Optical ILA Site Guidelines and Requirements
Optical ILA Environmental Requirements and Specifications
The optical ILA must be installed in a rack or cabinet. It must be housed in a dry, clean, well-ventilated, and temperature-controlled environment.
Follow these environmental guidelines:
The site must be as dust-free as possible, because dust can clog air intake vents and filters, reducing the efficiency of the optical ILA cooling system.
Maintain ambient airflow for normal optical ILA operation. If the airflow is blocked or restricted, or if the intake air is too warm, the chassis might overheat, leading to the optical ILA temperature monitor shutting down the device to protect the hardware components.
Table 1 provides the required environmental conditions for normal operation of the optical ILA .
Table 1: Optical ILA Environmental Tolerances
Description | Tolerance |
---|---|
Altitude | No performance degradation up to 6000 feet (1828.8 meters). |
Relative humidity | Normal operation ensured in relative humidity range of 5% through 90%, noncondensing.
|
Temperature |
|
Seismic | Designed to comply with Zone 4 earthquake requirements per NEBS GR-63-CORE, Issue 3. |
Install the optical ILA only in restricted-access areas, such as dedicated equipment rooms and equipment closets, in accordance with Articles 110-16, 110-17, and 110-18 of the National Electrical Code, ANSI/NFPA 70.
Optical ILA Clearance Requirements for Airflow and Hardware Maintenance
When planning the site for an optical ILA installation, you must allow sufficient clearance around the installed chassis (see Figure 1).

Follow these guidelines:
For the cooling system to function properly, the airflow around the chassis must be unrestricted. See Optical ILA Cooling System Description for more information about the airflow through the chassis.
If you are mounting an optical ILA in a rack or cabinet with other equipment, ensure that the exhaust from other equipment does not blow into the intake vents of the optical ILA chassis.
You must leave at least 24 in. (61 cm) both in front of and behind the optical ILA. For service personnel to remove and install hardware components, you must leave adequate space at the front and back of the optical ILA. NEBS GR-63 recommends that you allow at least 30 in. (76.2 cm) in front of the rack or cabinet and 24 in. (61 cm) behind the rack or cabinet.
Optical ILA Physical Specifications
Table 2 lists the physical specifications for the optical ILA chassis and components.
Table 2: Physical Specifications for the Optical ILA
Model Numbers | Fans and Power | Height | Width | Depth | Weight |
---|---|---|---|---|---|
PTX-ILA-M-AC | 3 fan modules and 2 AC power supplies installed | 1.72 in. (4.36 cm) | 17.24 in. (43.8 cm) | 9.6 in. (24.4 cm) without handles for fans or power supplies. | With field-replaceable units (FRUs) installed: 11.7 lb (5.30 kg) |
PTX-ILA-M-DC | 3 fan modules and 2 DC power supplies installed | 1.72 in. (4.36 cm) | 17.4 in. (44.19 cm) | 9.8 in. (24.89 cm) without handles for fans or power supplies. | With FRUs installed: 11.8 lb (5.35 kg) |
Optical ILA Rack Requirements
The optical ILA chassis is designed to be installed in two-post or four-post racks.
Rack requirements consist of:
Rack type
Mounting bracket hole spacing
Rack size and strength
Table 3 provides the rack requirements and specifications for the optical ILA.
Table 3: Rack Requirements for the Optical ILA
Rack Requirement | Guidelines |
---|---|
Rack type: two-post or four-post | Use a two-post or four-post rack that provides bracket patterns spaced at 1-U (1.75 in. or 4.45 cm) increments and that meets the size and strength requirements to support the weight. A U is the standard rack unit defined in Cabinets, Racks, Panels, and Associated Equipment (document number EIA-310–D) published by the Electronics Components Industry Association (http://www.ecianow.org/). |
Mounting bracket hole spacing | The holes in the mounting brackets are spaced at 1.25 in. (or 3.17 cm), so that the optical ILA can be mounted in any rack that provides holes spaced at that distance. |
Rack size and strength |
|
Rack connection to building structure |
|
Optical ILA Cabinet Requirements
You can mount optical ILA models in a cabinet that contains a two-post 19-in. or four-post rack as defined in Cabinets, Racks, Panels, and Associated Equipment (document number EIA-310-E) published by the Electronics Components Industry Association (http://www.ecianow.org/).
Cabinet requirements consist of:
Cabinet size and clearance
Cabinet airflow requirements
Table 4 provides the cabinet requirements and specifications for the optical ILA.
Table 4: Cabinet Requirements for the Optical ILA
Cabinet Requirement | Guidelines |
---|---|
Cabinet size and clearance | The minimum cabinet size for accommodating an optical ILA is 18 in. (45.7 cm) deep. Large cabinets improve airflow and reduce the chance of overheating. Note: The DC version of the optical ILA conforms to the ETSI 300 mm cabinets. |
Cabinet airflow requirements | When you mount the optical ILA in a cabinet, ensure that ventilation through the cabinet is sufficient to prevent overheating.
|
Optical Specifications for the Optical ILA
Table 5 provides the optical specifications for the optical ILA.
Table 5: Optical Specifications
Parameter | Configurations | Minimum | Maximum |
---|---|---|---|
Input power range | Loaded system (96 channels) | –15.2 dBm | 9.8 dBm |
Single channel | –35 dBm | –10 dBm | |
Signal output power range | Loaded system (96 channels) | 19.8 dBm | |
Single channel | 0 dBm | ||
Gain range (standard) | Output gain tilt equal to 0 dB | 10 dB | 30 dB |
Gain range (extended) | Output gain tilt not equal to 0 | 30 dB | 35 dB |