MX2000 High-Voltage Universal (HVAC/HVDC) Power Supply Module Description

The MX2020 supports a two zone power system. Each zone upper and lower provides power to zone subsystem. In the HVAC/HVDC power configuration, the router contains up to eighteen universal (HVAC/HVDC) PSMs located at the rear of the chassis in slots PSM0 through PSM8 (bottom), and slots PSM9 through PSM17 (top) (left to right). The universal (HVAC/HVDC) PSMs in slots PSM0 through PSM8 provide power to the lower half of the router components, MPCs in slot 0 through 9, CB-REs in slot 0 and 1, SFBs in slot 0 through 7, and Fan Trays 0, 1, and 2. The universal PSMs in slots PSM9 through PSM17 provide power to the upper half of the router components, MPCs in slot 10 through 19, CB_REs in slot 0, and 1, SFBs in slot 0 through 7, and Fan Trays 0, 2, and 3. CB_REs in slot 0 and 1, and SFBs in slot 0 through 7 are powered from parallel connected PSM0 through PSM8, and parallel connected PSM9 through PSM17.

Note:

The MX2020 systems configured for universal (HVAC/HVDC) input power must use only universal PDMs and PSMs. AC, DC, 240 V China, and universal PSMs or PDMs must not be mixed within a single system.

Up to nine PSMs may be connected in parallel to increase available system power across MPCs as needed and provide redundancy. Figure 1 shows the universal PSM.

Figure 1: High-Voltage Universal (HVAC/HVDC) Power Supply ModuleHigh-Voltage Universal (HVAC/HVDC) Power Supply Module

The HVAC/HVDC power system is feed redundant. Each universal PSM can be connected to two separate feeds from different sources that are used to provide feed redundancy. The PSM has two independent power trains connected in parallel at the output while each input is connected to its own feed. Power always is drawn from both feeds. There are two PDMs per power subsystem capable of carrying nine feeds each. The bottom PDM in each power cage provides power to INP0 of all PSMs installed in the cage, while top PDM in each power cage provides power to INP1 of all PSMs installed in the cage. Feed connection to the PDMs should be done according to standard TIA-942 “Telecommunications Infrastructure Standard for Data” depending on tiering level. The primary input of the PSM is a dual-redundant feed, INP0 and INP1. Both feeds are active during operation, and always carry current. Two dual-position DIP switches accessible from front panel indicate whether respective input INP0 or INP1 is expected to be connected or not. Set the input mode DIP switch to the on or off position to determine the power supply feeds (see Table 1 and Figure 2). In addition, a PSM failure triggers the alarm LED on the craft interface. Each PDM has an LED per feed indicating whether the feed is active or not, or whether the feed is connected properly. See MX2020 High-Voltage Universal Power Supply Module LEDs.

Table 1: DIP Switch Positions on the Universal (HVAC/HVDC) PSM

Switch Location Left (Input 0)

Switch Location Middle (Input 1)

Input Source

Off

Off

None are expected to be connected.

On

Off

Only input (0) is expected to be connected.

Off

On

Only input( 1) is expected to be connected.

On

On

Both input 0 and input 1 are expected to be connected.

Figure 2: Selecting the Input Feed on the Universal (HVAC/HVDC) Power Supply ModuleSelecting the Input Feed on the Universal (HVAC/HVDC) Power Supply Module

The universal HVAC/HVDC PSM has one more (third) DIP input switch accessible from the front panel, see Figure 2. This switch indicates the PSM in the system is using the universal (MX2K-PDM-HV) PDM that has 30 A rated power cord. This should be in the ON position.

Table 2:

Switch Location Right (Input 2)

Meaning

On. See Figure 2.

PSM is using the universal HVAC/HVDC PDM that has 30 A-rated power cord.

Note:

The switch must be in the On position for proper operation.