TX Matrix DC Power Electrical Safety Guidelines
The following electrical safety guidelines apply to a
DC-powered TX Matrix router:
- A DC-powered TX Matrix router is equipped with a
DC terminal block that is rated for the power requirements of a maximally
configured TX Matrix router. To supply sufficient power, terminate
the DC input wiring on a facility DC source capable of supplying at
least 76 A @ –48 VDC. We recommend that the 48 VDC
facility DC source be equipped with a circuit breaker rated at 125%
of the power provisioned for the input minimum, or as required
by local code. Incorporate an easily accessible disconnect device
into the facility wiring. In the United States and Canada, the –48 VDC
facility should be equipped with a circuit breaker rated a minimum
of 125% of the power provisioned for the input in accordance with
the National Electrical Code in the US and the Canadian Electrical
Code in Canada. Be sure to connect the ground wire or conduit to a
solid office (earth) ground. A closed loop ring is recommended for
terminating the ground conductor at the ground stud.
- Run two wires from the circuit breaker box to a source
of 48 VDC. Use appropriate gauge wire to handle up to 100 A.
- A DC-powered TX Matrix router that is equipped with
a DC terminal block is intended only for installation in a restricted
access location. In the United States, a restricted access area is
one in accordance with Articles 110-16, 110-17, and 110-18 of the
National Electrical Code ANSI/NFPA 70.
 | Note:
Primary overcurrent protection is provided by the building
circuit breaker. This breaker should protect against excess currents,
short circuits, and earth faults in accordance with NEC ANSI/NFPA70. |
- Ensure that the polarity of the DC input wiring is correct.
Under certain conditions, connections with reversed polarity might
trip the primary circuit breaker or damage the equipment.
- For personal safety, connect the green and yellow wire
to safety (earth) ground at both the TX Matrix router and the
supply side of the DC wiring.
- The marked input voltage of –48 VDC for a DC-powered
TX Matrix router is the nominal voltage associated with the battery
circuit, and any higher voltages are only to be associated with float
voltages for the charging function.
- Because the TX Matrix router is a positive ground
system, you must connect the positive lead to the terminal labeled RTN, the negative lead to the terminal labeled –48V, and the earth ground to the chassis grounding points.
Published: 2011-12-19