Replacing a T1600 Three-Phase Delta AC Power Supply
The T1600 router has either
one nonredundant power supply or two redundant, load-sharing power
supplies. Each redundant power supply is hot-insertable and hot-removable.
When a redundant power supply is powered down or removed, the other
power supply automatically assumes the entire electrical load for
the router. If you have only one power supply, you must power off
the system before removing the power supply.
- Removing a T1600 Three-Phase Delta AC Power Supply
- Installing a T1600 Three-Phase Delta AC Power Supply
Removing a T1600 Three-Phase Delta AC Power Supply
To remove a three-phase delta AC power supply:
- Switch off the customer site circuit breakers to the power
supply being removed. Make sure that the voltage across the AC power
source cord is 0 V and that there is no chance that the cord might
become active during the removal process.
- Attach an electrostatic discharge (ESD) grounding strap
to your bare wrist, and connect the strap to one of the ESD points
on the chassis.
- Switch the power switch on the power supply faceplate
to the standby position.
 | Note:
After powering off a power supply, wait at least 60 seconds
before turning it back on. |
- Remove the ESD grounding strap from the ESD point on the
chassis, and attach it to an approved site ESD grounding point. See
the instructions for your site.
- Disconnect the AC power cord (see Figure 1) from the power source.
Figure 1: Three-Phase Delta
AC Power Supply
- Remove the ESD grounding strap from the approved site
ESD grounding point. See the instructions for your site. Reconnect
the strap to one of the ESD points on the chassis.
- Using a number 2 Phillips (+) screwdriver, loosen the
two screws on the door of the metal wiring compartment that protects
the AC terminal block.
- Open the door of the metal wiring compartment.
Disconnect the wires from the AC terminal block on the
three-phase delta AC power supply (Figure 2), Loosen each of
the input terminals or grounding point screws, and remove each wire
from the grounding point or input terminal.
 | Note:
The terminal connections have either slotted screws or
hex screws. Use a 1/4-in. slotted screwdriver for the slotted screws.
Use a 5/32-in (4-mm) Allen wrench for the 5/16-in hex screws. |
- Remove the wire labeled L3 from the L3 input terminal.
- Remove the wire labeled L2 from the L2 input terminal.
- Remove the wire labeled L1 from the L1 input terminal.
- Remove the wire labeled GND from the grounding
point labeled GND.
Figure 2: Disconnecting
the Power Cord from a Three-Phase Delta AC Power Supply
- Loosen the plastic cable tie fastening the AC power cord
to the power supply.
- Loosen and remove the retaining nut from the AC power
cord.
- Pull the AC power cord out of the metal wiring compartment.
- Carefully move the AC power cable out of the way.
- Disconnect the AC power cord from the AC power supply.
- Loosen the captive screws on the lower corners of the
power supply faceplate completely.
- Twist the ejector handles on the upper corners of the
faceplate counterclockwise to unseat the power supply.
- Grasp the handle on the power supply faceplate and pull
firmly. Slide it halfway out of the chassis (see Figure 3).
 | Caution:
Each three-phase delta AC power supply weighs approximately 31.0 lb. (14.06 kg).
Be prepared to support the full weight of the power supply as you
remove it from the router. |
- Place one hand underneath the power supply to support
it and slide it completely out of the chassis.
Figure 3: Removing a Three-Phase Delta AC Power Supply
 | Warning:
Do not touch the power connectors on the rear of the
power supply (see Figure 4).
They can contain dangerous voltages. |
Figure 4: Rear of the Power Supply
Showing Midplane Connectors
Installing a T1600 Three-Phase Delta AC Power Supply
Each three-phase delta AC power supply weighs approximately 31.0 lb. (14.06 kg).
To install a three-phase delta AC power supply:
- Make sure that the voltage across the AC power source
cord leads is 0 V and that there is no chance that the cord might
become active during installation.
- Attach an electrostatic discharge (ESD) grounding strap
to your bare wrist, and connect the strap to one of the ESD points
on the chassis.
- Switch the power switch on the power supply faceplate
to the standby position.
- Using both hands, slide the power supply into the chassis
until you feel resistance (see Figure 6).
- Twist the ejector handles at the upper corners of the
power supply faceplate clockwise until they stop.
- Tighten the captive screws at the lower corners of the
power supply faceplate to secure the power supply in the chassis.
- Using a number 2 Phillips (+) screwdriver, loosen the
two screws on the door of the metal wiring compartment that protects
the AC terminal block.
- Open the door of the metal wiring compartment.
- Unscrew the retaining nut from the AC power cord.
- Place the retaining nut inside the metal wiring compartment.
- Put the wires of the AC power cord through the hole of
the metal wiring compartment.
- Screw the retaining nut onto the AC power cord to secure
it to the metal wiring compartment.
Connect the wires to the AC terminal block on the three-phase
delta AC power supply (Figure 5). Loosen each of the input terminal or grounding point screws, insert
the wire into the grounding point or input terminal, and tighten the
screw.
 | Note:
The terminal connections have either slotted screws or
hex screws. Use a 1/4-in. slotted screwdriver for the slotted screws.
Use a 5/32-in (4-mm) Allen wrench for the 5/16-in hex screws. |
- Insert the wire labeled GND into the grounding
point labeled GND.
- Insert the wire labeled L1 into the L1 input terminal
- Insert the wire labeled L2 into the L2 input terminal.
- Insert the wire labeled LC3 into the LC3 input terminal.
Figure 5: Connecting Power to a Three-Phase Delta AC Power Supply
- Verify that the power cord wire connections are correct.
- Using a number 2 Phillips (+) screwdriver, tighten the
two captive screws on the metal AC wiring compartment.
- Verify that the AC power cord is not touching or blocking
access to router components, and that it does not drape where
people could trip on it.
- Remove the ESD grounding strap from the ESD points on
the chassis. Connect the strap to an approved site ESD grounding point.
See the instructions for your site.
- Connect the AC power cord plug to the power source.
- Switch on the customer site circuit breakers to provide
voltage to the AC power cord.
- Remove the ESD grounding strap from the approved site
ESD grounding point. See the instructions for your site. Reconnect
the strap to one of the ESD points on the chassis.
- Verify that the AC OK LED on the power supply
faceplate is lit steadily, indicating that the AC terminal block is
receiving power.
- Switch the power switch on the power supply to the ON position (|) to provide power to the router components.
- Verify that the DC OK LED on the power supply
faceplate is lit steadily, indicating that the power supply is correctly
installed and is functioning properly. The DC OK LED blinks
momentarily, then lights steadily.
 | Note:
After a power supply is powered on, it can take up to
60 seconds for status indicators—such as the LEDs on the power
supply, the command output displays, and messages on the LED display
on the craft interface—to indicate that the power supply is
functioning normally. Ignore error indicators that appear during the
first 60 seconds. |
Figure 6: Installing
a Three-Phase Delta AC Power Supply
Published: 2011-12-20