PTX10003 Power System

 

The PTX10003 is powered by 3000-W redundant AC/HDVC or DC power supplies that are pre-installed at the factory. The PTX10003-160C is powered by four power supplies for 2+2 redundancy. The PTX10003-80C is powered by two power supplies for 1 + 1 redundancy. The power supplies are hot-removable and hot-insertable. If one power supply fails, you can replace it without powering off or disrupting the routing function. The other power supply balances the electrical load without interruption. Each power supply has two outputs: 12 V and 12 V standby. Two counter-rotating fans in each power supply provide front to back cooling. The input voltages are as follows:

  • AC input voltage range: 200—277 V/50—60 Hz

  • DC input voltage range: —40 VDC Min, —72 VDC maximum

Caution

Do not mix AC/HVDC and DC power supplies in the same chassis.

PTX10003 AC/HVDC Power Supply Description

The input power to the AC/HVDC power supplies can be AC power or HVDC power. The power supplies automatically detect whether there is AC or HVDC input voltage and manage the power accordingly. AC power can be 180—305 VAC input voltage and HVDC power can be 190—400 VDC input voltage. Each 3000- W AC/HVDC power supply module has a single AC or HVDC input and provides 12 V power to the system.

Figure 1 shows the location of the AC/HVDC power supplies on the PTX10003-160C FRU panel, and Figure 2 shows the location of the AC/HVDC power supplies on the PTX10003-80C FRU panel.

Figure 1: PTX10003-160C FRU Panel (AC Power Supplies Installed)
PTX10003-160C FRU Panel (AC Power
Supplies Installed)
  1
Chassis grounding points (2)
  3
ESD grounding point
  2
AC/HVDC Power supplies (4)
  4
Fan modules (5)
Figure 2: PTX10003-80C FRU Panel (AC/HVDC Power Supplies Installed)
PTX10003-80C FRU Panel (AC/HVDC
Power Supplies Installed)
  1
Chassis grounding points (2)
  3
ESD grounding point
  2
AC/HVDC power supplies (2)
  4
Fan modules (3)

Figure 3 shows the AC/HVDC power supply components.

Figure 3: PTX10003 AC/HVDC Power Supply
PTX10003 AC/HVDC Power Supply
  1
Male power connector
  3
Ejector lever
  2
Status LED
  4
Orange handle
Caution

To avoid electrical injury, carefully follow the instructions in Maintaining the PTX10003 Power Supplies.

PTX10003 AC/HVDC Power Supply LED

Each PTX10003 AC/HVDC power supply has a status LED on the power supply faceplate. Refer to Figure 4.

Figure 4: PTX10003 AC/HVDC Power Supply LED
PTX10003 AC/HVDC Power Supply
LED
  1
Power supply LED
 

The PTX10003 AC/HVDC power supply uses an amber and green bi—color LED to indicate the operating state. Refer to Table 1.

Table 1: PTX10003 AC/HVDC Power Supply States

State

Green

Amber

The power supply is on and operating properly

On

Off

One or both power supplies do not have AC power

Off

Off

The power supply shut down due to a critical event. Possible causes: high temperature, high power, high current, fan failure

Off

On

The power supply is operating but there are warning events. Possible conditions: high temp (inlet temperature is greater than 53 degrees or a hot spot temperature is greater than 95 degrees), high power, high current, slow fan (less than 1200 rpm)

Off

Blinking amber

There is no input power but the power supply module from another slot in the same system is on with 12 VSB active

Blinking

Off

The AC power cord is unplugged

Off

On

You can get additional information about the status of the power modules using the show chassis power command and the show chassis power detail command. Here’s some examples of the CLI output:

PTX10003-160C Power with Four AC/HVDC Power Supplies

user@device> show chassis power
user@device> show chassis power detail

PTX10003-80C with Two AC/HVDC Power Supplies

user@device> show chassis power
user@device> show chassis power detail

PTX10003 AC/HVDC Power Specifications

The PTX10003 operates within the AC/HVDC input voltage range listed in Table 2.

Table 2: PTX10003 AC/HVDC Power Specifications

Parameter

Minimum

Rated

Maximum

Input voltage (AC)

180 VAC

200—277 VAC

305 VAC

Input voltage (HVDC)

190 VDC

240—380 VDC

400 VDC

AC input line frequency

47 Hz

50—60 Hz

63 Hz

PTX10003 AC Power Cord Specifications

Detachable AC power cords are shipped with the chassis if you include them as part of your order. The plug at the male end of the power cord fits into the power source outlet that is standard for your geographical location.

Note

In North America, AC power cords must not exceed 14.75 feet (approximately 4.5 meters) in length, to comply with National Electrical Code (NEC) Sections 400-8 (NFPA 75, 5-2.2) and 210-52 and Canadian Electrical Code (CEC) Section 4-010(3). The cords that can be ordered for the PTX10003 are in compliance.

Table 3 lists AC power cord specifications provided for each country or region.

Table 3: PTX10003 Power Cord Specifications

Locale

Cord Set Rating

Plug Standards

Spare Juniper Model Number

Graphic

Argentina

16 A, 250 VAC

IRAM 2073 Type RA/3

CBL-JNP-SG4-AR

Australia and New Zealand

15 A, 250  VAC

AS/NZS 4417

CBL-JNP-SG4-AU

Brazil

16 A, 250 VAC

NBR 14136 Type BR/3

CBL-JNP-SG4-BR

China

16 A, 250 VAC

GB2099

CBL-JNP-SG4-CH

Europe (except Italy, Switzerland, and United Kingdom)

20 A, 250 VAC

CEE 7/7 STRAIGHT

CBL-JNP-SG4-EU

Great Britain

13 A, 250 VAC,

BS1363

CBL-JNP-SG4-UK

India

16 A, 250 VAC

SANS 164/1

CBL-JNP-SG4-SA

Israel

16 A, RA, 250 VAC

SI 32/1971 Type IL/3G

CBL-JNP-SG4-IL

Italy

16 A, 250 VAC

CEI 23-16

CBL-JNP-SG4-IT

North America

20 A, 250 VAC

C20 to Anderson 3-5958p4

CBL-JNP-SG4-C20

North America

16 A, 250 VAC

Locking NEMA L6-20P

CBL-JNP-SG4-US-L

North America

16 A, 250 VAC

NEMA 6-20P

CBL-JNP-SG4-US

North America

15 A, 277 V

NEMA I7-20P

CBL-JNP-SG4-HVAC

North America

20 A, 250 V

IEC 320P6W

CG_CBL-APP-400-02

South Africa

16 A, 250 VAC

SANS 164/1

CBL-JNP-SG4-SA

Switzerland

16 A, 250 VAC

CEI 23-50

CBL-JNP-SG4-SZ

Table 4: PTX10003 HVDC Cable Specifications (Bare Wire)

Locale

Cord Set Rating

Spare Juniper Model Number

HVDC power cord

16 A, 400 VAC

CBL-PWR2-BARE

Note

The insulation color for wires in the HVDC cables are color coded. Green is ground, black is line, and white is neutral. For HVDC, the black and white wires are not polarity-sensitive. The black wire can be positive (+) or neutral (–) and the white wire can be positive (+) or negative (–).

PTX10003 DC Power Supply Description

The PTX10003 DC power supplies are hot-removable and hot-insertable FRUs. Each 3000 W power supply has a single DC input and provides 12 VDC output with a standby voltage of 12 VDC.

Figure 5 shows the location of the DC power supplies on the PTX10003-160C FRU panel, and Figure 6shows the location of the DC power supplies on the PTX10003-80C FRU panel.

Figure 5: PTX10003-160C FRU Panel (DC Power Supplies Installed)
PTX10003-160C FRU Panel (DC
Power Supplies Installed)
  1
Chassis grounding points (2)
  3
ESD grounding point
  2
DC power supplies (4)
  4
Fan modules (5)
Figure 6: PTX10003-80C FRU Panel (DC Power Supplies Installed)
PTX10003-80C FRU Panel
(DC Power Supplies Installed)
  1
Chassis grounding points (2)
  3
ESD grounding point
  2
DC power supplies (2)
  4
Fan modules (3)

Figure 7 shows the DC power supply components.

Caution

Do not mix AC/HVDC and DC power supplies in the same chassis.

Figure 7: PTX10003 DC Power Supply
PTX10003 DC Power Supply
  1
Ejector lever
  4
Handle
  2
Status LED
  5
Terminal block cover
  3
DC input current selector (DIP switch)
 
Caution

To avoid electrical injury, carefully follow instructions in Maintaining the PTX10003 Power Supplies.

PTX10003 DC Power Supply LED

Each PTX10003 DC power supply has a status LED on the power supply faceplate. Refer to Figure 8.

Figure 8: PTX10003 DC Power Supply Status LED
PTX10003 DC Power Supply
Status LED
  1
Power supply status LED
 

Use Table 5 to interpret the state of the power supply status LED.

Table 5: PTX10003 DC Power Supply LED

LED Color

Power Supply State

Solid green

The power supply is on and in the OK state.

Off

One or both power supplies do not have DC power

Blinking green

The power supply is in cold redundant state

Solid amber

The DC power cord is unplugged but the second power supply still has DC power

Blinking amber

The power supply is operating but there are warning events. Possible causes: high temp, high power, high current, slow fan

Solid amber

The power supply shut down due to a critical event. Possible causes: high temperature, high power, high current, slow fan

Blinking green

The power supply is uploading firmware

PTX10003 DC Input Current Selector (DIP Switch)

The PTX10003 DC power supply can operate with an input current of 80 A or 60 A. You select the input rating by moving the DC input current selector (DIP switch) to the desired setting. Refer to Figure 7 for the location of the DC input current selector (DIP switch). If you select 60 A, the power supply limits the output power so that the input current does not exceed 60 A under normal steady-state operation. If you select 80 A, the power supply limits the output power so that the input current does not exceed 80 A.

Caution

The PTX10003 DC power supply does not support a 60 A power source in Junos OS Evolved software release 19.1. When installing the PTX10003 DC power supply, be sure you set the DC input current selector (DIP switch) to 80 A.

For example:

If you select...

Then...

60 A

The power supply limits the output power to 2200 W at 40 V input and linearly increases the output power if the input voltage increases. The power supply provides 3000 W output power for input voltage greater than 55 V assuming 92% efficiency.

Caution: The PTX10003 DC power supply does not support a 60 A power source in Junos OS Evolved software release 19.1. When installing the PTX10003 DC power supply, be sure you set the DC input current selector (DIP switch) to 80 A.

80 A

The power supply provides 3000 W output power throughout the input voltage range from 40 VDC to 72 VDC.

PTX10003 DC Power Redundancy

To provide power redundancy for the PTX10003, the power supply modules must be connected to an 80 A power source and the input current selector (DIP switch) on the power supply must be set to 80 A. For the PTX10003-80C, the maximum power budget is 3000 W. For the PTX10003-160C, the maximum output power budget is 4700 W.

Caution

The PTX10003 DC power supply does not support an 60 A power source in Junos OS Evolved software release 19.1. When installing the PTX10003 DC power supply, be sure you set the input current selector to 80 A.

PTX10003 Input DC Voltage Specification

The PTX10003 DC power supply modules operate within the DC input voltage range listed in Table 6.

Note

Depending on the available input source, Juniper recommends that the 48-VDC facility DC source be equipped with a circuit breaker rated at a minimum of 60 A (-48 VDC) or 80 A (-48 VDC), or as required by local code.

Table 6: PTX10003 DC Power Specifications

Input Switch Setting

Minimum Input DC Voltage

Rated Input DC Voltage

MaximumInput DC Voltage

Maximum Input DC Current

Maximum Output Power

60 A

-40 VDC

-48 VDC to -60 VDC

-72 VDC

60 ADC

2200 W

80 A

-40 VDC

-48 VDC to  -60 VDC

-72 VDC

90 ADC

3000 W

PTX10003 DC Power Cables

You must supply the DC power cables that meet the specifications required by the local code, laws, and standards. The insulation color of the wires are color coded. Green is ground, black is line, and white is neutral. The wires are labeled (+) and (–) to indicate their polarity.

Caution

You must ensure that power connections maintain the proper polarity.

Warning

For field-wiring connections, use copper conductors only.

Warning

DC Power cables must not block access to PTX10003 components or drape where people could trip on them.

PTX10003 DC Power Lugs

The accessory box shipped with the PTX10003 includes the cable lugs that attach to the terminal studs of each power supply module. (The cable lug shown in Figure 9 is also used for grounding the chassis.) The cable lugs are dual hole and sized to fit 1/4-20 UNC terminal studs at 15.86-mm (0.625-in.) center line.

Figure 9: DC Power Cable Lugs
DC Power Cable Lugs
Caution

Before you begin to install the PTX10003, a licensed electrician must attach a cable lug to the power cables that you supply. A cable with an incorrectly attached lug can damage the PTX10003.

Viewing Power Statistics

You can get additional information about the status of the power modules using the show chassis power command and show chassis power detail command. Here’s some examples of the CLI output:

PTX10003-160C with Four DC Power Supplies

user@device> show chassis power
user@device> show chassis power detail

PTX10003-80C with two DC Power Supplies

user@device>show chassis power