EnvVoltHighTh

 

Table 1: Alarm Details

Parameter

Description

Code

envVoltHighTh

Description/Cause

Environment Voltage Above High Threshold: The voltage on the equipment (PEM) or module exceeds the high-voltage threshold. For information, see Voltage thresholds.

Caution: Continued operation might cause equipment damage.

Entities Affected

  • Equipment (see respective table below).

  • Traffic modules (see respective table below).

Default Severity

Major

Service Affecting

Yes (true).

Alarm Clearing

See Clearing an EnvVoltHighTh alarm.

Related Fault Hierarchy

See Environment fault hierarchy.

Table 2: Equipment

Entity Name

 

Fault Indicator

Equipment

Indicator

Status

pem:<chassis>/<slot>

AC PEM

See the PEM specifications in the BTI7800 Series Hardware Overview and Installation Guide.

Table 3: Traffic Modules

Entity Name

 

Fault Indicator

Module

Indicator

Status

ufm:<chassis>/<slot>

UFM

See BTI7800 Series Module and BIC LED Behavior.

amp:<chassis>/<slot>

AMP1

wps:<chassis>/<slot>

WPS4

Clearing an EnvVoltHighTh Alarm

Note

Follow all applicable safety requirements as described in the BTI7800 Series Hardware Overview and Installation Guide.

Note

Refer to the BTI7800 Series Software Configuration Guide before rebooting a traffic module or to the BTI7800 Series Hardware Overview and Installation Guide before reseating (removing and reinstalling) or replacing equipment or traffic modules.

  1. Retrieve environment information to view voltage readings for the equipment or traffic module:
    show environment voltage
  2. Do the following:
    • If the alarm is raised against the equipment, go to step 5.

    • If the alarm is raised against a traffic module, go to the next step.

  3. Perform a warm reload of the traffic module.
    system reload warm module
    • If the alarm has cleared, you have completed this procedure.

    • If the alarm does not clear, go to the next step.

  4. Perform a cold reload of the traffic module.
    system reload cold module
    • If the alarm has cleared, you have completed this procedure.

    • If the alarm does not clear, go to the next step.

  5. Reseat the equipment or module.
    • If the alarm has cleared, you have completed this procedure.

    • If the alarm does not clear, go to the next step.

  6. Replace the equipment or module.
  7. Check for alarms on the equipment or module.
    • If the alarm has cleared, you have completed this procedure.

    • If the alarm does not clear, contact your next level of support.