    EnvTempHighTh

    Table 1: Alarm Details

    Parameter

    Description

    Code

    envTempHighTh

    Description/Cause

    Environment Temperature Above High Threshold: The temperature at the equipment or module has exceeded the high temperature threshold. For information, see Temperature thresholds - equipment and traffic modules.

    Entities Affected

    • Equipment (see respective table below).
    • Management and traffic modules (see respective table below).

    Default Severity

    Major

    Service Affecting

    Yes (true).

    Alarm Clearing

    See Clearing an EnvTempHighTh alarm.

    Related Fault Hierarchy

    See Environment fault hierarchy.

    Table 2: Equipment

    Entity Name

     

    Fault Indicator

    Equipment

    Indicator

    Status

    pem:<chassis>/<slot>

    PEM

    See equipment specifications in the BTI7800 Series Hardware Overview and Installation Guide.

    fan:<chassis>/<slot>

    Cooling module

    Entity Name

     

    Fault Indicator

    Module

    Indicator

    Status

    cmm:<chassis>/<slot>

    CMM

    See BTI7800 Series Module and BIC LED Behavior.

    ufm:<chassis>/<slot>

    UFM

    bic:<chassis>/<slot>/<subslot>

    BIC

    roadm:<chassis>/<slot>

    ROADM2

    ila:<chassis>/<slot>

    ILA

    amp:<chassis>/<slot>

    AMP1

    wps:<chassis>/<slot>

    WPS4

    Clearing an EnvTempHighTh Alarm

    Note: Follow all applicable safety requirements as described in the BTI7800 Series Hardware Overview and Installation Guide.

    Note: Refer to the BTI7800 Series Software Configuration Guide before rebooting a traffic module or to the BTI7800 Series Hardware Overview and Installation Guide before reseating (removing and reinstalling) or replacing equipment or traffic modules.

    1. Retrieve environment information to view the temperature reading for the equipment or traffic module:
      show environment temperature
    2. Check for and clear a FanSpeedLowTh alarm on each cooling module installed in the chassis.
    3. Check for alarms on the affected equipment or traffic module.
      • If the alarm has cleared, you have completed this procedure.
      • If the alarm does not clear, go to the next step.
    4. Ensure that the ambient temperature is within the specified range for chassis operation. For information, see the BTI7800 Series Hardware Overview and Installation Guide.
    5. Check for alarms on the affected equipment or traffic module.
      • If the alarm has cleared, you have completed this procedure.
      • If the alarm does not clear, go to the next step.
    6. Do the following:
      • If the alarm is raised against equipment, reseat the equipment.
      • If the alarm is raised against a traffic module, perform a warm reboot of the module.
    7. Check for alarms on the equipment or module.
      • If the alarm has cleared, you have completed this procedure.
      • If the alarm does not clear, go to the next step.
    8. Replace the equipment or module.
    9. Check for alarms on the equipment or module.
      • If the alarm has cleared, you have completed this procedure.
      • If the alarm does not clear, contact your next level of support.

    Modified: 2017-04-25