SRX550 Services Gateway Grounding Specifications

 

To meet safety and electromagnetic interference (EMI) requirements and to ensure proper operation, the SRX550 Services Gateway must be adequately grounded before power is connected. You must provide a grounding lug to connect the services gateway to earth ground.

Warning

Before services gateway installation begins, a licensed electrician must attach a cable lug to the grounding and power cables that you supply. A cable with an incorrectly attached lug can damage the services gateway (for example, by causing a short circuit).

To ground the services gateway before connecting power, you connect the grounding cable to earth ground and then attach the lug on the cable to the chassis grounding point, using the screw.

Table 1 lists the specifications of the grounding cable used with the device.

Table 1: Grounding Cable Specifications for the SRX550 Services Gateway

Grounding Requirement

Specification

Grounding cable

14 AWG single-strand wire cable

Amperage of grounding cable

Up to 25A

Grounding lug

Ring-type, Panduit LCC6-10A-L lug, or equivalent