EqptBrownout

 

Table 1: Alarm Details

Parameter

Description

Code

eqptBrownout

Description

Equipment Brownout: A brownout condition has been detected on a UFM that is installed in a BTI7800 Series chassis powered by a DC power entry module (PEM).

Caution: Continued operation might cause equipment damage.

Entities Affected

UFM modules (see table below)

Note: For UFM3 and UFM4 modules, this alarm results in an automatic cold reload of the UFM.

Possible Cause

The supply voltage to a UFM is lower than the minimum normal voltage threshold for the module, but not lower than the power-off threshold.

Default Severity

Major

Service Affecting

Yes (true)

Alarm Clearing

See Clearing an EqptBrownout alarm.

Related Fault Hierarchy

Table 2: UFM Modules

Entity Name

 

Fault Indicator

Module

Indicator

Status

ufm:<chassis>/<slot>

UFM

See BTI7800 Series Module and BIC LED Behavior.

Clearing an EqptBrownout Alarm

Note

Follow all applicable safety requirements as described in the BTI7800 Series Hardware Overview and Installation Guide.

  1. Retrieve environment information to view voltage data for the UFM and each PEM installed in the chassis:
    show environment voltage
  2. Check for and clear alarms raised against the PEMs, and ensure that they are properly seated and connected to power.
  3. Check for alarms on the UFM.
    • If the alarm has cleared, you have completed this procedure.

    • If the alarm does not clear, contact your next level of support.