MX10003 Power Planning

Calculating Power Requirements for MX10003 Router

Use the information in this topic to determine the power consumption for your router and plan the amount of power you need to provide to the router.

Power Requirements for MX10003 Components

Table 1 lists the power requirements for various hardware components when the router is operating under typical and maximum voltage conditions.

Table 1: Power Requirements for MX10003 Components

Component

Power Requirement at 25° C (Watts; Typical)

Power Requirement at 55° C (Watts; Maximum)

JNP-MIC1 (MIC)

80 W

85 W

JNP-MIC1-MACSEC (MIC)

110 W

120 W

JNP10003-LC2103 (MPC)

660 W

715 W

JNP10003-LC2103-V2 (MPC)

665 W

725 W

JNP10003-RE1 (RCB)

58 W

65 W

JNP-FAN-3RU (Fan module)

20 W

95 W

Calculating Power Consumption for Your Configuration

These examples use generalized values per MIC. For exact MIC power requirements, see the MX Series Interface Module Reference.

The following calculations show the typical power consumption (at 25° C) for modular routers :

  • Fully loaded AC-powered router with four fan modules, two MPCs, two JNP-MIC1 MICs, and two RCBs :

  • Fully loaded AC-powered router with four fan modules, two MPCs, two JNP-MIC1-MACSEC MICs, and two RCBs:

The following calculations show the maximum power consumption (at 55° C) for modularrouters :

  • Fully loaded AC-powered router with four fan modules, two MPCs, two JNP-MIC1 MICs, and two RCBs:

  • Fully loaded AC-powered router with four fan modules, two MPC, two JNP-MIC1-MACSEC MICs, and two RCBs:

Table 2 lists the power requirements for the fully configured routers operating under typical voltage conditions.

Table 2: MX10003 Router Power Requirements at Typical Temperature (25° C)

Fixed Chassis Configuration

Power Requirement at 25° C (Watts)

Power Requirement (Watts) with 90% Efficiency

Fully configured chassis running at high activity, with QSFP28 optics and JNP-MIC1

1676 W

1862 W

Fully configured chassis running at high activity, with QSFP28 optics and JNP-MIC1-MACSEC

1736 W

1929 W

Table 3 lists the power requirements for the fully configured routers operating under maximum voltage conditions.

Table 3: MX10003 Router Power Requirements at Maximum Temperature (55° C)

Fixed Chassis Configuration

Power Requirement at 55° C (Watts)

Power Requirement (Watts) with 90% Efficiency

Fully configured chassis running at high activity, with QSFP28 optics and JNP-MIC1

2110 W

2344 W

Fully configured chassis running at high activity, with QSFP28 optics and JNP-MIC1-MACSEC

2180 W

2422 W

Table 4 shows how much power is available with AC and DC power supplies.

Table 4: Total Power

Number of Power Supplies

AC

DC

1

1600 W

1100 W

2

3200 W

2200 W

3

4800 W

3300 W

4

6400 W

4400 W

5

8000 W

5500 W

6

9600 W

6600 W

Calculating System Thermal Output

After you have calculated the power consumption for your configuration, you can use that information to determine the system thermal output (BTUs per hour). To do so, multiply the power consumption in watts by 3.41.

For example, in Table 2 we calculated the power consumption for a fully configured chassis running at high activity, with QSFP28 optics, and JNP-MIC1 at 25° C typical temperature to be 1676 W. Using that information we can calculate the system thermal output for the configuration: