    EnvVoltHighTh

    Table 1: Alarm Details

    Parameter

    Description

    Code

    envVoltHighTh

    Description/Cause

    Environment Voltage Above High Threshold: The voltage on the equipment (PEM) or module exceeds the high-voltage threshold. For information, see Voltage thresholds.

    Caution: Continued operation might cause equipment damage.

    Entities Affected

    • Equipment (see respective table below).
    • Traffic modules (see respective table below).

    Default Severity

    Major

    Service Affecting

    Yes (true).

    Alarm Clearing

    See Clearing an EnvVoltHighTh alarm.

    Related Fault Hierarchy

    See Environment fault hierarchy.

    Table 2: Equipment

    Entity Name

     

    Fault Indicator

    Equipment

    Indicator

    Status

    pem:<chassis>/<slot>

    AC PEM

    See the PEM specifications in the BTI7800 Series Hardware Overview and Installation Guide.

    Table 3: Traffic Modules

    Entity Name

     

    Fault Indicator

    Module

    Indicator

    Status

    ufm:<chassis>/<slot>

    UFM

    See BTI7800 Series Module and BIC LED Behavior.

    amp:<chassis>/<slot>

    AMP1

    wps:<chassis>/<slot>

    WPS4

    Clearing an EnvVoltHighTh Alarm

    Note: Follow all applicable safety requirements as described in the BTI7800 Series Hardware Overview and Installation Guide.

    Note: Refer to the BTI7800 Series Software Configuration Guide before rebooting a traffic module or to the BTI7800 Series Hardware Overview and Installation Guide before reseating (removing and reinstalling) or replacing equipment or traffic modules.

    1. Retrieve environment information to view voltage readings for the equipment or traffic module:
      show environment voltage
    2. Do the following:
      • If the alarm is raised against the equipment, go to step 5.
      • If the alarm is raised against a traffic module, go to the next step.
    3. Perform a warm reload of the traffic module.
      system reload warm module
      • If the alarm has cleared, you have completed this procedure.
      • If the alarm does not clear, go to the next step.
    4. Perform a cold reload of the traffic module.
      system reload cold module
      • If the alarm has cleared, you have completed this procedure.
      • If the alarm does not clear, go to the next step.
    5. Reseat the equipment or module.
      • If the alarm has cleared, you have completed this procedure.
      • If the alarm does not clear, go to the next step.
    6. Replace the equipment or module.
    7. Check for alarms on the equipment or module.
      • If the alarm has cleared, you have completed this procedure.
      • If the alarm does not clear, contact your next level of support.

    Modified: 2017-07-26