Connecting the EX4550 to Power

 

Connect Earth Ground to an EX Series Switch

To ensure proper operation and to meet safety and electromagnetic interference (EMI) requirements, you must connect an EX Series switch to earth ground before you connect power to the switch. You must use the protective earthing terminal on the switch chassis to connect the switch to earth ground (see Figure 2).

You must install the EX Series switch in a restricted–access location and ensure that the chassis is always properly grounded. EX Series switches have a two–hole protective grounding terminal provided on the chassis. See Table 1 for the location of the earthing terminals on various EX Series switches. We recommend that you use the protective grounding terminal as the preferred method for grounding the chassis regardless of the power supply configuration. However, if additional grounding methods are available, you can also use those methods. For example, you can use the grounding wire in the power cord of an AC power supply or use the grounding terminal or lug on a DC power supply. This system was tested to meet or exceed all applicable EMC regulatory requirements with the two-hole protective grounding terminal connected correctly.

Ensure that a licensed electrician has attached an appropriate grounding lug to the grounding cable you supply. Using a grounding cable with an incorrectly attached lug can damage the switch.

Parts and Tools Required for Connecting an EX Series Switch to Earth Ground

Before you begin connecting an EX Series switch to earth ground, ensure you have the parts and tools required for your switch.

Table 1 lists the earthing terminal location, grounding cable and lug specifications, and parts needed for connecting an EX Series switch to earth ground.

Table 1: Parts Required for Connecting an EX Series Switch to Earth Ground

Switch

Earthing Terminal Location

Grounding Cable Requirements

Grounding Lug Specifications

Screws and Washers

Additional Information

EX2200

Rear panel of the chassis

14 AWG (2 mm²), minimum 90° C wire, or as permitted by the local code

Panduit LCC10-14BWL or equivalent—

not provided

  • Two 10-32 x .25 in. screws with #10 split-lock washer—

    not provided

  • Two #10 flat washers—not provided

 

EX2300-C

Rear panel of the chassis

14 AWG (2 mm²), minimum 90° C wire, or as permitted by the local code

Panduit LCC10-14AW-L or equivalent—

not provided

  • Two 10-32 x .25 in. screws with #10 split-lock washer—

    not provided

  • Two #10 flat washers—not provided

 

EX2300

Rear panel of the chassis

  • EX2300 switches except EX2300-24MP and EX2300-48MP models—14 AWG (2 mm²), minimum 90°C wire, or as permitted by the local code

  • EX2300-24MP and EX2300-48MP models—14-10 AWG STR (2.5-6 mm²), 12-10 AWG SOL (4-6 mm²) minimum 90°C wire, or as permitted by the local code—not provided

  • EX2300 switches except EX2300-24MP and EX2300-48MP models—Panduit LCC10-14AW-L or equivalent—not provided

  • EX2300-24MP and EX2300-48MP models—Panduit LCA10-10L or equivalent—not provided

  • EX2300 switches except EX2300-24MP and EX2300-48MP models

    • Two 10-32 x .25 in. screws with #10 split-lock washer—not provided

    • Two #10 flat washers—not provided

  • EX2300-24MP and EX2300-48MP models

    • One Pan Phillips M 4 x 6 mm Nickel plated screw—provided

 

EX3200, EX3300, and EX3400

Rear panel of the chassis

14 AWG (2 mm²), minimum 90° C wire, or as permitted by the local code

Panduit LCC10-14BWL or equivalent—

not provided

  • Two 10-32 x .25 in. screws with #10 split-lock washer—

    not provided

  • Two #10 flat washers—

    not provided

For EX3200 Switches See Special Instructions to Follow Before Connecting Earth Ground to an EX Series Switch.

EX4200, EX4500, and EX4550

Left side of the chassis

14 AWG (2 mm²), minimum 90° C wire, or as permitted by the local code

Panduit LCC10-14BWL or equivalent—

not provided

  • Two 10-32 x .25 in. screws with #10 split-lock washer—

    not provided

  • Two #10 flat washers—

    not provided

See Special Instructions to Follow Before Connecting Earth Ground to an EX Series Switch.

EX6210

Rear panel of the chassis (on lower left side)

The grounding cable must be the same gauge as the power feed cables and as permitted by the local code.

Panduit LCD2-14A-Q or equivalent

—provided

  • Two ¼ -20 x 0.5 in. screws with #¼” split-washer

    —provided

  • Two #¼” flat washers—

    provided

 

EX8208

Left side of the chassis

6 AWG (13.3 mm²), minimum 90° C wire, or as permitted by the local code

Panduit LCD2-14A-Q or equivalent

—provided

  • Two ¼ -20 x 0.5 in. screws with #¼” split-washer

    —provided

  • Two #¼” flat washers—

    provided

 

EX8216

Two earthing terminals:

  • Left side of the chassis

  • Rear panel of the chassis

Note: You must use only one of the two protective earthing terminals.

2 AWG (33.6 mm²), minimum 90° C wire, or as permitted by the local code

Panduit LCD2-14A-Q or equivalent

—provided

  • Two ¼ -20 x 0.5 in. screws with #¼” split-washer

    —provided

  • Two #¼” flat washers—

    provided

 

EX9204, EX9208, and EX9214

Rear panel of the chassis

One 6 AWG (13.3 mm²), minimum 90° C wire, or one that complies with the local code

Thomas& Betts LCN6-14 or equivalent—

provided

  • Two ¼ -20 x 0.5 in. screws with #¼” split-washer—

    provided

  • Two #¼” flat washers—

    provided

See Grounding Cable and Lug Specifications for EX9200 Switches.

EX9251

Rear panel of the chassis

12 AWG (2.5 mm²), minimum 90° C wire, or one that complies with the local code—

not provided

Panduit LCD10-10A-L or equivalent—

not provided

Two 10-32 screws—

provided

See Grounding Cable and Lug Specifications for EX9200 Switches.

EX9253

Right side of the chassis

14-10 AWG (2-5.3 mm²), minimum 90° C wire, or one that complies with the local code—

not provided

Panduit LCD10-14B-L or equivalent—

provided

Two M5 Pan Head screws—

provided

 

Tools required for connecting an EX Series switch to earth ground:

  • An electrostatic discharge grounding strap (provided)

  • A Phillips (+) number 2 screwdriver to tighten the screws.

An AC–powered EX Series switch gains additional grounding when you plug the power supply in the switch into a grounded AC power outlet by using an AC power cord appropriate for your geographical location.

Special Instructions to Follow Before Connecting Earth Ground to an EX Series Switch

Table 2 lists the special instructions that you might need to follow before connecting earth ground to a switch.

Table 2: Special Instructions to Follow Before Connecting Earth Ground to an EX Series Switch

Switch

Special Instructions

EX3200 and EX4200

Some early variants of EX3200 and EX4200 switches for which the Juniper Networks model number on the label next to the protective earthing terminal is from 750-021xxx through 750-030xxx require 10-24x.25 in. screws.

EX4200, EX4500, and EX4550

If you plan to mount your switch on four posts of a rack or cabinet, mount your switch in the rack or cabinet before attaching the grounding lug to the switch.

Note: The protective earthing terminal on switches mounted on four posts of a rack is accessible through the slot on the left rear bracket only if the rack is 27.5 in. (69.85 cm) through 30.5 in. (77.47 cm) deep for a switch mounted flush with the rack front and 29.5 in. (74.93 cm) through 32.5 in. (82.55 cm) deep for a switch mounted 2 in. (5.08 cm) recessed from the rack front. See Figure 1.

Figure 1: Connecting the Grounding Lug to a Switch Mounted on Four Posts of a Rack
Connecting the Grounding
Lug to a Switch Mounted on Four Posts of a Rack
  1
Protective earthing terminal
  3
Grounding lug
  2
Side mounting-rail
  4
Rear mounting-blade

Note: The brackets must be attached to the chassis before the grounding lug is attached. (The brackets are shown pulled away from the chassis so that the protective earthing terminal is seen.)

Connecting Earth Ground to an EX Series Switch

To connect earth ground to an EX Series switch:

  1. Verify that a licensed electrician has attached the cable lug to the grounding cable.
  2. Connect one end of the grounding cable to a proper earth ground, such as the rack in which the switch is mounted.
  3. Attach an ESD grounding strap to your bare wrist, and connect the strap to the ESD grounding point on the switch.
  4. Place the grounding lug attached to the grounding cable over the protective earthing terminal. See Figure 2.
    Figure 2: Connecting a Grounding Cable to an EX Series Switch
    Connecting a Grounding Cable to an EX Series Switch
  5. Secure the grounding lug to the protective earthing terminal with the washers and screws.
  6. Dress the grounding cable and ensure that it does not touch or block access to other switch components and that it does not drape where people could trip over it.

Connecting AC Power to an EX4550 Switch

The power supply in an EX4550 switch is a hot-removable and hot-insertable field-replaceable unit (FRU): You can remove and replace it without powering off the switch or disrupting switch functions.

Ensure that you have a power cord appropriate for your geographical location available to connect AC power to an EX4550 switch.

Before you begin connecting AC power to an EX4550 switch:

  • Ensure that you have taken the necessary precautions to prevent electrostatic discharge (ESD) damage (see Prevention of Electrostatic Discharge Damage).

  • Ensure that you have connected the device chassis to earth ground, if required by your site guidelines or installation. A ground connection to the protective earthing terminal is not required for an AC-powered switch. The AC power cords provide adequate grounding when you connect the power supply in the switch to a grounded AC power outlet by using the AC power cord appropriate for your geographical location (see AC Power Cord Specifications for an EX4550 Switch).

    Caution

    For installations that require a separate grounding conductor to the chassis, have a licensed electrician complete this connection before you connect the switch to power. For instructions on connecting earth ground, see Connect Earth Ground to an EX Series Switch.

  • Install the power supply in the chassis. For instructions on installing a power supply in an EX4550 switch, see Installing an AC Power Supply in an EX4550 Switch.

Note

Each power supply must be connected to a dedicated power source outlet.

To connect AC power to an EX4550 switch:

  1. Attach the grounding strap to your bare wrist and to a site ESD point.
  2. Ensure that the power supplies are fully inserted in the chassis and the latches are secure. If only one power supply is installed, ensure that a blank cover panel is installed over the second power supply slot.
  3. Locate the power cord or cords shipped with the switch; the cords have plugs appropriate for your geographical location. See AC Power Cord Specifications for an EX4550 Switch.Warning

    Ensure that the power cord does not block access to switch components or drape where people can trip on it.

  4. Insert the coupler end of the power cord into the AC power cord inlet on the AC power supply faceplate.
  5. Push the power cord retainer onto the power cord (see Figure 3).
    Figure 3: Connecting an AC Power Cord to an AC Power Supply in an EX4550 Switch
    Connecting an
AC Power Cord to an AC Power Supply in an EX4550 Switch
      1
    Power cord retainer clip
     
  6. If the AC power source outlet has a power switch, set it to the off (O) position.
  7. Insert the power cord plug into an AC power source outlet.
  8. If the AC power source outlet has a power switch, set it to the on (|) position.
  9. Repeat these steps for the second AC power supply, if one is installed.
  10. Verify that the AC and DC LEDs on each power supply are lit green.

    If the fault status (!) LED is lit yellow, remove power from the power supply, and replace the power supply (see Removing an AC Power Supply from an EX4550 Switch). Do not remove the power supply until you have a replacement power supply ready: the power supplies or a blank cover panel must be installed in the switch to ensure proper airflow.

    Caution

    We recommend that you install either a replacement power supply or a cover panel in the empty power supply slot to avoid chassis overheating and dust accumulation.

Connecting DC Power to an EX4550 Switch

The power supply in an EX4550 switch is a hot-removable and hot-insertable field-replaceable unit (FRU): You can remove and replace it without powering off the switch or disrupting switch functions.

Before you begin connecting DC power to an EX4550 switch:

  • Ensure that you have taken the necessary precautions to prevent electrostatic discharge (ESD) damage (see Prevention of Electrostatic Discharge Damage).

  • Ensure that you have connected the switch chassis to earth ground.

    Caution

    Ensure that you install the power supply module first and then install the DC input wire, before closing input breaker ON.

    Caution

    Before you connect power to the device, a licensed electrician must attach a cable lug to the grounding and power cables that you supply. A cable with an incorrectly attached lug can damage the device (for example, by causing a short circuit).

    To meet safety and electromagnetic interference (EMI) requirements and to ensure proper operation, you must connect the chassis to earth ground before you connect it to power. For installations that require a separate grounding conductor to the chassis, use the protective earthing terminal on the switch chassis to connect to the earth ground. For instructions on connecting earth ground, see Connect Earth Ground to an EX Series Switch.

  • Install the power supply in the chassis. For instructions on installing a DC power supply in an EX4550 switch, see Installing a DC Power Supply in an EX4550 Switch.

Ensure that you have the following parts and tools available:

  • DC power source cables (14–16 AWG) with ring lug (Molex 190700069 or equivalent) (not provided)

  • Phillips (+) screwdriver, number 2 (not provided)

  • Multimeter (not provided)

To connect DC power to an EX4550 switch:

  1. Attach the grounding strap to your bare wrist and to a site ESD point.
  2. Verify that the DC power cables are correctly labeled before making connections to the power supply. In a typical power distribution scheme where the return is connected to chassis ground at the battery plant, you can use a multimeter to verify the resistance of the –48V and RTN DC cables to chassis ground:
    • The cable with very low resistance (indicating a closed circuit) to chassis ground is positive (+) and will be installed on the V+ (return) DC power input terminal.

    • The cable with very high resistance (indicating an open circuit) to chassis ground is negative (–) and will be installed on the V– (input) DC power input terminal.

    Caution

    You must ensure that power connections maintain the proper polarity. The power source cables might be labeled (+) and (–) to indicate their polarity. There is no standard color coding for DC power cables. The color coding used by the external DC power source at your site determines the color coding for the leads on the power cables that attach to the DC power input terminals on each power supply.

  3. Ensure that the input circuit breaker is open so that the voltage across the DC power source cable leads is 0 V and that the cable leads will not become active while you are connecting DC power.Note

    The V+ terminals are referred to as +RTN and V– terminals are referred to as –48 V in DC Power Wiring Sequence Warning and DC Power Electrical Safety Guidelines.

  4. Ensure that the power supplies are fully inserted in the chassis.
  5. Remove the terminal block cover. The terminal block cover is a piece of clear plastic that snaps into place over the terminal block.
  6. Remove the screws on the terminals using the screwdriver. Save the screws.Warning

    Ensure that the power cables do not block access to switch components or drape where people can trip on them.

    Note

    To supply sufficient power, terminate the DC input wiring on a facility DC source that is capable of supplying a minimum of 20 A at –48 VDC.

  7. Connect each power supply to the power source. Secure power source cables to the power supplies by screwing the ring lugs attached to the cables to the appropriate terminals by using the screw from the terminals (see Figure 4 and Figure 5).Note

    The DC power supply has four input terminals labeled V+, V+, V–, and V– for connecting DC power source cables labeled positive (+) and negative (–). The V+ terminals are shunted internally together, as are the V– terminals to provide parallel current path. The same polarity input terminals can be connected with the same source to provide an additional current path in a higher power chassis. Each power supply must be connected to a single source only.

    1. Secure the ring lug of the positive (+) DC power source cable to the V+ terminal on the DC power supply.
    2. Secure the ring lug of the negative (–) DC power source cable to the V– terminal on the DC power supply.
    3. Tighten the screws on the power supply terminals until snug using the screwdriver. Do not overtighten—apply between 5 in-lb (0.56 Nm) and 6 in-lb (0.68 Nm) of torque to the screws.
    Figure 4: DC Power Supply Faceplate for an EX4550 Switch
    DC Power Supply
Faceplate for an EX4550 Switch
      1
    V+ input terminals
      5
    ESD grounding point
      2
    V– input terminals
      6
    Fault LED
      3
    Terminal block
      7
    Output LED
      4
    Ejector lever
      8
    Input LED
    Figure 5: Securing Ring Lugs to the Terminals on the DC Power Supply
    Securing Ring Lugs
to the Terminals on the DC Power Supply
  8. Replace the terminal block cover.
  9. Close the input circuit breaker.Note

    The device powers on as soon as power is provided to the power supply. There is no power switch on the device.

  10. Verify that the IN and OUT LEDs on the power supply are lit green and are on steadily.