![]() | Note: If you plan to operate a maximally configured DC-powered services gateway, we recommend that you provision 45 A @ -48 VDC for the system. |
If you do not plan to provision 45 A @ -48 VDC for the system, you can use the information in Table 1 and Table 2 to calculate the power consumption @ -48 VDC, and thermal output for various hardware configurations.
Table 1 lists the power requirements for base DC-powered services gateways operating under typical voltage conditions.
Table 1: DC-Powered Base System Requirements
DC Power Supply Configuration | Power Requirement (Watts) |
|---|---|
Nonredundant configuration includes two DC power supplies, midplane, SFB, Routing Engine, and fan tray | 375 W (approximate) |
Redundant configuration includes four DC power supplies, midplane, SFB, Routing Engine, and fan tray | 430 W (approximate) |
![]() | Note: The power requirement values shown in Table 1 are for a lightly loaded system. For a heavily loaded system, the contribution of the base system to the overall system power requirement is lower, because the power supply efficiency improves as the load increases. For a heavily loaded system, both the redundant and nonredundant base systems contribute approximately 375 W to the overall system power requirement. |
Table 2 lists the power requirements for various hardware components when the services gateway is operating under typical voltage conditions.
Table 2: Component DC Power Requirements
Component | Power Requirement (Watts) | 48V Input Power Requirement at 80% Power Supply Efficiency |
|---|---|---|
Routing Engine | 53 W | 66 W |
SPC | 118 W | 148 W |
NPC | 64 W | 80 W |
SCM | 35 W | 44 W |
IOC (max) | 40 W | 50 W |
IOC (min) | 52 W | 65 W |
Use the information in Table 1 and Table 2 to calculate power consumption for various hardware configurations, input current from a different source voltage, and thermal output, as shown in the following examples. These examples use maximum values per IOC.
Typical power consumption for DC-powered services gateways: