Connecting DC Power to the M40e Router
Connect DC power to the router by attaching power cables
from external power sources to the terminal studs on the circuit breaker
box. Power cables are not supplied with the router. For DC power cable
specifications, see M40e DC Power, Connection, and Cable Specifications.
 | Note:
The router must be connected to at least two separate
external DC power sources. |
 | Caution:
You must ensure that power connections maintain the
proper polarity. The power source cables might be labeled (+) and (–) to indicate their polarity. There is no standard
color coding for DC power cables. The color coding used by the external
DC power source at your site determines the color coding for the leads
on the power cables that attach to the terminal studs on the circuit
breaker box. |
To connect DC power to the router (see Figure 1):
- Verify that there is no power flowing from either external power
source, so that the voltage across the leads of the power cables is
0 V. Ensure that there is no chance that the cable leads might
become active during the procedure.
- For each power supply, verify that the power switch
on the circuit breaker box is in the OFF (O) position.
- Using a Phillips screwdriver, loosen and remove the screws securing
the protective shield over the terminal studs on the circuit breaker
box. Remove the cover.
- Install one flat washer and one nut (in that order) on each power
terminal stud:
- If no washers and nuts are already installed, they should
be in the accessory box.
- If two pairs of nuts and washers are installed on the
studs, use a 7/16-in. nut driver or wrench to loosen the outer nut
on each stud. Remove the outer nuts and washers, leaving the inner
nut and washer on each stud.
 | Caution:
The inner washer and nut prevent direct contact between
the power cable lug and the circuit breaker box, which can cause a
short circuit. |
- Slide the power cable lugs onto the terminal
studs. Install another washer and nut (in that order) on each terminal
stud to secure each power cable lug.
- Connect the positive (+) source cable lugs to the return
terminals, which are labeled RTN(+).
- Connect the negative (–) source cable lugs to the
input terminals, which are labeled –48V.
Using a 7/16-in. nut driver or wrench, tighten the nuts.
Apply between 23 lb-in. (2.6 Nm) and 25 lb-in. (2.8 Nm) of torque
to each nut.
- Bend the power cables at a radius appropriate for
the AWG being used and tie them together to ensure that the power
cables do not obstruct any other components. To
identify the minimum bend radius for each type of power cable types,
see published industry standards, such as the National Electrical
Code (NEC) and Insulated Cable Engineers Association (ICEA). Do not
bend a power cable beyond the specified minimum bend radius.
- Verify that the source power cabling and the grounding
cabling are correct, that they are not touching or blocking access
to router components, and that they do not drape where people could
trip on them.
- Replace the protective shield over the terminal
studs and use a Phillips screwdriver to tighten the screws.
- Turn on the current from the power source so that voltage
flows to the router.
Figure 1: Connecting DC Power
Cables
Published: 2010-10-28