Juniper Networks
Log in
|
How to Buy
|
Contact Us
|
United States (Change)
Choose Country
Close

Choose Country

North America

  • United States

Europe

  • Deutschland - Germany
  • España - Spain
  • France
  • Italia - Italy
  • Россия - Russia
  • United Kingdom

Asia Pacific

  • Asean Region (Vietnam, Indonesia, Singapore, Malaysia)
  • Australia
  • 中国 - China
  • India
  • 日本 - Japan
  • 대한민국 - Korea
  • 台灣 - Taiwan
Solutions
Products & Services
Company
Partners
Support
Education
Community
Security Intelligence Center

Technical Documentation

Support
Technical Documentation
Content Explorer New
 
Enterprise MIBs
 
EOL Documentation
 
File Format Help
 
Glossary
 
Portable Libraries
 
 
Home > Support > Technical Documentation > SRX Series Services Gateways > SRX5600 > Installing an SRX5600 Services Gateway DC Power Supply
Print
Rate and give feedback:  Feedback Received. Thank You!
Rate and give feedback: 
Close
This document helped resolve my issue.  Yes No

Additional Comments

800 characters remaining

May we contact you if necessary?

Name:  
E-mail: 
Submitting...
 

Related Documentation

  • Preventing Electrostatic Discharge Damage to the SRX5600 Services Gateway
  • Removing an SRX5600 Services Gateway DC Power Supply
  • Replacing an SRX5600 Services Gateway DC Power Supply Cable
 

Installing an SRX5600 Services Gateway DC Power Supply

To install a DC power supply (see Figure 1):

  1. Ensure that the voltage across the DC power source cable leads is 0 V and that there is no chance that the cable leads might become active during installation.
  2. Attach an electrostatic discharge (ESD) grounding strap to your bare wrist, and connect the strap to one of the ESD points on the chassis.
  3. Switch the circuit breaker on the power supply faceplate to the OFF position O.
  4. Using both hands, slide the power supply straight into the chassis until the power supply is fully seated in the chassis slot. The power supply faceplate should be flush with any adjacent power supply faceplate (see Figure 1).
  5. Tighten the captive screws on the lower edge of the power supply faceplate.
  6. Remove the clear plastic cover protecting the terminal studs on the faceplate.
  7. Remove the nuts and washers from the terminal studs.
  8. Secure each power cable lug to the terminal studs, first with the washer, then with the nut. Apply between 23 lb-in. (2.6 Nm) and 25 lb-in. (2.8 Nm) of torque to each nut. (see Figure 2).
    1. Attach the positive (+) DC source power cable lug to the RTN (return) terminal.
    2. Attach the negative (–) DC source power cable lug to the –48V (input) terminal.

    Caution: You must ensure that power connections maintain the proper polarity. The power source cables might be labeled (+) and (–) to indicate their polarity. There is no standard color coding for DC power cables. The color coding used by the external DC power source at your site determines the color coding for the leads on the power cables that attach to the terminal studs on each power supply.

    Note: For the SRX5600 services gateway, the DC power supplies in PEM0 and PEM1 must be powered by dedicated power feeds derived from feed A, and the DC power supplies in PEM2 and PEM3must be powered by dedicated power feeds derived from feed B. This configuration provides the commonly deployed A/B feed redundancy for the system.

  9. Replace the clear plastic cover over the terminal studs on the faceplate.
  10. Route the power cables along the cable restraint towards the left or right corner of the chassis. If needed to hold the power cables in place, thread plastic cable ties, which you must provide, through the openings on the cable restraint.
  11. Verify that the power cabling is correct, that the cables are not touching or blocking access to services gateway components, and that they do not drape where people could trip on them.
  12. Verify that the INPUT OK LED on the power supply is lit green.
  13. Switch the circuit breaker on the power supply to the ON position — and observe the status LEDs on the power supply faceplate. If the power supply is correctly installed and functioning normally, the PWR OK, BRKR ON, and INPUT OK LEDs light green steadily.

    Note: If more than one power supply is being installed, turn on all power supplies at the same time.

Note: An SCB must be present for the PWR OK LED to go on.

Figure 1: Installing a DC Power Supply

Image g004241.gif

Figure 2: Connecting DC Power

Image g004222.gif
 

Related Documentation

  • Preventing Electrostatic Discharge Damage to the SRX5600 Services Gateway
  • Removing an SRX5600 Services Gateway DC Power Supply
  • Replacing an SRX5600 Services Gateway DC Power Supply Cable
 

Published: 2011-03-29

 
  • About Juniper
  • The New Network
  • Investor Relations
  • Press Releases
  • Newsletters
  • Juniper Offices
  • Resources
  • How to Buy
  • Partner Locator
  • Image Library
  • Visio Templates
  • Security Center
  • Community
  • Forums
  • Blogs
  • Junos Central
  • Social Media
  • Support
  • Technical Documentation
  • Knowledge Base (KB)
  • Software Downloads
  • Product Licensing
  • Contact Support
Site Map / RSS Feeds / Careers / Accessibility / Feedback / Privacy & Policy / Legal Notices
Copyright© 1999-2012 Juniper Networks, Inc. All rights reserved.
Help
|
My Account
|
Log Out