EnvVoltHighTh
Table 1: Alarm Details
Parameter | Description |
---|---|
Code |
|
Description/Cause | Environment Voltage Above High Threshold: The voltage on the equipment (PEM) or module exceeds the high-voltage threshold. For information, see Voltage thresholds. Caution: Continued operation might cause equipment damage. |
Entities Affected |
|
Default Severity | Major |
Service Affecting | Yes (true). |
Alarm Clearing | |
Related Fault Hierarchy |
Table 2: Equipment
Entity Name | Fault Indicator | ||
---|---|---|---|
Equipment | Indicator | Status | |
pem:<chassis>/<slot> | AC PEM | See the PEM specifications in the BTI7800 Series Hardware Overview and Installation Guide. |
Table 3: Traffic Modules
Entity Name | Fault Indicator | ||
---|---|---|---|
Module | Indicator | Status | |
ufm:<chassis>/<slot> | UFM | ||
amp:<chassis>/<slot> | AMP1 | ||
wps:<chassis>/<slot> | WPS4 |
Clearing an EnvVoltHighTh Alarm
Follow all applicable safety requirements as described in the BTI7800 Series Hardware Overview and Installation Guide.
Refer to the BTI7800 Series Software Configuration Guide before rebooting a traffic module or to the BTI7800 Series Hardware Overview and Installation Guide before reseating (removing and reinstalling) or replacing equipment or traffic modules.
- Retrieve environment information to view voltage readings
for the equipment or traffic module:
show environment voltage
- Do the following:
If the alarm is raised against the equipment, go to step 5.
If the alarm is raised against a traffic module, go to the next step.
- Perform a warm reload of the traffic module.
system reload warm module
If the alarm has cleared, you have completed this procedure.
If the alarm does not clear, go to the next step.
- Perform a cold reload of the traffic module.
system reload cold module
If the alarm has cleared, you have completed this procedure.
If the alarm does not clear, go to the next step.
- Reseat
the equipment or module.
If the alarm has cleared, you have completed this procedure.
If the alarm does not clear, go to the next step.
- Replace the equipment or module.
- Check for alarms on the equipment or module.
If the alarm has cleared, you have completed this procedure.
If the alarm does not clear, contact your next level of support.