Technical Documentation

Power Consumption for an AC-Powered SRX5800 Services Gateway

We recommend that you provision 11 A  @ 240 VAC for each input.

If you do not plan to provision 11 A  @ 240 VAC for each input, you can use the information in Table 1 and Table 2 to calculate the power consumption and thermal output for your hardware configuration.

Table 1 lists the power requirements for base AC-powered services gateways operating under typical voltage conditions and includes nonredundant and redundant power supply configurations.

Table 1: Base Device AC Power Requirements

AC Power Supply Configuration

Power Requirement (Watts)

Nonredundant AC configuration includes three AC power supplies, the midplane, craft interface, and fan trays (running at normal speed)

471 W (approximate)

Redundant AC configuration includes four AC power supplies, the midplane, craft interface, and fan trays (running at normal speed)

500 W (approximate)

Table 2 lists the power requirements for various hardware components under typical voltage conditions.

Table 2: Component Power Requirements for AC-Powered Devices

Component

Power Requirement (Watts)

Power Requirement (Watts) with 85% Efficiency

Cooling system (full speed – normal speed)

600 W – 400 W = 200 W

235 W

SCB

150 W

176 W

Routing Engine

90 W

106 W

IOC—Generalized typical value

312 W

367 W

IOC—Generalized maximum value

365 W

429 W

SPC—Generalized typical value

213 W

251 W

SPC—Generalized maximum value

351 W

413 W

Typical power consumption for AC-powered devices:

  • Power consumption for minimum configuration:
    Base device and three power supplies + 2 SCBs + 1 Routing Engine + 1 IOC + 1 SPC—Generalized typical value=
    471 W + (2)176  W + 106 W + 367 W + 251 = 1547 W
  • AC Power consumption for maximum configuration:
    Base device and four power supplies + fan tray at full speed + 2 SCBs + 1 Routing Engine + 10 IOCs + 1 SPC—Generalized maximum value=
    500 W + 235 W + 2(176 W) + 106 W + 10(429 W)+ 413 W = 500 W + 235 W + 352 W + 106 W + 4290 W+ 413 W = 5896 W
  • Current requirement adjustment for fans running at full speed (high temperature environment or cooling component failure):
    Calculated system current (X) – Cooling (normal) + Cooling (full speed) =
    X A – 8.3 A + 12.5 A =
    X A + 4.2 A
  • System thermal output for maximally configured AC-powered services gateway:
    Watts DC* 3.41 = BTU/hr
    5896 W * 3.41 = 20,105 BTU/hr

Published: 2009-11-03