Troubleshooting the T1600 Power System
Problem
The following alarms, LEDs, and other conditions indicate
a problem with the power system:
- If all power supplies have failed, the system temperature
might have exceeded the threshold, causing the system to shut down.
- The blue DC OK LED blinks when a power supply
detects a fault (the power supply fails, does not have sufficient
airflow, is going through a startup test, or is not properly inserted).
- The yellow OVER TEMP LED lights when a power
supply is not receiving enough airflow to maintain proper temperature.
- The green AC OK LED is off when an AC power supply
is not receiving voltage.
Solution
- Check the LEDs on each three-input 240-A DC or four-input
240-A DC power supply faceplate.
- DC OK power supply LED is blinking—Check
the red alarm LED on the craft interface.
- DC OK power supply LED is off and no red
alarm condition exists—Check that the circuit breakers are switched
to the ON position (|).
- DC OK LED on one or both of the power supplies
is not lit—Check the power supply fans to see if they are operating.
- OVER TEMP LED on one of the power supplies
lights—Check the fans and air filters to be sure they are functioning
and providing sufficient airflow through the chassis.
- Check the LEDs on each three-phase delta or wye power
supply faceplate.
- AC OK power supply LED is off—Check
that the power supply is receiving voltage.
- DC OK power supply LED is blinking—Check
the red alarm LED on the craft interface.
- DC OK LED on one or both of the power supplies
is not lit—Check the power supply fans to see if they are operating.
- OVER TEMP LED on one of the power supplies
lights—Check the fans and air filters to be sure they are functioning
and providing sufficient airflow through the chassis.
- Check the display on the craft interface to determine
the source of a yellow or red alarm (see Table 1). Junos OS constantly updates the screen with status information
for each component.
 | Note:
On the display and in the CLI, the power supplies are
referred to as PEM0 and PEM1, from top to bottom. If the system temperature exceeds the threshold, Junos OS shuts
down all power supplies so that no status is displayed. Junos OS also can shut down one of the power supplies for other
reasons. In that case, the remaining power supply assumes the load,
and you can still view the system status through the CLI or display. |
- Verify that the source circuit breaker has the proper
current rating.
 | Note:
All inputs on a DC power supply in slot PEM0 must be
powered by dedicated power feeds derived from feed A, and all inputs
on a DC power supply in slot PEM 1 must be powered by dedicated power
feeds derived from feed B. This configuration provides the commonly
deployed A/B feed redundancy for the system. |
 | Note:
The AC power cord on an AC power supply in slot PEM0
must be powered by a dedicated power feed derived from feed A, and
The AC power cord on an AC power supply in slot PEM 1 must be powered
by dedicated power feeds derived from feed B. This configuration provides
the commonly deployed A/B feed redundancy for the system. |
- Verify that the DC power cables or AC power cord from
the power source to the router are not damaged. If the insulation
is cracked or broken, immediately replace the DC power cable or AC
power cord.
- Connect the power supply to a different power source with
a new DC power cable or AC power cord. If the power supply DC OK LED still does not light, the power supply is the source of the
problem. Replace the power supply with a spare.
DC OK LED on the installed spare does not light—the
replaced power supply might be faulty. To return it for replacement,
see Contacting Customer Support.
- If you cannot determine the cause of the problem or need
additional assistance, see Contacting Customer Support.
Table 1: Power
System Chassis Alarms
Component | Alarm Type | LCD Message | CLI Message |
|---|
Power supplies | Red | PEM pem-number Over Temp | PEM pem-number Over Temperature |
PEM pem-number Output Fail | PEM pem-number Output Failure |
PEM pem-number Input Fail | PEM pem-number Input Failure |
Yellow | PEM pem-number Removed | PEM pem-number Removed |
Published: 2011-12-20