Help us improve your experience.

Let us know what you think.

Do you have time for a two-minute survey?

 

EnvCurrentHighTh

 

Table 1: Alarm Details

Parameter

Description

Code

envCurrentHighTh

Description/Cause

Current Above High Threshold: The output current at the AC power entry module (PEM) is above the high-current threshold. For information, see Output-current thresholds.

Entities Affected

Equipment (see respective table below).

Default Severity

Major

Service Affecting

Yes (true).

Alarm Clearing

See Clearing an EnvCurrentHighTh alarm.

Related Fault Hierarchy

See Environment fault hierarchy.

Table 2: Equipment

Entity Name

 

Fault Indicator

Equipment

Indicator

Status

pem:<chassis>/<slot>

AC PEM

See the PEM specifications in the BTI7800 Series Hardware Overview and Installation Guide.

Clearing an EnvCurrentHighTh Alarm

Note

Follow all applicable safety requirements as described in the BTI7800 Series Hardware Overview and Installation Guide.

Note

Refer to the BTI7800 Series Hardware Overview and Installation Guide before reseating (removing and reinstalling) or replacing equipment.

  1. Retrieve environment information to view output-current readings for the PEM:
    show environment current
  2. Reseat the PEM.
    • If the alarm has cleared, you have completed this procedure.

    • If the alarm does not clear, go to the next step.

  3. Replace the PEM.
  4. Check for alarms on the PEM.
    • If the alarm has cleared, you have completed this procedure.

    • If the alarm does not clear, contact your next level of support.