    Monitoring the Physical Environment of the Router

    Purpose

    Display information about the router’s physical environment, such as voltage or temperature. The system displays a message if the voltage or temperature exceeds normal operating limits. The system enters thermal protection mode if the temperature exceeds maximum operating limits or if the fan system on the E120 and E320 routers reports a critical error. For information about thermal protection mode on ERX7xx models, ERX14xx models, and the ERX310 router, see the Troubleshooting chapter in the ERX Hardware Guide. For information about thermal protection mode on the E120 and E320 routers, see the Troubleshooting chapter in the E120 and E320 Hardware Guide.

    Optionally, you can specify the all keyword to view both the system environment information and the detailed temperature status table, or specify the table keyword to view only the temperature status table.

    Action

    To display the environment of an ERX7xx model:

    host1#show environment all
        chassis: 14 slot (id 0x3, rev. 0x0)
        fabric: 5 Gbps (rev. 1)
        fans: ok
        nvs: ok (81MB flash disk, 54% full)
        power: A ok, B not present
        AC power: A not present, B not present
        srp redundancy: none
    *** slots: cards missing or offline
            online: 6 9
            standby: 8
            offline: 2
            empty: 0 1 3 4 5 7 10 11 12 13
        line redundancy: 1 redundancy group(s)
            width 6, spare 8, primary 9
        temperature: ok
        timing: primary
            primary: internal SC oscillator (ok)
            secondary: internal SC oscillator (ok)
            tertiary: internal SC oscillator (ok)
            auto-upgrade enabled
    *** system operational: no
            processor     processor        IOA           IOA    
           temperature   temperature   temperature   temperature
    slot   (10C - 70C)     status      (10C - 70C)     status   
    ----   -----------   -----------   -----------   -----------
    0          31        normal            30        normal     
    3          31        normal            30        normal 
    5          31        normal            30        normal 
    7          31        normal            30        normal 
    processor temperature ranges
            below -5C is too cold
            above 80C is too hot
            low temperature warning below 10C
            high temperature warning above 70C
    IOA temperature ranges
            below -5C is too cold
            above 80C is too hot
            low temperature warning below 10C
            high temperature warning above 70C

    To display the environment of an E320 router:

    host1#show environment all
    
        chassis: 17 slot (id 0x3, rev. 0x0)
        fabric: 100 Gbps (rev. 1)
        fans: fanSubsystemOk
        nvs: ok (977MB flash disk, 29% full), matches running config
        power: A ok, B not present
        srp redundancy: mode is file-system-synchronization        auto-sync
    enabled, switch-on-error enabled
    status unknown
    *** slots: cards missing or offline
    online: 0 6 13
    offline: 7
    empty: 1 2 3 4 5 11 12 14 15 16
    fabric slots: ok
    online: 6 7 8 9 10
    line redundancy: none
    temperature: ok
    timing: primary
    primary: internal SC oscillator (ok)
    secondary: internal SC oscillator (ok)
    tertiary: internal SC oscillator (ok)
    auto-upgrade enabled
    fabric redundancy: ok
    *** system operational: no
                                temperature   temperature
    slot          type          (10C - 70C)     status
    ----   ------------------   -----------   -----------
    0      LM-4                     42        normal
    0/1    GE-4 IOA                 23        normal
    6      SRP-100                  32        normal
    6      SFM-100                  32        normal
    6/0    SRP IOA                  25        normal
    7      SFM-100                  30        normal
    8      SFM-100                  23        normal
    9      SFM-100                  25        normal
    10     SFM-100                  24        normal
    13     LM-4                     24        normal
    13/0   GE-4 IOA                 23        normal
    fabric temperature ranges
            below -5C is too cold
            above 79C is too hot
            low temperature warning below 10C
            high temperature warning above 70C
    processor temperature ranges
            below -5C is too cold
            above 79C is too hot
            low temperature warning below 10C
            high temperature warning above 70C
    IOA temperature ranges
            below -5C is too cold
            above 79C is too hot
            low temperature warning below 10C
            high temperature warning above 70C

    To display the environment on an E120 router:

    host1#show environment all
        chassis: 11 slot (id 0x8, rev. 0x0)
        fabric: 120 Gbps (rev. 1)
        fans: fanSubsystemOk
        nvs: ok (998MB flash disk, 14% full), matches running config
        power: A ok, B not present
        srp redundancy: mode is file-system-synchronization        auto-sync
    enabled, switch-on-error enabled
    in sync
    slots: ok
    online: 1 2 6
    standby: 7
    empty: 0 3 5
    fabric slots: ok
    online: 6 7 8 9 10
    line redundancy: none
    temperature: ok
    timing: primary
    primary: internal SC oscillator (ok)
    secondary: internal SC oscillator (ok)
    tertiary: internal SC oscillator (ok)
    auto-upgrade enabled
    fabric redundancy: ok
    system operational: yes
                      temperature   temperature
    slot     type     (10C - 56C)     status
    ----   --------   -----------   -----------
    1      LM-10          37        normal
    1/1    GE-8 IOA       35        normal
    2      LM-10          37        normal
    2/1    GE-8 IOA       39        normal
    4      LM-10A-ADV     37        normal
    6      SRP-120        40        normal
    6      SFM-120        40        normal
    6/0    SRP IOA        30        normal
    7      SRP-120        41        normal
    7      SFM-120        41        normal
    8      SFM-120        31        normal
    9      SFM-120        32        normal
    10     SFM-120        32        normal
    fabric temperature ranges
            below -5C is too cold
            above 79C is too hot
            low temperature warning below 10C
            high temperature warning above 56C
    processor temperature ranges
            below -5C is too cold
            above 79C is too hot
            low temperature warning below 10C
            high temperature warning above 51C
    IOA temperature ranges
            below -5C is too cold
            above 79C is too hot
            low temperature warning below 10C
            high temperature warning above 56C

    To display the temperature status table on an E120 router:

    host1#show environment table
    
                      temperature   temperature
    slot     type     (10C - 56C)     status
    ----   --------   -----------   -----------
    1      LM-10          37        normal
    1/1    GE-8 IOA       35        normal
    2      LM-10          37        normal
    2/1    GE-8 IOA       39        normal
    4      LM-10A-ADV     37        normal
    6      SRP-120        40        normal
    6      SFM-120        40        normal
    6/0    SRP IOA        30        normal
    7      SRP-120        41        normal
    7      SFM-120        41        normal
    8      SFM-120        31        normal
    9      SFM-120        32        normal
    10     SFM-120        32        normal
    fabric temperature ranges
            below -5C is too cold
            above 79C is too hot
            low temperature warning below 10C
            high temperature warning above 56C
    processor temperature ranges
            below -5C is too cold
            above 79C is too hot
            low temperature warning below 10C
            high temperature warning above 51C
    IOA temperature ranges
            below -5C is too cold
            above 79C is too hot
            low temperature warning below 10C
            high temperature warning above 56C

    Meaning

    Table 1 lists the show environment command output fields.

    Table 1: show environment Output Fields

    Field Name

    Field Description

    chassis

    Number of slots, midplane identifier, and hardware revision number:

    • 14Slot—5 Gbps, 14 slot midplane
    • midplaneId7Slot—5 Gbps, 7 slot midplane
    • midplaneIdRx1400—10 Gbps ASIC compatible, 12 line module slots, 2 SRP module slots for ERX14xx models
    • midplaneIdRx700—10 Gbps ASIC compatible, 5 line module slots, 2 SRP module slots for ERX7xx models
    • 17 slot—100 or 320 Gbps, 17-slot midplane for the E120 router
    • 11 slot—320 Gbps, 11-slot midplane for the E120 router

    fabric

    Capacity and hardware revision of the fabric

    fans

    Status of fans

    nvs

    Status and capacity of NVS and amount of space used

    power

    States of power feeds

    AC power

    For ERX310 router only; states of power feeds

    srp redundancy

    Availability of a redundant SRP module

    slots: cards missing or offline

    Status of each slot:

    • online
    • standby
    • offline
    • empty

    line redundancy

    Number of redundancy groups installed:

    • width—Number of slots the redundant midplane covers
    • spare—Slot that contains a spare line module
    • primary—Slot that contains the primary line module

    fabric redundancy

    Status of redundancy on the switch fabric on the E120 and E320 routers:

    • ok
    • none

    temperature

    Status of the system temperature

    timing

    Source of the timing signal:

    • primary—Type and status of the primary timing signal
    • secondary—Type and status of the secondary timing signal
    • tertiary—Type and status of the tertiary timing signal
    • auto-upgrade—Status of the auto-upgrade parameter, which enables the system to revert to a higher-priority timing source after switching to a lower-priority timing source.

    system operational

    Status of the system

    slot

    Number of the slot in which the module resides

    type

    Type of module in the slot on the E120 and E320 routers

    temperature

    Temperature of the line module, SRP module, or SFM on the E120 and E320 routers

    processor temperature

    Temperature of the line module or SRP module

    processor temperature status

    Temperature condition of the line module:

    • normal—Temperature is in normal range
    • too hot—Module is too hot; system will go into thermal protection mode if the temperature of modules in any two slots exceed 80° C
    • too cold—Module is too cold; system will go into thermal protection mode if the temperature of any module drops below –5° C

    IOA temperature

    Temperature of the corresponding I/O module or IOA

    IOA temperature status

    Temperature condition of the corresponding I/O module or IOA:

    • normal—Temperature is in normal range
    • too hot—Module is too hot; system will go into thermal protection mode if the temperature of modules in any two slots exceed 80° C
    • too cold—Module is too cold; system will go into thermal protection mode if the temperature of any module drops below –5° C

    processor temperature ranges

    Displays the temperature ranges for the line modules and SRP modules

    IOA temperature ranges

    Displays the temperature ranges for the I/O modules on ERX7xx models, ERX14xx models, and the ERX310 router or IOAs on the E120 and E320 routers

    fabric temperature ranges

    Displays the temperature ranges for the SRP modules and SFMs on the E120 and E320 routers

    Published: 2014-08-12