During normal operation:
The following indicate a problem with a TXP-CIP:
To troubleshoot the TXP-CIPs:
user@host> show chassis environment cip sfc
0CIP 0 status:
State Online Active
Temperature 30 degrees C / 86 degrees F
Power 1
1.0 V 1015 mV
1.8 V 1820 mV
2.5 V 2491 mV
3.3 V 3306 mV
3.3 V bias 3300 mV
5.0 V 5085 mV
9.0 V 9087 mV
Bus Revision 74
CIP 1 status:
State Online Inactive
Temperature 30 degrees C / 86 degrees F
Power 1
1.0 V 1008 mV
1.8 V 1807 mV
2.5 V 2494 mV
3.3 V 3293 mV
3.3 V bias 3300 mV
5.0 V 5078 mV
9.0 V 8991 mV
Bus Revision 74
user@host> show chassis cipsfc0-cip0 Eswitch Port Type Connected-to Link Speed Duplex Auto-Neg 0 4 XE SFC1 Down 0 Full Off 0 5 XE SFC0 Down 0 Full Off 0 6 XE SFC3 Down 0 Full Off 0 7 XE SFC2 Down 0 Full Off 0 8 XE SFC4 Down 0 Full Off 1 0 GE LCC0 Up 1000Mbps Full On 1 1 GE LCC8 Down 0 Half On 1 2 GE LCC1 Up 1000Mbps Full On 1 3 GE LCC9 Down 0 Half On 1 4 GE LCC2 Up 1000Mbps Full On 1 5 GE LCC10 Down 0 Half On 1 6 GE LCC3 Up 1000Mbps Full On 1 7 GE LCC11 Down 0 Half On 1 8 GE LCC4 Down 0 Half On 1 9 GE LCC12 Down 0 Half On 1 10 GE LCC5 Down 0 Half On 1 11 GE LCC13 Down 0 Half On 1 12 GE LCC6 Down 0 Half On 1 13 GE LCC14 Down 0 Half On 1 14 GE LCC7 Down 0 Half On 1 15 GE LCC15 Down 0 Half On 1 16 GE GE16 Down 0 Half On 1 17 GE GE17 Down 0 Half On
The text in the column labeled ”LCD Message” appears in the display of the craft interface. The text in the column labeled “CLI Message” appears in the output from the show chassis alarms command.
Table 1: TXP-CIP Alarm Messages
Alarm Type | LCD Message | CLI Message | Alarm Condition | Solution |
|---|---|---|---|---|
Red | CIP cip-number Failed | CIP cip-numberFailed | A TXP-CIP has failed. | Replace the TXP-CIP. |
Yellow | CIP cip-number Removed | CIP cip-number Removed | A TXP-CIP has been removed. | Reinstall the TXP-CIP in the chassis. |
CIP cip-number voltage sensor failed | CIP cip-number voltage sensor failed | A failure occured in reading the voltage sensors on the TXP-CIP. | Replace the TXP-CIP. |