TX Matrix DC Power Requirements
Table 1 lists the system current
requirements for various hardware components when the TX Matrix
router is operating under typical voltage conditions.
Table 1: Component
Power Requirements
Component | System Current Requirement (Amps @ –48 VDC) |
|---|
Base system (includes five TX-SIBs,
one host subsystem, one TX-CIP, two power supplies, cooling system
at normal speed, and craft interface) | 63.0 A |
TX-SIB | 10.0 A |
Host subsystem (Routing Engine
and TX-CB) | 2.6 A |
TX-CIP | 0.1 A |
Two-input power supply or three-input power supply in 2-INPUTmode | 1.7 A |
Cooling system (normal speed) | 6.7 A |
Cooling system (full speed) | 22.0 A |
Craft interface | 0.2 A |
You can use the information in Table 1 to calculate power consumption for various hardware configurations,
input current from a different source voltage, and thermal output,
as shown in the following examples.
- Example of caluclating power consumption for minimum configuration:
Base System =63.0 A @ –48 VDC =3024 W
- Example of caluclating power consumption for maximum configuration:
Base System + 1 Host + (Cooling system:
full speed -normal speed) =63.0 A + 2.6 A + 15.3 A = 80.9 A @ –48 VDC = 3883 W
 | Note:
The power system rating is 4560 W. |
- Current requirement adjustment for fans running at full
speed (high temperature environment or cooling component failure):
Calculated system current (X) – Cooling (normal) + Cooling (full speed) =X A – 6.7 A + 22 A = X A + 15.3 A
- Low line maximum input current for maximum configuration:
Input 0 : 59 A @ –48 VDC
(with fans running at high speed)Input 1 : 36 A @ –48 VDC
- Input current from a DC source other than –48 VDC
(based on maximum configuration):
(–54 VDC input) x (input current X) = (–48 VDC)
x (input current Y)54 x X = 48 x 62 AX = 48 x 62 A/54 = 55 A
- Example of calculating system thermal output:
Watts DC/0.293 = BTU/hr3883 W/0.293 = 13,253 BTU/hr