Help us improve your experience.

Let us know what you think.

Do you have time for a two-minute survey?

 

EnvTempHighTh

 

Table 1: Alarm Details

Parameter

Description

Code

envTempHighTh

Description/Cause

Environment Temperature Above High Threshold: The temperature at the equipment or module has exceeded the high temperature threshold. For information, see Temperature thresholds - equipment and traffic modules.

Entities Affected

  • Equipment (see respective table below).

  • Management and traffic modules (see respective table below).

Default Severity

Major

Service Affecting

Yes (true).

Alarm Clearing

See Clearing an EnvTempHighTh alarm.

Related Fault Hierarchy

See Environment fault hierarchy.

Table 2: Equipment

Entity Name

 

Fault Indicator

Equipment

Indicator

Status

pem:<chassis>/<slot>

PEM

See equipment specifications in the BTI7800 Series Hardware Overview and Installation Guide.

fan:<chassis>/<slot>

Cooling module

Entity Name

 

Fault Indicator

Module

Indicator

Status

cmm:<chassis>/<slot>

CMM

See BTI7800 Series Module and BIC LED Behavior.

ufm:<chassis>/<slot>

UFM

bic:<chassis>/<slot>/<subslot>

BIC

roadm:<chassis>/<slot>

ROADM2

ila:<chassis>/<slot>

ILA

amp:<chassis>/<slot>

AMP1

wps:<chassis>/<slot>

WPS4

Clearing an EnvTempHighTh Alarm

Note

Follow all applicable safety requirements as described in the BTI7800 Series Hardware Overview and Installation Guide.

Note

Refer to the BTI7800 Series Software Configuration Guide before rebooting a traffic module or to the BTI7800 Series Hardware Overview and Installation Guide before reseating (removing and reinstalling) or replacing equipment or traffic modules.

  1. Retrieve environment information to view the temperature reading for the equipment or traffic module:
    show environment temperature
  2. Check for and clear a FanSpeedLowTh alarm on each cooling module installed in the chassis.
  3. Check for alarms on the affected equipment or traffic module.
    • If the alarm has cleared, you have completed this procedure.

    • If the alarm does not clear, go to the next step.

  4. Ensure that the ambient temperature is within the specified range for chassis operation. For information, see the BTI7800 Series Hardware Overview and Installation Guide.
  5. Check for alarms on the affected equipment or traffic module.
    • If the alarm has cleared, you have completed this procedure.

    • If the alarm does not clear, go to the next step.

  6. Do the following:
    • If the alarm is raised against equipment, reseat the equipment.

    • If the alarm is raised against a traffic module, perform a warm reboot of the module.

  7. Check for alarms on the equipment or module.
    • If the alarm has cleared, you have completed this procedure.

    • If the alarm does not clear, go to the next step.

  8. Replace the equipment or module.
  9. Check for alarms on the equipment or module.
    • If the alarm has cleared, you have completed this procedure.

    • If the alarm does not clear, contact your next level of support.