Environmental Requirements and Specifications for ACX710 Routers

 

The router must be installed in a rack or cabinet. It must be housed in a dry, clean, well-ventilated, and temperature-controlled environment.

Follow these environmental guidelines:

  • The site must be as dust-free as possible because dust can clog air intake vents and filters, reducing the efficiency of the router cooling system.

  • Maintain ambient airflow for normal router operation. If the airflow is blocked or restricted, or if the intake air is too warm, the router might overheat, and the router temperature monitor might shut down the device to protect the hardware components.

Table 1 lists the environmental conditions required for normal router operation.

Table 1: ACX710 Router Environmental Tolerances

Description

Tolerance

Altitude

-60 m to 4000 m

Relative humidity

5% to 95% (non-condensing)

Nominal operating temperature

-40° C to 65° C (-40° F to 149° F)

Shipping and storage temperature

-40° C to 70° C (-40° F to 158° F)

Cold start temperature

-40° C (-40° F)

Pollution degree

2 (IEC 60950)

Acoustic noise level

< 7.2 Bels (EN 300 753)

Enclosure classification

IP20 (IEC 60529)

Environmental class

GR-3108 Class 1 and Class 2

Seismic

Complies with Zone 4 earthquake requirements per NEBS GR-63-CORE, Issue 4.

Note

Install ACX Series devices only in restricted areas, such as dedicated equipment rooms and equipment closets, in accordance with Articles 110-16, 110-17, and 110-18 of the National Electrical Code, ANSI/NFPA 70.