Connecting the SRX1400 Services Gateway to a DC Power Supply

 

You connect DC power to the services gateway by attaching power cables from the external DC power sources to the terminal studs on the power supply faceplates.

Warning

To meet safety and electromagnetic interference (EMI) requirements and to ensure proper operation, you must properly ground the services gateway chassis before connecting power. See Grounding the SRX1400 Services Gateway for instructions.

Warning

Before performing the following procedure, ensure that power is removed from the DC circuit. To ensure that all power is off, locate the circuit breaker on the panel board that services the DC circuit, switch the circuit breaker to the off position, and tape the switch handle of the circuit breaker in the off position.

Caution

Do not mix AC and DC power supplies within the same services gateway. Damage to the services gateway might occur.

Caution

Before you connect power to the services gateway, a licensed electrician must attach appropriate cable lugs to the grounding and power cables that you use. A cable with an incorrectly attached lug can damage the device (for example, by causing a short circuit).

To connect the DC source power cables to the services gateway for each power supply:

  1. Switch off the dedicated facility circuit breakers. Ensure that the voltage across the DC power source cable leads is 0 V and that there is no chance that the cable leads might become active during installation.
  2. Remove the clear plastic cover that protects the terminal studs on the faceplate.
  3. Verify that the DC power cables are correctly labeled before making connections to the power supply.

    In a typical power distribution scheme where the return is connected to chassis ground at the battery plant, you can use a multimeter to verify that the ohm output of the -48V and RTN DC cables to chassis ground. The cable with very large resistance (indicating an open circuit) to chassis ground will be -48V, and the cable with very low resistance (indicating a closed circuit) to chassis ground will be RTN.

    Caution

    You must ensure that power connections maintain the proper polarity. The power source cables might be labeled (+) and (–) to indicate their polarity. There is no standard color coding for DC power cables. The color coding used by the external DC power source at your site determines the color coding for the leads on the power cables that attach to the terminal studs on each power supply.

  4. Remove the screws and square washers from the terminals, using a Phillips (+) screwdriver, number 2.
  5. Secure each power cable lug to the terminals with the square washers and the screws. Apply between 23 in.-lb (2.6 Nm) and 25 in.-lb (2.8 Nm) of torque to each screw.
    • Secure each positive (+) DC source power cable lug to a RTN (return) terminal.

    • Secure each negative (–) DC source power cable lug to a -48V (input) terminal.

  6. Replace the clear plastic cover over the terminal studs on the faceplate.
  7. Verify that the power cables are connected correctly, that they are not touching or blocking access to services gateway components, and they do not cause a tripping hazard.
  8. Repeat Steps 1 through 7 for the second power supply, if you are installing one.
Note

If power is lost to the services gateway, the Power-On/Power-Off state is retained. For example, if the services gateway loses power while the device is on, when power returns, the device will still be in the On state.