Juniper Networks
Log in
|
How to Buy
|
Contact Us
|
United States (Change)
Choose Country
Close

Choose Country

North America

  • United States

Europe

  • Deutschland - Germany
  • España - Spain
  • France
  • Italia - Italy
  • Россия - Russia
  • United Kingdom

Asia Pacific

  • Asean Region (Vietnam, Indonesia, Singapore, Malaysia)
  • Australia
  • 中国 - China
  • India
  • 日本 - Japan
  • 대한민국 - Korea
  • 台灣 - Taiwan
Solutions
Products & Services
Company
Partners
Support
Education
Community
Security Intelligence Center

Technical Documentation

Technical Documentation
 
CLI Explorer New
 
Content Explorer New
 
Documentation Help New
 
Enterprise MIBs
 
EOL Documentation
 
Feature Explorer Login required New
 
Glossary
 
Portable Libraries
 
Home > Support > Technical Documentation > QFX Series > QFX3000-G QFabric System Hardware Documentation > Connecting AC Power to a QFX3008-I Interconnect Device with Three-Phase Wye Wiring Trays
Print
Rate and give feedback:  Feedback Received. Thank You!
Rate and give feedback: 
Close
This document helped resolve my issue.  Yes No

Additional Comments

800 characters remaining

May we contact you if necessary?

Name:  
E-mail: 
Submitting...
 

Related Documentation

  • QFX Series
  • Powering On a QFX3008-I Interconnect Device
  • Wiring Tray in a QFX3008-I Interconnect Device
  • Wiring Tray LEDs on a QFX3008-I Interconnect Device
 

Connecting AC Power to a QFX3008-I Interconnect Device with Three-Phase Wye Wiring Trays

A QFX3008-I Interconnect device is configured with six AC power supplies and two wiring trays.

Caution: Mixing different types of wiring trays in the same chassis is not a supported configuration.

Caution: To meet safety and electromagnetic interference (EMI) requirements and to ensure proper operation, the QFX3008-I Interconnect device must be adequately grounded before it is connected to power.

For installations that require a separate grounding conductor to the chassis, use the protective earthing terminal on the QFX3008-I Interconnect device to connect to earth ground. For instructions on connecting a QFX3008-I Interconnect device to ground using a separate grounding conductor, see Connecting Earth Ground to a QFX3008-I Interconnect Device.

A QFX3008-I Interconnect device receives additional grounding when you plug the power supply in the device into a grounded AC power outlet by using the AC power cord appropriate for your geographical location. See AC Power Cord Specifications for a QFX3008-I Interconnect Device with Three-Phase Wye Wiring Trays.

Note: Each wiring tray must be connected to a dedicated AC power source outlet.

Before you begin to connect power to the device:

  • Ensure that you understand how to prevent ESD damage. See Prevention of Electrostatic Discharge Damage.
  • Ensure that a licensed electrician has prepared the power cords. See Preparing Delta and Wye Three-Phase Power Cords.

Ensure that you have the following parts and tools available to connect power to the device:

  • Electrostatic discharge (ESD) grounding strap
  • Phillips (+) screwdriver, number 1
  • Slotted (–) screwdriver, 1/4 inch, with a torque range between 23 in-lb (2.6 Nm) and 25 in-lb (2.8 Nm)

    Caution: You must use an appropriate torque-controlled tool to tighten the screws on the terminal block. Applying excessive torque damages the terminal block and the wiring tray. The absolute maximum torque that may be applied to this screw is 50 in-lb (5.6 Nm).

Warning: Ensure that the power cords do not block access to device components or drape where people can trip on them.

To connect AC power to three-phase wye wiring trays:

  1. Attach the ESD grounding strap to your bare wrist, and connect the strap to the ESD point on the chassis.
  2. Ensure that the power cords are not connected to power outlets. Switch off the customer site circuit breakers. Ensure that the voltage across the AC power source is 0 V and that there is no chance that the voltage might become active during installation.
  3. If the wiring tray is installed in the chassis, remove it. See Removing a Wiring Tray from a QFX3008-I Interconnect Device. The power cord must be attached to the wiring tray as described in Preparing Delta and Wye Three-Phase Power Cords.
  4. Ensure that the power switch on the wiring tray faceplate is in the OFF (O) position.
  5. Using a number 1 Phillips (+) screwdriver, loosen the four screws on the metal AC wiring compartment on the side of the wiring tray (see Figure 1).
  6. Open the metal door of the wiring tray compartment.
  7. Connect the wires to the AC terminal block on the three-phase wye wiring tray (Figure 1). Use a 1/4-in. slotted screwdriver to loosen the input terminal or grounding point screw, insert each wire into the grounding point or input terminal, and tighten the screw to between 23 in-lb (2.6 Nm) and 25 in-lb (2.8 Nm).

    Caution: You must use an appropriate torque-controlled tool to tighten the screws on the terminal block. Applying excessive torque damages the terminal block and the wiring tray. The absolute maximum torque that may be applied to this screw is 50 in-lb (5.6 Nm).

    1. Insert the wire labeled GND into the grounding point labeled GND.
    2. Insert the wire labeled L1 into the L1 input terminal.
    3. Insert the wire labeled L2 into the L2 input terminal.
    4. Insert the wire labeled L3 into the L3 input terminal.
    5. Insert the wire labeled N into the N input terminal

    Figure 1: Connecting Power to the Three-Phase Wye Wiring Tray

    Connecting
Power to the Three-Phase Wye Wiring Tray

    Note: The color of each AC power wire might vary.

  8. Verify that the power cable connections are correct.
  9. Replace the cover on the wiring compartment, and using a number 1 Phillips (+) screwdriver, tighten the four screws.
  10. Repeat Step 3 through Step 9 for the other wiring tray.
 

Related Documentation

  • QFX Series
  • Powering On a QFX3008-I Interconnect Device
  • Wiring Tray in a QFX3008-I Interconnect Device
  • Wiring Tray LEDs on a QFX3008-I Interconnect Device
 

Published: 2013-01-08

 
  • About Juniper
  • Investor Relations
  • Press Releases
  • Newsletters
  • Juniper Offices
  • Green Networking
  • Resources
  • How to Buy
  • Partner Locator
  • Image Library
  • Visio Templates
  • Security Center
  • Community
  • Forums
  • Blogs
  • Junos Central
  • Social Media
  • Developers
  • Support
  • Technical Documentation
  • Knowledge Base (KB)
  • Software Downloads
  • Product Licensing
  • Contact Support
Site Map / RSS Feeds / Careers / Accessibility / Feedback / Privacy & Policy / Legal Notices
Copyright© 1999-2013 Juniper Networks, Inc. All rights reserved.
Help
|
My Account
|
Log Out