Installing an SRX5600 Services Gateway DC Power Supply
To install a DC power supply (see Figure 1):
- Ensure that the voltage across the DC power source
cable leads is 0 V and that there is no chance that the cable
leads might become active during installation.
- Attach an electrostatic discharge (ESD) grounding
strap to your bare wrist, and connect the strap to one of the ESD
points on the chassis.
- Switch the circuit breaker on the power supply
faceplate to the OFF position O.
- Using both hands, slide the power supply straight
into the chassis until the power supply is fully seated in the chassis
slot. The power supply faceplate should be flush with any adjacent
power supply faceplate (see Figure 1).
- Tighten the captive screws on the lower edge of
the power supply faceplate.
- Remove the clear plastic cover protecting the terminal
studs on the faceplate.
- Remove the nuts and washers from the terminal studs.
- Secure each power cable lug to the terminal studs,
first with the washer, then with the nut. Apply between 23 lb-in.
(2.6 Nm) and 25 lb-in. (2.8 Nm) of torque to each nut.
(see Figure 2).
- Attach the positive (+) DC source power cable lug to the RTN (return) terminal.
- Attach the negative (–) DC source power cable lug
to the –48V (input) terminal.
 | Caution:
You must ensure that power connections maintain the proper polarity.
The power source cables might be labeled (+) and (–) to indicate their polarity. There is no standard color coding for
DC power cables. The color coding used by the external DC power source
at your site determines the color coding for the leads on the power
cables that attach to the terminal studs on each power supply. |
 | Note:
For the SRX5600 services gateway, the DC power supplies
in PEM0 and PEM1 must be powered by dedicated power
feeds derived from feed A, and the DC power supplies in PEM2 and PEM3must be powered by dedicated power feeds
derived from feed B. This configuration provides the commonly
deployed A/B feed redundancy for the system. |
- Replace the clear plastic cover over the terminal
studs on the faceplate.
- Route the power cables along the cable restraint
towards the left or right corner of the chassis. If needed to hold
the power cables in place, thread plastic cable ties, which you must
provide, through the openings on the cable restraint.
- Verify that the power cabling is correct, that
the cables are not touching or blocking access to services gateway
components, and that they do not drape where people could trip on
them.
- Verify that the INPUT OK LED on the power
supply is lit green.
- Switch the circuit breaker on the power supply
to the ON position — and observe the status
LEDs on the power supply faceplate. If the power supply is correctly
installed and functioning normally, the PWR OK, BRKR ON, and INPUT OK LEDs light green steadily.
 | Note:
If more than one power supply is being installed, turn
on all power supplies at the same time. |
 | Note:
An SCB must be present for the PWR OK LED to
go on. |
Figure 1: Installing
a DC Power Supply
Figure 2: Connecting DC Power
Published: 2011-03-29