Troubleshooting the Power System on the SRX3400 Services Gateway
To verify that a power supply is functioning normally, perform the following steps:
- Check the LEDs on each power supply faceplate. If an AC power supply is correctly installed and functioning normally, the OUTPUT OK status LED on the power supply faceplate blinks, then lights steadily approximately one minute after you switch the power supply circuit breaker on. If a DC power supply is correctly installed and functioning normally, the PWR OK, BRKR ON, and INPUT OK LEDs light green steadily.
- Issue the CLI show chassis environment pem command to check the status of installed power supplies. As shown
in the sample output, the value Online in the rows labeled State indicates that the power supplies in slots 0 and 1 are functioning normally:
user@host>show chassis environment pem
If a power supply is not functioning normally, perform the following steps to diagnose and correct the problem:
- If a red alarm condition occurs, issue the show chassis
alarms command to determine the source of the problem.

Note: If the system temperature exceeds the threshold, the JUNOS Software shuts down all power supplies so that no status is displayed.
The JUNOS Software also can shut down one of the power supplies for other reasons. In this case, the remaining power supplies provide power to the services gateway, and you can still view the system status through the CLI or J-Web interface.
- Verify that the source circuit breaker has the proper current rating. Each power supply must be connected to a separate source circuit breaker.
- Verify that the AC power cord or DC power cables from the power source to the device are not damaged. If the insulation is cracked or broken, immediately replace the cord or cable.
- Connect the power supply to a different power source with a new power cord or power cables. If the power supply status LEDs indicate that the power supply is not functioning normally, the power supply is the source of the problem. Replace the power supply with a spare, as described in Replacing an AC Power Supply on the SRX3400 Services Gateway or Replacing a DC Power Supply on the SRX3400 Services Gateway.
- If you cannot determine the cause of the problem or need additional assistance while troubleshooting a services gateway, open a support case using the Case Manager link at: http://www.juniper.net/support/ , or call 1-888-314-JTAC (within the United States) or 1-408-745-9500.