MX80 Router Cabinet Requirements and Specifications
Table 1 summarizes
cabinet requirements and specifications for MX80 routers.
Table 1: Cabinet Requirements and Specifications for an MX80 Router
Cabinet Requirement | Guidelines for the MX80 Router |
|---|
Cabinet size and clearance | - The minimum-sized
cabinet that can accommodate the router is 19-in. (482-mm) wide and
23.62-in. (600-mm) deep. A cabinet larger than the minimum requirement
provides better airflow and reduces the chance of overheating. If
you provide adequate cooling air and airflow clearance, you can stack
several routers in a cabinet that has sufficient usable vertical space.
Each router requires 2 U.
A U is the standard rack unit defined in Cabinets,
Racks, Panels, and Associated Equipment (document number
EIA-310–D) published by the Electronics Industry Association
(http://www.eia.org). - With adequate cooling air and airflow clearance, you can
stack multiple MX80 routers in a cabinet with a four-post rack. In
all cases, the rack must meet the strength requirements to support
the weight.
- The minimum total clearance inside the cabinet is 30.7 in.
(780 mm) between the inside of the front door and the inside of the
rear door.
|
Cabinet airflow requirements | When you install the router in a cabinet,
you must ensure that ventilation through the cabinet is sufficient
to prevent overheating. Consider the following requirements to when
planning for chassis cooling: - Airflow must always be from front to back with respect
to the rack. If the device has side to rear airflow, then provisions
must be made to ensure that fresh air from the front of the rack is
supplied to the inlets, and exhaust exits the rear of the rack. The
device must not interfere with the cooling of other systems in the
rack. Fillers must be used as appropriate in the rack to ensure there
is no recirculation of heated exhaust air back to the front of the
rack. Care must also be taken around cables to ensure no leakage of
air in situations where recirculation may result.
- Ensure that the cabinet allows the chassis hot exhaust
air to exit from the cabinet without recirculating into the router.
An open cabinet (without a top or doors) that employs hot air exhaust
extraction from the top allows the best airflow through the chassis.
If the cabinet contains a top or doors, perforations in these elements
assist with removing the hot air exhaust. For an illustration of chassis
airflow, see Figure 1.
- Ensure that the cool air supply you provide through the
cabinet can adequately dissipate the thermal output of the router.
- Route and dress all cables to minimize the blockage of
airflow to and from the chassis.
- Ensure that the spacing of rails and adjacent racks allows
for the proper clearance around the router and rack as specified in MX80 Router Clearance Requirements for Airflow and Hardware Maintenance.
- Install the router as close as possible to the front of
the cabinet so that the chassis just clears the inside of the front
door. This maximizes the clearance in the rear of the cabinet for
critical airflow.
|
Figure 1: Airflow Through Chassis

Published: 2010-08-13