Technical Documentation

T1600 Three-Input 240-A DC Power Supply Overview

T1600 Three-Input 240-A DC Power Supply Description

Each three-input 240-A DC power supply weighs approximately 25 lb. (11.3 kg) and consists of three inputs, three 80-A circuit breakers, a fan, and LEDs to monitor the status of the power supply. Figure 1 shows the three-input 240-A DC power supply.

Figure 1: Three-Input 240-A DC Power Supply

Image g002404.gif

T1600 Three-Input 240-A DC Power Supply Inputs

The three-input 240-A DC power supply inputs are labeled INPUT 0, INPUT 1, and INPUT 2, from top to bottom. Each input consists of –48 VDC and return—each with its own 80-A circuit breaker. The input mode switch on the faceplate allows you to set the DC power supply to either 2-INPUT or 3-INPUT mode. 3-INPUT mode is required for the T1600 Core Router.

Table 1 describes which components are powered by each input.

Table 1: Components Powered by Each Three-Input 240-A DC Power Supply Input

InputThree-Input Mode

INPUT 0

SIBs, control boards, fan trays, and Routing Engines

INPUT 1

FPCs in slots FPC4 through FPC7

INPUT 2

FPCs in slots FPC0 through FPC3

T1600 Three-Input 240-A DC Power Supply Load Sharing and Fault Tolerance

When the T1600 router is operating normally and both power supplies are switched on, load sharing between them occurs automatically. When one power supply fails or is turned off, the other power supply immediately assumes the entire electrical load for the system. A single power supply can provide full power for as long as the router is operational. Table 2 describes the behavior of the power supply if one of the inputs fails.

Table 2: Fault Tolerance in Three-Input Mode

InputThree-Input Mode

INPUT 0

If this input fails, INPUT 0, INPUT 1, and INPUT 2 shut down. The power supply shuts down, and the other power supply assumes the electrical load for all three inputs.

INPUT 1

If this input fails, INPUT 0 is unaffected and INPUT 1 and INPUT 2 shut down. The other power supply assumes the electrical load of INPUT 1 and INPUT 2.

INPUT 2

If this input fails, INPUT 0 is unaffected and INPUT 1 and INPUT 2 shut down. The other power supply assumes the electrical load of INPUT 1 and INPUT 2.


Published: 2010-08-11

|
|