PTX10008 Power Planning for JNP10008-SF Switch Fabric
Use this information to calculate the power consumption for the PTX10008 in a JNP10008-SF switch fabric and plan your configuration’s power requirements.
Power Requirements for PTX10008 Components in a JNP10008-SF Fabric
Table 1 lists the power requirements for the PTX10008 router running the JNP10008-SF switch fabric under typical voltage conditions and optics. For power requirements for chassis configurations, seeCalculate Power Requirements for a PTX10008.
Table 1: Power Consumption JNP10008-SF Fabric Systems
Component | Description | At 25° C | At 55° C |
---|---|---|---|
JNP10008-SF | PTX10008 Switch Interface Board | 170 W | 235 W |
JNP10008-FAN | PTX10008 fan tray | 225 W | 475 W |
JNP10008-FAN2 | PTX10008 enhanced fan tray | 600 W | 1280 W at maximum fan speed |
JNP10K-RE0 | PTX10008 standard Routing Control Board | 50 W | 100 W |
JNP10K-RE1 or JNP10K-RE1-LT | PTX10008 enhanced Routing Control Board | 150 W | 175 W |
PTX10K-LC1101 | PTX10008 30-port QSFP28 line card | 890 W | 1750 W |
PTX10K-LC1102 | PTX10008 36-port QSFP+ line card | 520 W | 675 W |
PTX10K-LC1104 | PTX10008 coherent DWDM line card | 900 W | 1050 W |
PTX10K-LC1105 | PTX10008 30-port MACsec QSFP28 line card | 950 W | 1250 W |
QFX10000-60S-60Q | QFX10000 60-port SFP+ and 6-port QSFP+ line card | 365 W | 465 W |
Calculate Power Requirements for a PTX10008
Use the information in this topic to calculate power requirements of your PTX10008 configuration and the number of power supplies required for different PTX10008 router configurations.
To ensure adequate power and to avoid raising a power alarm, we recommend that you maintain n +1 power supplies in JNP10008-SF configurations at all times. Replace failed power supplies immediately to prevent unexpected failures.
If a new line card is installed in an operational router, power management does not power on the line card if the increased power demand exceeds the total available power, including redundant power. If redundant power is used to power on the line card, a minor alarm is raised, which becomes a major alarm in five minutes if the condition is not corrected.
The calculations in this topic represent the maximum power requirements that you need to budget for your PTX10008 router configuration. The actual power consumption of your router will be less than the calculated results shown here and will vary based on the hardware and software configuration of your router, the amount of traffic passing through the line cards, and environmental variables such as room temperature.
Before you begin these calculations:
Ensure you understand the different router configurations. See PTX10008 Configurations and Upgrade Options.
Ensure that you know the power requirements of different router components. See Power Requirements for PTX10008 Components in a JNP10008-SF Fabric.
This topic describes these tasks:
Calculate the Power Consumption of Your PTX10008 Configuration
Calculate the Number of Power Supplies Required for Your PTX10008 Configuration
Calculate the Power Consumption of Your PTX10008 Configuration
Use the following procedure to determine the maximum power you need to supply to the router. To calculate maximum system power consumption, you first determine the combined maximum internal power requirements of all the router components and then divide this result by the power supply output power.
To calculate maximum system power consumption:
- Determine the maximum power consumption
of the base chassis components (that is, the components other than
the line cards). Use Table 2 if
your router is configured as either the standard base or redundant
configuration.
Table 2: Chassis Power Consumption for Standard Configurations
Chassis Component
Base Configuration
Premium Configuration
JNP10008-FAN
950 W
950 W
JNP10008-FAN2 *
—
—
JNP10K-RE0, or JNP10K-RE1
175 W
350 W
JNP10008-SF
1175 W (5 SIBs)
1410 W (6 SIBs)
Total
2300 W
2710 W
* JNP10008-FAN2 is an optional upgrade that replaces JNP10008-FAN. Use 2,560 W for JNP10008-FAN2 configurations. JNP10008-FAN2 systems require JNP10K-PWR-AC2 or JNP10K-PWR-DC2 power supplies.
- Calculate the maximum internal power
consumption of the entire router by adding in the power requirements
of each line card. See Table 3 for a
chart of the power needed for line cards.
Table 3: Line Card Power Consumption
Line Cards
PTX10K-
LC1101PTX10K-
LC1102PTX10K-
LC1104PTX10K-
LC1105QFX10000-
60S-6Q1
1150 W
675 W
1050 W
1250 W
455 W
2
2300 W
1350 W
2100 W
2500 W
910 W
3
3450 W
2025 W
3150 W
3750 W
1365 W
4
4600 W
2700 W
4200 W
5000 W
1820 W
5
5750 W
3375 W
—
6250 W
2275 W
6
6900 W
4050 W
—
7500 W
2730 W
7
8050 W
4725 W
—
8750 W
3185 W
8
9200 W
5400 W
—
10,000 W
3640 W
Note: * The PTX10K-LC1201-36CD power numbers do not include the power draw of optical transceivers. See the Hardware Compatibility Tool for further information.
Note The PTX10K-LC1104 line card is designed to comply with NEBS regulations on the PTX10008 Packet Transport Router when these routers are used in typical configurations. In a typical configuration, a PTX10008 router supports up to eight line cards, with up to four PTX10K-LC1104 line cards in any of the eight slots.
For example, for a PTX10008 with five PTX10K-LC1102 line cards and three PTX10K-LC1101 line cards, the maximum power consumption is:
= 5 (power consumed by PTX10K-LC1102 in watts) + 3 (power consumed by PTX10K-LC1101 line cards in watts)
= 5 (675 W) + 3 (1150 W)
= (3375 W + 3450 W)
= 6825 W
- Add the power consumption from Step 1 and the total line card consumption
from Step 2.
To continue from the previous example, add the wattage from five PTX10K-LC1102 and three PTX10K-LC1101 cards to a premium configuration.
(6825 W) + (2710 W)
= 9535 W required
Calculate the Number of Power Supplies Required for Your PTX10008 Configuration
Use this procedure to calculate the number of power supplies required by your router configuration. The minimum power configuration for PTX10008 routers is three power supplies. However, using the calculated minimum power configuration does not prevent the system from raising a power alarm. If you are running the router in a JNP10008-SF switch fabric configuration, you must configure your router for n+1 power supplies to ensure you do not log power alarms.
To calculate the number of power supplies required for your minimum router configuration:
- Determine the power available from the power supplies. Table 4 shows the power available for
installed power supplies.
Note DC systems are supported only in the redundant configuration.
Table 4: Total Power Available
Power Supply Module Models
With Three Power Supplies
With Four Power Supplies
With Five Power Supplies
JNP10K-PWR-AC
8,100 W
10,800 W
13,500 W
JNP10K-PWR-AC2 dual feed, high power (30-A) setting
16,500 W
22,000 W
27,500 W
JNP10K-PWR-AC2 single feed, high power (30-A) setting
15,000 W
20,000 W
25,000 W
JNP10K-PWR-AC2, dual feed, low power (20-A) setting
9,000 W
12,000 W
15,000 W
JNP10K-PWR-AC2, single feed, low power (20-A) setting
8,100 W
10,800 W
13,500 W
JNP10K-PWR-DC
7,500 W
10,000 W
12,500 W
JNP10K-PWR-DC2 dual feed, high power (80-A) setting
16,500 W
22,000 W
27,500 W
JNP10K-PWR-DC2 dual feed, low power (60-A) setting
13,200 W
17,600 W
22,000 W
JNP10K-PWR-DC2 single feed, high power (80-A) setting
8,250 W
11,000 W
13,750 W
JNP10K-PWR-DC2 single feed, low power (60-A) setting
6,600 W
8,800 W
11,000 W
Note The HVAC/HVDC power supply, JNP10K-PWR-AC2, has a set of DIP switches on the faceplate that allows you to configure the power supply for either high power (30 A) or low power (20 A) input mode. If any JNP10K-PWR-AC2 power supply is set to 20 A, then the power budget for all power supplies installed in the system becomes 20 A, regardless of whether other power supplies are set at 30 A. This design helps prevent overloading of the power supply that is set to 20 A. See Table 5 for details about setting the DIP switches and available power.
Table 5: Power Input and Output Voltages for JNP10K-PWR-AC2 Power Supplies
INP0 (Switch 1)
INP1 (Switch 2)
H/L (High Input 30 A/
Low Input 20A)Output Power
On
On
On (30 A)
5500 W
On
On
Off (20 A)
3000 W
On
Off
On (30 A)
5000 W
Off
On
On (30 A)
5000 W
On
Off
Off (20 A)
2700 W
Off
On
Off (20 A)
2700 W
- Determine the total power required for your configuration
with line cards installed. The total power available to the chassis
is calculated by dividing the wattage needed by the power rating,
and then rounding up.
In the previous examples, we calculated that a premium PTX10008 AC system would require 9535 W with five PTX10K-LC1102 and three PTX10K-LC1101 line cards. In this example, we calculate the total power available for the 2700 W JNP10K-PWR-AC power supplies:
= (9535 W) / (2700 W)
= 3.5
Round up the result to 4 AC power supplies to determine the minimum power level.
Caution The minimum power level does not prevent the system from raising a power alarm. Add an additional power supply for redundancy (n+1) to ensure you have covered the maximum power budget for your specific configuration.
In our example, a basic configuration (3 power supplies, standard) would require two additional power supplies, one for the minimum power level and second as the redundant power supply. In a redundant AC system (6 power supplies, standard), the system would have sufficient power supplies for both minimum and n+1 redundancy.
- Calculate how much power the power supplies need. To determine
the power required, multiply the number of power supplies by the power
supply wattage and divide by the efficiency of the power supply. The
efficiency rate accounts for the loss of energy within the power supply
and is 89 percent for PTX10008 power supplies.
For example, if you have an AC system with four power supplies:
= 4 (2700 W) / (efficiency rating)
= (10800 W) / (0.89)
= 12135 W
JNP10K-PWR-AC Power Specifications
PTX10008 and PTX10016 redundant-configuration routers can use either AC or DC power supplies; base-configuration routers are AC only. You can run the JNP10K-PWR-AC power supply only in JNP10008-SF fabric systems.
Table 6 lists the power specifications for the AC power supply (JNP10K-PWR-AC) used in a PTX10008 or PTX10016 chassis.
Table 6: Power Specifications for a JNP10K-PWR-AC Power Supply
Item | Specifications |
---|---|
AC input voltage | Operating range: 200–240 VAC |
AC input line frequency | 50–60 Hz |
AC input current rating | 16 A |
AC output power | 2700 W |
Use a 2-pole circuit breaker rated at 25 A in the building installation and the system, or as per local electrical code.
Table 7 shows the physical specifications for an AC power supply.
Table 7: Physical Specifications for a JNP10K-PWR-AC Power Supply
Specification | Value |
---|---|
Height | 3.5 in. (8.89 cm) |
Width | 3.6 in. (9.14 cm) |
Depth | 14.4 in. (36.58 cm) |
Weight | 6.8 lb (3.08 kg) |
JNP10K-PWR-AC2 Power Specifications
The JNP10K-PWR-AC2 power supply supports AC, HVAC, and HVDC. You can run JNP10K-PWR-AC2 power supplies in either a JNP10008-SF or a JNP10008-SF3 system. If you are upgrading a JNP10008-SF system to use JNP10K-PWR-AC2 power supplies, also upgrade your fans and fan tray controllers to ensure the proper airflow. JNP10K-PWR-AC2 power supplies require JNP10008-FAN2 and JNP10008-FTC2 cooling systems.
Table 8 lists the power specifications for the AC power supply (JNP10K-PWR-AC2) used in a PTX10008 or PTX10016 chassis.
Table 8: Power Specifications for a JNP10K-PWR-AC2 Power Supply
Item | Specifications |
---|---|
AC input voltage | 180–305 VAC |
DC input voltage | 190–410 VDC |
Input current rating | 28.5 A |
DC output power | 5500 W with dual feed and 5000 W with single feed |
Table 9 shows the physical specifications for a JNP10K-PWR-AC2 power supply.
Table 9: Physical Specifications for a JNP10K-PWR-AC2 Power Supply
Specification | Value |
---|---|
Height | 3.5 in. (8.89 cm) |
Width | 3.6 in. (9.14 cm) |
Depth | 15.1 in. (38.35 cm) |
Weight | 11.4 lb (5.17 kg) |
PTX10008 Power Cables Specifications
Most sites distribute power through a main conduit that leads to frame-mounted power distribution panels, one of which can be located at the top of the rack that houses the router. An AC power cord connects each power supply to the power distribution panel.
In North America, AC power cords must not exceed 15 feet (approximately 4.5 meters) in length, to comply with National Electrical Code (NEC) Sections 400-8 (NFPA 75, 5-2.2) and 210-52 and Canadian Electrical Code (CEC) Section 4-010(3). The cords shipped with the router to North America and Canada are in compliance.
PTX10008 AC, high-voltage alternating current (HVAC), and high-voltage direct current (HVDC) power supplies have specific cord requirements. Use the following sections to determine the cable requirements based on the model of your power supply and any mode settings:
For JNP10K-PWR-AC, see JNP10K-PWR-AC Power Cable Specifications
For JNP10K-PWR-AC2 with 20-A input, see JNP10K-PWR-AC2 Power Cable Specifications
For JNP10K-PWR-AC2 with 30-A input, see JNP10K-PWR-AC2 Power Cable Specifications for 30-A Input
JNP10K-PWR-AC Power Cable Specifications
Each JNP10K-PWR-AC power supply has two independent 16 A rated AC inlets on the faceplate.
Each detachable AC power cord is 8 feet (approximately 2.5 meters) long. The coupler end of the appliancecord inserts into the AC appliance inlet on the faceplate of the AC power supply. The coupler type is C19 as described by the International Electrotechnical Commission (IEC) standard 60320. The plug end of the power cord fits into the power source outlet that is standard for your geographical location.
Table 10 lists the AC power cord specifications for JNP10K-PWR-AC for various countries and regions.
Table 10: AC Power Cord Specifications for JNP10K-PWR-AC Power Supplies
Country/Region | Electrical Specifications | Plug Standards | Juniper Model Number | Graphic |
---|---|---|---|---|
Argentina | 250 VAC, 16 A, 50 Hz | IRAM Type RA/3/20 | CBL-EX-PWR-C19-AR | ![]() |
Australia | 250 VAC, 15 A, 50 Hz | AS/NZS 3112 Type SAA/3/15 | CBL-EX-PWR-C19-AU | ![]() |
Brazil | 250 VAC, 16 A, 50 Hz | NBR 14136: 2002 Type BR/3/20 | CBL-EX-PWR-C19-BR | ![]() |
China | 250 VAC, 16 A, 50 Hz | GB 1002 Type PRC/3/16 | CBL-EX-PWR-C19-CH | ![]() |
Europe (except Italy, Switzerland, and United Kingdom) | 250 VAC, 16 A, 50 Hz | CEE (7) VII Type VIIG | CBL-EX-PWR-C19-EU | ![]() |
India | 250 AC, 16 A, 50 Hz | SABS 164/1:1992 Type ZA/3 | CBL-EX-PWR-C19-SA | ![]() |
Israel | 250 AC, 16 A, 50 Hz | SI 32/1971 Type IL/3 | CBL-EX-PWR-C19-IL | ![]() |
Italy | 250 VAC, 16 A, 50 Hz | CEI 23-16 Type I/3/16 | CBL-EX-PWR-C19-IT | ![]() |
Japan | 250 VAC, 16 A, 60 Hz | NEMA 6–20 Type N6/20 | CBL-EX-PWR-C19-JP (default) | ![]() |
250 VAC, 16 A, 60 Hz | NEMA L6–20P Type NEMA Locking | CBL-EX-PWR-C19-JPL | ![]() | |
Korea | 250 VAC, 16 A, 50 Hz | CEE (7) VII Type VIIG | CBL-EX-PWR-C19-KR | ![]() |
North America | 250 VAC, 16 A, 60 Hz | NEMA 6–20 Type N6/20 | CBL-EX-PWR-C19-US (default) | ![]() |
250 VAC, 16 A, 60 Hz | NEMA L6–20P Type NEMA Locking | CBL-EX-PWR-C19-USL | ![]() | |
South Africa | 250 VAC, 16 A, 50 Hz | SABS 164/1:1992 Type ZA/3 | CBL-EX-PWR-C19-SA | ![]() |
Switzerland | 250 VAC, 16 A, 50 Hz | SEV 5934/2 Type 23G | CBL-EX-PWR-C19-SZ | ![]() |
United Kingdom | 250 VAC, 13 A, 50 Hz | BS 1363/A Type BS89/13 | CBL-EX-PWR-C19-UK | ![]() |
Worldwide (except Japan) | 250 VAC, 16 A, 50 Hz | EN 60320-2-2/1 | CBL-EX-PWR-C19-C20 | ![]() |
JNP10K-PWR-AC2 Power Cable Specifications
The JNP10K-PWR-AC2 power supply operates in two modes:
30-A input with 5500-W output
JNP10K-PWR-AC2 Power Cable Specifications for 30-A Input shows cables and connectors for 30-A input.
20-A input with 3000-W output
Table 11 shows cables appropriate for 20-A input.
Do not run JNP10K-PWR-AC2 power supplies using 16-A or 20-A cables if connected to 30-A input.
You can prevent AC power cables from being exposed to hot air exhaust by always routing the power cables away from the fan trays and power supplies.
It is important to connect both input feeds of the JNP10K-PWR-AC2 power supply to AC mains before loading the system with power.
Table 11: JNP10K-PWR-AC2 Power Cable Specifications for 20-A Input
Locale | Cord Set Rating | Plug Standards | Spare Juniper Model Number | Graphic |
---|---|---|---|---|
Argentina | 16 A, 250 VAC | IRAM 2073 Type RA/3 | CBL-JNP-SG4-AR | ![]() |
Australia and New Zealand | 15 A, 250 VAC | AS/NZS 3112 | CBL-JNP-SG4-AU | ![]() |
Brazil | 16 A, 250 VAC | NBR 14136 Type BR/3 | CBL-JNP-SG4-BR | ![]() |
China | 16 A, 250 VAC | GB2099 | CBL-JNP-SG4-CH | ![]() |
Europe (except Italy, Switzerland, and United Kingdom) | 20 A, 250 VAC | CEE 7/7 | CBL-JNP-SG4-EU | ![]() |
Great Britain | 13 A, 250 VAC, | BS1363 | CBL-JNP-SG4-UK | ![]() |
India | 16 A, 250 VAC | SANS 164/1 | CBL-JNP-SG4-SA | ![]() |
Israel | 16 A, RA, 250 VAC | SI 32/1971 Type IL/3C | CBL-JNP-SG4-IL | ![]() |
Italy | 16 A, 250 VAC | CEI 23-50 | CBL-JNP-SG4-IT | ![]() |
North America | 20 A, 250 VAC | 3-5958P4 to IEC 60320 C20 | CBL-JNP-SG4-C20 | ![]() |
16 A, 250 VAC | Locking NEMA L6-20P | CBL-JNP-SG4-US-L | ![]() | |
NEMA 6-20P | CBL-JNP-SG4-US | ![]() | ||
15 A, 277 V | NEMA I7-20P | CBL-JNP-SG4-HVAC | ![]() | |
South Africa | 16 A, 250 VAC | SANS 164/1 | CBL-JNP-SG4-SA | ![]() |
Switzerland | 16 A, 250 VAC | CEI 23-50 | CBL-JNP-SG4-SZ | ![]() |
JNP10K-PWR-AC2 Power Cable Specifications for 30-A Input
The JNP10K-PWR-AC2 HVAC or HVDC power supply requires a high current cable assembly when set for 30-A input. One end of the cable has an Anderson APP-400 connector, while the other end of the cable is bare wire. See Figure 1 and Table 12. These cables are separately orderable and are not shipped automatically with JNP10K-PWR-AC2 orders. An example of the right-angle cable and connector is shown in Figure 3.
For connection to AC systems, Juniper provides a cable with either a NEMA 30-A connector (Figure 1) or an IEC 330P6W connector (Figure 2).


Table 12: 30-A Cabling Options
Locale | Cord Set Rating | Plug Standards | Connector | Spare Juniper Model Number | |
---|---|---|---|---|---|
HVAC/HVDC power cord | Any | 30-A, 400 VAC | UL 950 and IEC 60950 | Anderson/straight to bare wire | CBL-PWR2-BARE |
30-A, 400 VAC | UL 950 and IEC 60950 | Anderson/right-angle to bare wire | CBL-PWR2-BARE-RA | ||
AC power cord | Continental Europe | 30-A 250 VAC | UL 950 and IEC332P6 | Anderson/right-angle to IEC 332P6 | CBL-PWR2-332P6W-RA |
30-A 250 VAC | UL 950 and IEC332P6 | Anderson/straight to IEC332P6 | CBL-PWR2-332P6W | ||
North America | 30-A 240 VAC | IEC330P6 | Anderson/right-angle to IEC 330P6 | CBL-PWR2-330P6W-RA | |
30-A 240 VAC | IEC330P6 | Anderson/straight to IEC 330P6 | CBL-PWR2-330P6W | ||
30-A 250 VAC | UL 498, CSA | Anderson/right-angle to L6-30P (NEMA-30A) | CBL-PWR2-L6-30P-RA | ||
30-A 250 VAC | UL 498, IEC5958P4 | Anderson/straight to L6-30P (NEMA-30A) | CBL-PWR2-L6-30P |

1 — Black wire – “+” or “-“ for HVDC
and “Hot or neutral” for AC | 3 — White wire – “+” or “-“ for HVDC
and “Hot or neutral” for AC |
2 — Green wire - Ground |
JNP10K-PWR-DC Power Specifications
The DC power supply (JNP10K-PWR-DC) is supported only in PTX10008-SF or PTX10016-SF fabric systems. Table 13 lists the power specifications for the JNP10K-PWR-DC power supply used in a PTX10008 and PTX10016 modular chassis.
Table 13: Power Specifications for the JNP10K-PWR-DC Power Supply
Item | Specifications |
---|---|
DC input voltage |
|
DC input current rating | 60 A maximum at nominal operating voltage (–48 VDC) for each input terminal |
Output power | 2500 W |
Table 14 shows the physical specifications for a JNP10K-PWR-DC power supply.
Table 14: Physical Specifications of a JNP10K-PWR-DC Power Supply
Specification | Value |
---|---|
Height | 3.5 in. (8.89 cm) |
Width | 3.6 in. (9.14 cm) |
Depth | 14.4 in. (36.58 cm) |
Weight | 6 lb (2.72 kg) |
JNP10K-PWR-DC2 Power Specifications
If you are upgrading a JNP10008-SF system to use JNP10K-PWR-DC2 power supplies, also upgrade your fans and fan tray controllers to ensure the proper airflow. JNP10K-PWR-DC2 power supplies require JNP10008-FAN2 and JNP10008-FTC2 cooling systems.Table 15 lists the power specifications for the dual DC power supply used in a PTX10008 chassis.
Table 15: Power Specifications for the JNP10K-PWR-DC2 Power Supply
Item | Specifications |
---|---|
DC input voltage |
|
DC input current rating |
|
Output power | 2200 W for low input (60-A) single feed 4400 W for low input (60-A) dual feed 2750 W for high input (80-A) single feed 5500 W for high input (80-A) dual feed |
Table 16 shows the physical specifications for a JNP10K-PWR-DC2 power supply.
Table 16: Physical Specifications of a JNP10K-PWR-DC2 Power Supply
Specification | Value |
---|---|
Height | 3.5 in. (8.89 cm) |
Width | 3.6 in. (1.63 cm) |
Depth | 16.05 in. (40.77 cm) |
Weight | 8.1 lb (3.67 kg) |