Home > Support > Technical Documentation > Connecting the SRX650 Services Gateway to the DC Power Supply
Print
Rate and give feedback:  Feedback Received. Thank You!
Rate and give feedback: 
Close
This document helped resolve my issue.  Yes No

Additional Comments

800 characters remaining

May we contact you if necessary?

Name:  
E-mail: 
Submitting...

Documentation Search

Advanced Search |  Search Tips
 

Related Documentation

  • Preventing Electrostatic Discharge Damage to the SRX650 Services Gateway
  • Grounding the SRX650 Services Gateway
  • Organizing Interface Cables on the SRX650 Services Gateway
  • SRX650 Services Gateway General Safety Guidelines and Warnings
 

Connecting the SRX650 Services Gateway to the DC Power Supply

Caution: Do not mix AC and DC power supplies within the same services gateway. Damage to the device might occur.

The 645 W DC power supply with PoE support is available for the SRX650 Services Gateway.

Warning: Before performing the following procedure, ensure that power is removed from the DC circuit. To ensure that all power is off, locate the circuit breaker on the panel board that services the DC circuit, switch the circuit breaker to the off position (O), and tape the switch handle of the circuit breaker in the off position.

You connect DC power to the device by attaching power cables from the external DC power sources to the terminal studs on the power supply faceplate. You must provide the power cables (the cable lugs are supplied with the services gateway).

To connect the DC source power cables to the services gateway power supply:

  1. Switch off the dedicated facility circuit breakers. Ensure that the voltage across the DC power source cable leads is 0 V and that there is no chance that the cable leads might become active during installation.
  2. Attach an electrostatic discharge (ESD) grounding strap to your bare wrist, and connect the strap to the ESD point on the side of the chassis.
  3. Remove the clear plastic cover protecting the terminal studs on the faceplate.
  4. Verify that the DC power cables are correctly labeled before making connections to the power supply. In a typical power distribution scheme where the return is connected to chassis ground at the battery plant, you can use a multimeter to verify that the ohm output of the –48V and RTN DC cables to chassis ground. The cable with very large resistance (indicating an open circuit) to chassis ground will be –48V and the cable with very low resistance (indicating a closed circuit) to chassis ground will be RTN.

    Caution: You must ensure that power connections maintain the proper polarity. The power source cables might be labeled (+) and (–) to indicate their polarity. There is no standard color coding for DC power cables. The color coding used by the external DC power source at your site determines the color coding for the leads on the power cables that attach to the terminal studs on the power supply.

  5. Remove the screws and square washers from the terminals. Use a number 2 Phillips screwdriver.
  6. Secure each power cable lug to the terminals, first with the square washer, then with the screw. Apply between 23 lb-in. (2.6 Nm) and 25 lb-in. (2.8 Nm) of torque to each screw.
    • Secure each positive (+) DC source power cable lug to a RTN (return) terminal.
    • Secure each negative (–) DC source power cable lug to a –48V (input) terminal.
  7. Replace the clear plastic cover over the terminal studs on the faceplate.
  8. Verify that the power cables are connected correctly, that they are not touching or blocking access to services gateway components, and that they do not drape where people could trip on them.

Note: The services gateway must be connected to earth ground during normal operation. The protective earthing terminal on the side of the chassis is provided to connect the services gateway to ground.

Caution: We recommend using a surge protector for the power connection.

 

Related Documentation

  • Preventing Electrostatic Discharge Damage to the SRX650 Services Gateway
  • Grounding the SRX650 Services Gateway
  • Organizing Interface Cables on the SRX650 Services Gateway
  • SRX650 Services Gateway General Safety Guidelines and Warnings
 

Published: 2010-12-01

 
  • About Juniper
  • The New Network
  • Investor Relations
  • Press Releases
  • Newsletters
  • Juniper Offices
  • Resources
  • How to Buy
  • Partner Locator
  • Image Library
  • Visio Templates
  • Security Center
  • Community
  • Forums
  • Blogs
  • Junos Central
  • Social Media
  • Support
  • Technical Documentation
  • Knowledge Base (KB)
  • Software Downloads
  • Product Licensing
  • Contact Support
Site Map / RSS Feeds / Careers / Accessibility / Feedback / Privacy & Policy / Legal Notices
Copyright© 1999-2012 Juniper Networks, Inc. All rights reserved.
Help
|
My Account
|
Log Out