EnvCurrentLowTh

 

Table 1: Alarm Details

Parameter

Description

Code

envCurrentLowTh

Description/Cause

Current Below Low Threshold: The output current at the AC power entry module (PEM) is below the low-current threshold. For information, see Output-current thresholds.

Entities Affected

Equipment (see respective table below).

Default Severity

Major

Service Affecting

Yes (true).

Alarm Clearing

See Clearing an EnvCurrentLowTh alarm.

Related Fault Hierarchy

See Environment fault hierarchy.

Table 2: Equipment

Entity Name

 

Fault Indicator

Equipment

Indicator

Status

pem:<chassis>/<slot>

AC PEM

See the PEM specifications in the BTI7800 Series Hardware Overview and Installation Guide.

Clearing an EnvCurrentLowTh Alarm

Note

Follow all applicable safety requirements as described in the BTI7800 Series Hardware Overview and Installation Guide.

Note

Refer to the BTI7800 Series Hardware Overview and Installation Guide before reseating (removing and reinstalling) or replacing equipment.

  1. Retrieve environment information to view current readings for the PEM:
    show environment current
  2. Reseat the PEM.
    • If the alarm has cleared, you have completed this procedure.

    • If the alarm does not clear, go to the next step.

  3. Replace the PEM.
  4. Check for alarms on the PEM.
    • If the alarm has cleared, you have completed this procedure.

    • If the alarm does not clear, contact your next level of support.