![]() | Note: If you plan to operate a maximally configured DC-powered services gateway, we recommend that you provision 58 A (32 A per feed) @ –48 VDC for the system. |
If you do not plan to provision 58 A (32 A per feed) @ –48 VDC for the system, you can use the information in Table 1 and Table 2 to calculate the power consumption @ –48 VDC, and thermal output for various hardware configurations.
Table 1 lists the power requirements for base DC-powered devices operating under typical voltage conditions.
Table 1: DC-Powered Base System Requirements
DC Power Supply Configuration | Power Requirement (Watts) | Current Requirement (Amps @ –48 VDC) |
|---|---|---|
Nonredundant configuration includes two DC power supplies, midplane, craft interface, and the fan tray (running at normal speed) | 135 W (approximate) | 2.8 A (approximate) |
Redundant configuration includes four DC power supplies, midplane, craft interface, and the fan tray (running at normal speed) | 180 W (approximate) | 3.8 A (approximate) |
Table 2 lists the power requirements for various hardware components when the services gateway is operating under typical voltage conditions.
Table 2: Component Power Requirements
Component | Power Requirement (Watts) | Current Requirement (Amps @ -48 VDC) |
|---|---|---|
Fan tray (full speed) – Fan tray (normal speed) | 110 W – 80 W =30 W | 0.6 A |
SCB | 150 W | 3.1 A |
Routing Engine | 90 W | 1.9 A |
IOC—Generalized typical value | 312 W | 6.5 A |
IOC—Generalized maximum value | 365 W | 7.6 A |
SPC—Generalized typical value | 213 W | 4.4 A |
SPC—Generalized maximum value | 351 W | 7.3 A |
Use the information in Table 1 and Table 2 to calculate power consumption for various hardware configurations, input current from a different source voltage, and thermal output, as shown in the following examples. These examples use generalized values per IOC. Typical power consumption for DC-powered devices: