Connecting the EX6210 to Power

 

Connect Earth Ground to an EX Series Switch

To ensure proper operation and to meet safety and electromagnetic interference (EMI) requirements, you must connect an EX Series switch to earth ground before you connect power to the switch. You must use the protective earthing terminal on the switch chassis to connect the switch to earth ground (see Figure 2).

You must install the EX Series switch in a restricted–access location and ensure that the chassis is always properly grounded. EX Series switches have a two–hole protective grounding terminal provided on the chassis. See Table 1 for the location of the earthing terminals on various EX Series switches. We recommend that you use the protective grounding terminal as the preferred method for grounding the chassis regardless of the power supply configuration. However, if additional grounding methods are available, you can also use those methods. For example, you can use the grounding wire in the power cord of an AC power supply or use the grounding terminal or lug on a DC power supply. This system was tested to meet or exceed all applicable EMC regulatory requirements with the two-hole protective grounding terminal connected correctly.

Ensure that a licensed electrician has attached an appropriate grounding lug to the grounding cable you supply. Using a grounding cable with an incorrectly attached lug can damage the switch.

Parts and Tools Required for Connecting an EX Series Switch to Earth Ground

Before you begin connecting an EX Series switch to earth ground, ensure you have the parts and tools required for your switch.

Table 1 lists the earthing terminal location, grounding cable and lug specifications, and parts needed for connecting an EX Series switch to earth ground.

Table 1: Parts Required for Connecting an EX Series Switch to Earth Ground

Switch

Earthing Terminal Location

Grounding Cable Requirements

Grounding Lug Specifications

Screws and Washers

Additional Information

EX2200

Rear panel of the chassis

14 AWG (2 mm²), minimum 90° C wire, or as permitted by the local code

Panduit LCC10-14BWL or equivalent—

not provided

  • Two 10-32 x .25 in. screws with #10 split-lock washer—

    not provided

  • Two #10 flat washers—not provided

 

EX2300-C

Rear panel of the chassis

14 AWG (2 mm²), minimum 90° C wire, or as permitted by the local code

Panduit LCC10-14AW-L or equivalent—

not provided

  • Two 10-32 x .25 in. screws with #10 split-lock washer—

    not provided

  • Two #10 flat washers—not provided

 

EX2300

Rear panel of the chassis

  • EX2300 switches except EX2300-24MP and EX2300-48MP models—14 AWG (2 mm²), minimum 90°C wire, or as permitted by the local code

  • EX2300-24MP and EX2300-48MP models—14-10 AWG STR (2.5-6 mm²), 12-10 AWG SOL (4-6 mm²) minimum 90°C wire, or as permitted by the local code—not provided

  • EX2300 switches except EX2300-24MP and EX2300-48MP models—Panduit LCC10-14AW-L or equivalent—not provided

  • EX2300-24MP and EX2300-48MP models—Panduit LCA10-10L or equivalent—not provided

  • EX2300 switches except EX2300-24MP and EX2300-48MP models

    • Two 10-32 x .25 in. screws with #10 split-lock washer—not provided

    • Two #10 flat washers—not provided

  • EX2300-24MP and EX2300-48MP models

    • One Pan Phillips M 4 x 6 mm Nickel plated screw—provided

 

EX3200, EX3300, and EX3400

Rear panel of the chassis

14 AWG (2 mm²), minimum 90° C wire, or as permitted by the local code

Panduit LCC10-14BWL or equivalent—

not provided

  • Two 10-32 x .25 in. screws with #10 split-lock washer—

    not provided

  • Two #10 flat washers—

    not provided

For EX3200 Switches See Special Instructions to Follow Before Connecting Earth Ground to an EX Series Switch.

EX4200, EX4500, and EX4550

Left side of the chassis

14 AWG (2 mm²), minimum 90° C wire, or as permitted by the local code

Panduit LCC10-14BWL or equivalent—

not provided

  • Two 10-32 x .25 in. screws with #10 split-lock washer—

    not provided

  • Two #10 flat washers—

    not provided

See Special Instructions to Follow Before Connecting Earth Ground to an EX Series Switch.

EX6210

Rear panel of the chassis (on lower left side)

The grounding cable must be the same gauge as the power feed cables and as permitted by the local code.

Panduit LCD2-14A-Q or equivalent

—provided

  • Two ¼ -20 x 0.5 in. screws with #¼” split-washer

    —provided

  • Two #¼” flat washers—

    provided

 

EX8208

Left side of the chassis

6 AWG (13.3 mm²), minimum 90° C wire, or as permitted by the local code

Panduit LCD2-14A-Q or equivalent

—provided

  • Two ¼ -20 x 0.5 in. screws with #¼” split-washer

    —provided

  • Two #¼” flat washers—

    provided

 

EX8216

Two earthing terminals:

  • Left side of the chassis

  • Rear panel of the chassis

Note: You must use only one of the two protective earthing terminals.

2 AWG (33.6 mm²), minimum 90° C wire, or as permitted by the local code

Panduit LCD2-14A-Q or equivalent

—provided

  • Two ¼ -20 x 0.5 in. screws with #¼” split-washer

    —provided

  • Two #¼” flat washers—

    provided

 

EX9204, EX9208, and EX9214

Rear panel of the chassis

One 6 AWG (13.3 mm²), minimum 90° C wire, or one that complies with the local code

Thomas& Betts LCN6-14 or equivalent—

provided

  • Two ¼ -20 x 0.5 in. screws with #¼” split-washer—

    provided

  • Two #¼” flat washers—

    provided

See Grounding Cable and Lug Specifications for EX9200 Switches.

EX9251

Rear panel of the chassis

12 AWG (2.5 mm²), minimum 90° C wire, or one that complies with the local code—

not provided

Panduit LCD10-10A-L or equivalent—

not provided

Two 10-32 screws—

provided

See Grounding Cable and Lug Specifications for EX9200 Switches.

EX9253

Right side of the chassis

14-10 AWG (2-5.3 mm²), minimum 90° C wire, or one that complies with the local code—

not provided

Panduit LCD10-14B-L or equivalent—

provided

Two M5 Pan Head screws—

provided

 

Tools required for connecting an EX Series switch to earth ground:

  • An electrostatic discharge grounding strap (provided)

  • A Phillips (+) number 2 screwdriver to tighten the screws.

An AC–powered EX Series switch gains additional grounding when you plug the power supply in the switch into a grounded AC power outlet by using an AC power cord appropriate for your geographical location.

Special Instructions to Follow Before Connecting Earth Ground to an EX Series Switch

Table 2 lists the special instructions that you might need to follow before connecting earth ground to a switch.

Table 2: Special Instructions to Follow Before Connecting Earth Ground to an EX Series Switch

Switch

Special Instructions

EX3200 and EX4200

Some early variants of EX3200 and EX4200 switches for which the Juniper Networks model number on the label next to the protective earthing terminal is from 750-021xxx through 750-030xxx require 10-24x.25 in. screws.

EX4200, EX4500, and EX4550

If you plan to mount your switch on four posts of a rack or cabinet, mount your switch in the rack or cabinet before attaching the grounding lug to the switch.

Note: The protective earthing terminal on switches mounted on four posts of a rack is accessible through the slot on the left rear bracket only if the rack is 27.5 in. (69.85 cm) through 30.5 in. (77.47 cm) deep for a switch mounted flush with the rack front and 29.5 in. (74.93 cm) through 32.5 in. (82.55 cm) deep for a switch mounted 2 in. (5.08 cm) recessed from the rack front. See Figure 1.

Figure 1: Connecting the Grounding Lug to a Switch Mounted on Four Posts of a Rack
Connecting the Grounding
Lug to a Switch Mounted on Four Posts of a Rack
  1
Protective earthing terminal
  3
Grounding lug
  2
Side mounting-rail
  4
Rear mounting-blade

Note: The brackets must be attached to the chassis before the grounding lug is attached. (The brackets are shown pulled away from the chassis so that the protective earthing terminal is seen.)

Connecting Earth Ground to an EX Series Switch

To connect earth ground to an EX Series switch:

  1. Verify that a licensed electrician has attached the cable lug to the grounding cable.
  2. Connect one end of the grounding cable to a proper earth ground, such as the rack in which the switch is mounted.
  3. Attach an ESD grounding strap to your bare wrist, and connect the strap to the ESD grounding point on the switch.
  4. Place the grounding lug attached to the grounding cable over the protective earthing terminal. See Figure 2.
    Figure 2: Connecting a Grounding Cable to an EX Series Switch
    Connecting a Grounding Cable to an EX Series Switch
  5. Secure the grounding lug to the protective earthing terminal with the washers and screws.
  6. Dress the grounding cable and ensure that it does not touch or block access to other switch components and that it does not drape where people could trip over it.

Powering On an EX6200 Switch

Before you power on the switch, ensure that:

Ensure that you have the following parts and tools available to power on the switch:

To power on the switch:

  1. Attach the ESD grounding strap to your bare wrist and connect the strap to the ESD point on the chassis.
  2. Connect the external management device to the primary SRE module's management (MGMT) port.Note

    Only one of the two management ports on the SRE module can be used at any given time.

  3. Turn on the power to the external management device.
  4. Ensure that the power supplies are fully inserted and secured in the chassis.
  5. Ensure that the source power cord or cords are inserted securely into the AC appliance inlet for each AC power supply.

    If you are using DC power supplies, ensure that the source power cables are connected to the appropriate terminal: the positive (+) source cable to the positive return terminal (+) and the negative (-) source cable to the input terminal (-).

  6. Switch on the site circuit breakers.
  7. Flip a power supply’s Enable switch to the on position (ON). Observe the power supply faceplate LEDs. If the power supply is installed correctly and functioning normally, the INPUT OK and OUTPUT OK LEDs light and remain constantly lit. The FAIL LED does not light.Note

    On a 5000 W AC power supply, if only one power feed is connected to the power supply, only the corresponding INPUT OK LED is lit and only half of the output power is delivered. This is normal operating behavior for the power supply.

  8. Repeat steps 1 through 7 for each of the remaining power supplies installed in the switch.
  9. On the external management device, monitor the startup process to ensure that the system boots properly.
Note

After you power on a power supply, wait for at least 60 seconds before you turn it off. After you power off a power supply, wait for at least 60 seconds before you turn it back on.

If the system is completely powered off when you switch on a power supply, the SRE module boots as the power supply completes its startup sequence.

After you power on a power supply, it can take up to 60 seconds for status indicators such as power supply LEDs and the show chassis operational mode CLI command display to indicate that the power supply is functioning normally. Ignore any error indicators that might appear during the first 60 seconds.