR-C15M-HITEMP-SZ |
250 VAC, 10 A, 50 Hz |
12G |
SEV 1011 / 6534-2 |
North America |
CBL-PWR-C15M-HITEMP-US |
125 VAC, 13 A, 60 Hz |
498G |
NEMA 5-15 |
United Kingdom |
CBL-PWR-C15M-HITEMP-UK |
250 VAC, 10 A, 50 Hz |
BS89/13 |
BS 1363/A |
The attached power cable is only for this product. Do not use the cable for another product. Translation in Japanese follows:

In North America, AC power cords must not exceed approximately 14.75 ft (4.5 m) in length, to comply with National Electrical Code (NEC) Sections 400-8 (NFPA 75, 5-2.2) and 210-52, and Canadian Electrical Code (CEC) Section 4-010(3). You can order AC power cords that are in compliance.
Power cords and cables must not block access to device components or drape where people could trip on them.
- Use power cords rated up to 149° F (65° C) for ambient temperatures up to 140° F (60° C).
- The supported power cord temperature ranges from -20°C to +90°C (for Japan), and from -20°C to +65°C (for China).
See Also
MX104 DC Power Specifications
The MX104 power supply contains DC power terminals to connect power to the router and supports the specifications shown in Table 5.
Item |
Specification |
---|---|
Power Supplies | |
DC input voltages |
|
DC input currents |
|
Maximum power supply output |
800 W |
System | |
Maximum output power |
800 W |
Each DC power supply has a single DC input (24, –48, or –60 VDC and return) that requires a dedicated circuit breaker. We recommend that you use a facility circuit breaker rated for 40 A @ 24 VDC. Doing so enables you to operate the router in any configuration without upgrading the power infrastructure, and allows the router to function at full capacity using multiple power supplies.
See Also
MX104 DC Power Cable and Lug Specifications
DC Power Cable Lug Specifications
Use cable lugs with the specifications shown in Figure 3 to attach each DC power cable to the DC power supply.

Before you install the router, a licensed electrician must attach a cable lug to the grounding and power cables that you supply. A cable with an incorrectly attached lug can damage the router.
DC Power Cable Specifications
You must supply two DC power cables for each DC power supply that meet the following specifications: 14-AWG (2.08 mm2), minimum 90° C wire, or as required by the local code.