M320 DC Power Electrical Safety Guidelines
The following electrical safety guidelines apply
to an M320 DC-powered router:
- A DC-powered router is equipped with a DC terminal block
that is rated for the power requirements of a maximally configured
router. To supply sufficient power, terminate the DC input wiring
on a facility DC source capable of supplying at least 65 A @ –48 VDC for the system, or at least 48 A @ –48 VDC for each power supply.
We recommend that the 48 VDC facility DC source be equipped with
a circuit breaker rated at 60 A (–48 VDC) minimum,
or as required by local code. Incorporate an easily accessible disconnect
device into the facility wiring. In the United States and Canada,
the –48 VDC facility should be equipped with a circuit breaker
rated a minimum of 125% of the power provisioned for the input in
accordance with the National Electrical Code in the US and the Canadian
Electrical Code in Canada. Be sure to connect the ground wire or conduit
to a solid office (earth) ground. A closed loop ring is recommended
for terminating the ground conductor at the ground stud.
- Run two wires from the circuit breaker box to a source
of 48 VDC. Use appropriate gauge wire to handle up to 60 A.
- A DC-powered router that is equipped with a DC terminal
block is intended only for installation in a restricted access location.
In the United States, a restricted access area is one in accordance
with Articles 110-16, 110-17, and 110-18 of the National Electrical
Code ANSI/NFPA 70.
 | Note:
Primary overcurrent protection is provided by the building
circuit breaker. This breaker should protect against excess currents,
short circuits, and earth faults in accordance with NEC ANSI/NFPA70. |
- Ensure that the polarity of the DC input wiring is correct.
Under certain conditions, connections with reversed polarity might
trip the primary circuit breaker or damage the equipment.
- For personal safety, connect the green and yellow wire
to safety (earth) ground at both the router and the supply side of
the DC wiring.
- The marked input voltage of –48 VDC for a DC-powered
router is the nominal voltage associated with the battery circuit,
and any higher voltages are only to be associated with float voltages
for the charging function.
- Because the router is a positive ground system, you must
connect the positive lead to the terminal labeled RETURN, the negative lead to the terminal labeled –48V,
and the earth ground to the chassis grounding points.
Published: 2011-03-02