M320 Power Requirements

Table 1 lists the power requirements for various hardware components when the router is operating under typical voltage conditions. Generalized values are listed for PICs. For power requirements for specific PICs, see the M320 Multiservice Edge Router PIC Guide.

Table 1: Component Power Requirements

Component

Power Requirement (Watts)

Current Requirement (Amps @ –48 VDC)

Base system, not including FPCs and PICs (includes four SIBs, one host subsystem, two power supplies, cooling system running at normal speed, and craft interface)

450 W (approximate)

9.4 A (approximate)

Type 1 FPC (without PICs)

160 W

3.3 A

Type 2 FPC (without PICs)

160 W

3.3 A

Type 3 FPC (without PICs)

160 W

3.3 A

Host subsystem (Routing Engine and CB)

100 W

2.1 A

SIB

38 W

0.8 A

AC power supply

100 W

Not applicable.

DC power supply

40 W

0.8 A

Cooling system (normal speed)

140 W

2.9 A

Cooling system (full speed)

200 W

4.0 A

PIC—Generalized typical value

30 W

0.625 A

PIC—Generalized maximum value

52.8 W

1.1 A

You can use the information in Table 1 and the M320 Multiservice Edge Router PIC Guide to calculate power consumption for various hardware configurations, input current from a different source voltage, and thermal output, as shown in the following examples for a DC-powered router.

  • Example of calculating power consumption for minimum configuration:
    Base system + 1 FPC + 1 PIC =9.4 A + 3.3 A + 0.625 A = 13.3 A @ –48 VDC = 638 W DC
  • Example of calculating power consumption for maximum configuration:
    Base system + 1 Host subsystem + 2 redundant DC power supplies + 8 FPCs + 32 PICs =9.4 A + 2.1 A + 2(0.8) A + 8(3.3 A) + 32(1.1 A) =9.4 A + 2.1 A + 1.6 A + 26.4 A + 35.2 A = 74.7 A @ –48 VDC =3,586 W DC
  • Current requirement adjustment for fans running at full speed (high temperature environment or cooling component failure):
    Calculated system current (X) – Cooling (normal) + Cooling (full speed) =X A – 2.9 A + 4.0 A =X A + 1.1 A
  • Input current from a DC source other than –48 VDC (based on maximum configuration; applies to DC power supply only):
    (–54 VDC input)  x  (input current X) = (–48 VDC input)  x  (input current Y)54  x  X = 48  x  57.9 AX = 48 x 57.9 A/54 = 51.5 A
  • Example of calculating system thermal output for a DC-powered router:
    Watts DC/0.293 = BTU/hr3,586/0.293 = 12,239 BTU/hr
  • Example of calculating system thermal output for an AC-powered router:
    Watts DC/85% AC PEM efficiency/0.293 = BTU/hr3,586/0.85/0.293 = 14,398 BTU/hr