Technical Documentation

Power Requirements for AC-Powered SRX3600 Services Gateways

Note: If you plan to operate a maximally configured AC-powered services gateway, we recommend that you provision 24 A @ 100 V for the system, or 12.0 A @ 100-127 V / 7 A @ 200-240 V for each power supply.

If you do not plan to provision 24 A @ 100 V for the system, or 12.0 A @ 100-127 V / 7 A @ 200-240 V for each power supply, you can use the information in Table 1 and Table 2 to calculate power consumption for various hardware configurations, and thermal output.

Table 1 lists the power requirements for base AC-powered devices operating under typical voltage conditions. It includes the efficiency for the AC power supplies.

Table 1: Base System AC Power Requirements

Component

Power Requirement (Watts)

Nonredundant configuration includes two AC power supplies, midplane, SFB, Routing Engine, and the fan tray

353 W (approximate)

Redundant configuration includes four AC power supplies, midplane, SFB, Routing Engine, and the fan tray

430 W (approximate)

Note: The power requirement values shown in Table 1 are for a lightly loaded system. For a heavily loaded system, the contribution of the base system to the overall system power requirement is lower, because the power supply efficiency improves as the load increases. For a heavily loaded system, both the redundant and nonredundant base systems contribute approximately 353 W to the overall system power requirement.

Table 2 lists the power requirements for various hardware components when the services gateway is operating under typical voltage conditions.

Table 2: Component AC Power Requirements

Component

Power Requirement (Watts)

AC Input Power Requirement at 85% Power Supply Efficiency

Routing Engine

53 W

62 W

SPC

118 W

139 W

NPC

64 W

75 W

SCM

35 W

41 W

IOC (min)

40 W

47 W

IOC (max)

52 W

61 W

Use the information in Table 1 and Table 2 to calculate power consumption for various hardware configurations, and thermal output, as shown in the following examples. These examples use maximum values per IOC.

Typical power consumption for AC-powered devices:

  • Minimum AC-powered configuration:
    Base device (nonredundant) + 1 SPC + 1 NPC =353 W + 139 W + 75 W = 567 W
  • Maximum AC-powered configuration:
    Base device (redundant) + 7 SPCs + 3 NPCs + 2 IOCs + SCM =353 W + 7(139)  W + 3(75) W + (2) 61 W + 41 W =353 W + 973 W + 225 W + 122 W + 41 W = 1714 W
  • Typical system thermal output (based on maximally configured AC-powered services gateway @ 110 V input):
    Watts * 3.41 = BTU/hr1714 W * 3.41 = 5845 BTU/hr

Published: 2010-04-20