Juniper Networks
Log in
|
How to Buy
|
Contact Us
|
United States (Change)
Choose Country
Close

Choose Country

North America

  • United States

Europe

  • Deutschland - Germany
  • España - Spain
  • France
  • Italia - Italy
  • Россия - Russia
  • United Kingdom

Asia Pacific

  • Asean Region (Vietnam, Indonesia, Singapore, Malaysia)
  • Australia
  • 中国 - China
  • India
  • 日本 - Japan
  • 대한민국 - Korea
  • 台灣 - Taiwan
Solutions
Products & Services
Company
Partners
Support
Education
Community
Security Intelligence Center

Technical Documentation

Support
Technical Documentation
Content Explorer New
 
Enterprise MIBs
 
EOL Documentation
 
File Format Help
 
Glossary
 
Portable Libraries
 
 
Home > Support > Technical Documentation > T Series Routers > TX Matrix Plus Router Hardware > TX Matrix Plus DC Power Electrical Safety Guidelines
Print
Rate and give feedback:  Feedback Received. Thank You!
Rate and give feedback: 
Close
This document helped resolve my issue.  Yes No

Additional Comments

800 characters remaining

May we contact you if necessary?

Name:  
E-mail: 
Submitting...
 

Related Documentation

  • JCS 1200
  • General Electrical Safety Warnings for Juniper Networks Hardware Equipment
  • DC Power Electrical Safety Warnings for Juniper Networks Hardware Equipment
  • M Series
  • General Electrical Safety Warnings for Juniper Networks Hardware Equipment
  • DC Power Electrical Safety Warnings for Juniper Networks Hardware Equipment
  • MX Series
  • General Electrical Safety Warnings for Juniper Networks Hardware Equipment
  • DC Power Electrical Safety Warnings for Juniper Networks Hardware Equipment
  • T Series
  • Grounding the TX Matrix Plus Router
  • Providing Power to a Seven-Input 420-A Power Supply
  • TX Matrix Plus General Electrical Safety Guidelines
  • General Electrical Safety Warnings for Juniper Networks Hardware Equipment
  • DC Power Electrical Safety Warnings for Juniper Networks Hardware Equipment
 

TX Matrix Plus DC Power Electrical Safety Guidelines

When working with DC-powered equipment, observe the following guidelines:

The following electrical safety guidelines apply to a DC-powered router:

  • A DC-powered router is equipped with a DC terminal block that is rated for the power requirements of a maximally configured router. To supply sufficient power, terminate the DC input wiring on a facility DC source capable of supplying at least 48 A –48 VDC. We recommend that the 48 VDC facility DC source be equipped with a circuit breaker rated at 125% of the power provisioned for the input minimum, or as required by local code. Incorporate an easily accessible disconnect device into the facility wiring. In the United States and Canada, the –48 VDC facility should be equipped with a circuit breaker rated a minimum of 125% of the power provisioned for the input in accordance with the National Electrical Code in the US and the Canadian Electrical Code in Canada. Be sure to connect the ground wire or conduit to a solid office (earth) ground. A closed loop ring is recommended for terminating the ground conductor at the ground stud.
  • Run two wires from the circuit breaker box to a source of 48 VDC. Use appropriate gauge wire to handle up to 60 A @ –48 VDC, or as required by local code.
  • A DC-powered TX Matrix Plus router that is equipped with a DC terminal block is intended only for installation in a restricted access location. In the United States, a restricted access area is one in accordance with Articles 110-16, 110-17, and 110-18 of the National Electrical Code ANSI/NFPA 70.

    Note: Primary overcurrent protection is provided by the building circuit breaker. This breaker should protect against excess currents, short circuits, and earth faults in accordance with NEC ANSI/NFPA70.

  • Ensure that the polarity of the DC input wiring is correct. Under certain conditions, connections with reversed polarity might trip the primary circuit breaker or damage the equipment.
  • For personal safety, connect the green and yellow wire to safety (earth) ground at both the TX Matrix Plus router and the supply side of the DC wiring.
  • The marked input voltage of –48 VDC for a DC-powered TX Matrix Plus router is the nominal voltage associated with the battery circuit, and any higher voltages are only to be associated with float voltages for the charging function.
  • Because the TX Matrix Plus router is a positive ground system, you must connect the positive lead to the terminal labeled RTN, the negative lead to the terminal labeled –48V, and the earth ground to the chassis grounding points.
 

Related Documentation

  • JCS 1200
  • General Electrical Safety Warnings for Juniper Networks Hardware Equipment
  • DC Power Electrical Safety Warnings for Juniper Networks Hardware Equipment
  • M Series
  • General Electrical Safety Warnings for Juniper Networks Hardware Equipment
  • DC Power Electrical Safety Warnings for Juniper Networks Hardware Equipment
  • MX Series
  • General Electrical Safety Warnings for Juniper Networks Hardware Equipment
  • DC Power Electrical Safety Warnings for Juniper Networks Hardware Equipment
  • T Series
  • Grounding the TX Matrix Plus Router
  • Providing Power to a Seven-Input 420-A Power Supply
  • TX Matrix Plus General Electrical Safety Guidelines
  • General Electrical Safety Warnings for Juniper Networks Hardware Equipment
  • DC Power Electrical Safety Warnings for Juniper Networks Hardware Equipment
 

Published: 2011-12-19

 
  • About Juniper
  • The New Network
  • Investor Relations
  • Press Releases
  • Newsletters
  • Juniper Offices
  • Resources
  • How to Buy
  • Partner Locator
  • Image Library
  • Visio Templates
  • Security Center
  • Community
  • Forums
  • Blogs
  • Junos Central
  • Social Media
  • Support
  • Technical Documentation
  • Knowledge Base (KB)
  • Software Downloads
  • Product Licensing
  • Contact Support
Site Map / RSS Feeds / Careers / Accessibility / Feedback / Privacy & Policy / Legal Notices
Copyright© 1999-2012 Juniper Networks, Inc. All rights reserved.
Help
|
My Account
|
Log Out