Power Consumption for an AC-Powered SRX5600 Services Gateway
 |
Note:
If you plan to operate a maximally configured AC-powered
services gateway, we recommend that you provision 33 A @ 100 VAC
or 14 A @ 240 VAC for the system, or 11.0 A @ 200 VAC
or 14.5 A @ 110 VAC for each power supply.
|
We recommend
that you provision 11.0 A @ 200 VAC (2200 W) or
14.5 A @ 110 VAC (1595 W) for each input.
If you do not plan to provision 11.0 A @ 200 VAC
(2200 W) or 14.5 A @ 110 VAC (1595 W) for each
input, you can use the information in Table 1 and Table 2 to calculate power consumption
for various hardware configurations, and thermal output.
Table 1 lists the power
requirements for base AC-powered devices operating under typical voltage
conditions. It includes the efficiency for the AC power supplies.
Table 1: Base System AC Power Requirements
Component
|
Power Requirement (Watts)
|
Low-line nonredundant configuration @ 110 V includes
three AC power supplies, midplane, craft interface, and the fan tray
(running at normal speed)
|
455 W (approximate)
|
Low-line redundant configuration @ 110 V includes four
AC power supplies, midplane, craft interface, and the fan tray (running
at normal speed)
|
585 W (approximate)
|
High-line nonredundant configuration @ 220 V includes
two AC power supplies, one Routing Engine, one SCB, midplane, craft
interface, and the fan tray (running at normal speed)
|
410 W (approximate)
|
High-line redundant configuration @ 220 V includes four
AC power supplies, midplane, craft interface, and the fan tray (running
at normal speed)
|
745 W (approximate)
|
Table 2 lists the
power requirements for various hardware components when the services
gateway is operating under typical voltage conditions.
Table 2: Component Power Requirements
Component
|
Power Requirement (Watts)
|
Fan tray (full speed) – Fan tray (normal speed)
|
110 W – 80 W = 30 W
|
SCB
|
150 W
|
Routing Engine
|
90 W
|
IOC—Generalized typical value
|
312 W
|
IOC—Generalized maximum value
|
365 W
|
SPC—Generalized typical value
|
213 W
|
SPC—Generalized maximum value
|
351 W
|
These examples use generalized
values per IOC.
Typical power consumption for AC-powered devices:
- Minimum AC-powered low-line
configuration @ 110 V:
- Base device (low-line nonredundant) + 1 SCB + 1 Routing
Engine + 1 IOC + 1 SPC—Generalized typical value=
- 455 W + 150 W +90 W + 312 W + 213 W
= 1220 W
- Maximum AC-powered low-line configuration @ 110 V:
- Base device (low-line redundant) + fan tray at full speed
+ 2 SCBs + 1Routing Engine + 5 IOCs + 1 SPC—Generalized
maximum value=
- 585 W + 30 W + 2(150) W + 90 W + (5)365 W
+ 351 W=
- 585 W + 30 W + 300 W + 90 W + 1825 W
+ 351 W = 3181 W
- Typical system thermal output (based
on maximally configured AC-powered services gateway @ 110 V input):
- Watts * 3.41 = BTU/hr
- 3181 W * 3.41 = 10,847 BTU/hr
- Minimum AC-powered high-line configuration
@ 220 V:
- Base device (high-line nonredundant) + 1 SCB + 1 Routing
Engine + 1 IOC + 1 SPC—Generalized typical value=
- 410 W + 150 W + 90 W + 312 W + 213 W
= 1175 W
- Maximum AC-powered high-line configuration
@ 220 V:
- Base device (high-line redundant) + fan tray at full speed
+ 2 SCBs + 1Routing Engine + 5 IOCs + 1 SPC—Generalized
maximum value =
- 745 W + 30 W + 2(150) W + 90 W + (5)365 W
+ 351 W =
- 745 W + 30 W + 300 W + 90 W + 1825 W
+ 351 W = 3341 W
- Typical system thermal output (based on maximally configured
AC-powered services gateway @ 220 V input):
- Watts * 3.41 = BTU/hr
- 3341 W * 3.41 = 11,393 BTU/hr
Published: 2009-11-03