Power Consumption for a DC-Powered SRX5600 Services Gateway
![]() |
Note: If you plan to operate a maximally configured DC-powered services gateway, we recommend that you provision 58 A (32 A per feed) @ –48 VDC for the system. |
If you do not plan to provision 58 A (32 A per feed) @ –48 VDC for the system, you can use the information in Table 1 and Table 2 to calculate the power consumption @ –48 VDC, and thermal output for various hardware configurations.
Table 1 lists the power requirements for base DC-powered devices operating under typical voltage conditions.
Table 1: DC-Powered Base System Requirements
Table 2 lists the power requirements for various hardware components when the services gateway is operating under typical voltage conditions.
Table 2: Component Power Requirements
Use the information in Table 1 and Table 2 to calculate power consumption for various hardware configurations, input current from a different source voltage, and thermal output, as shown in the following examples. These examples use generalized values per IOC. Typical power consumption for DC-powered devices:
- Minimum DC-powered configuration:
- Maximum DC-powered configuration:
- Input current from a DC source other than –48 VDC (based on maximum configuration; applies to DC power supply only):
- Thermal output for maximally configured DC-powered services gateway: