Clearance Requirements for Airflow and Hardware Maintenance
of the SRX3600 Services Gateway
When planning the installation site, you need to allow
sufficient clearance around the rack (see Figure 1):
- For the cooling system to function properly, the airflow
around the chassis must be unrestricted. Allow at least 6 in. (15.2
cm) of clearance between services gateways. Allow 5 in. (13 cm) between
the side of the chassis and any non-heat-producing surface such as
a wall.
- For service personnel to remove and install hardware components,
there must be adequate space at the front and back of the services
gateway. At least 24 in. (61 cm) is required both in front of
and behind the services gateway. NEBS GR-63 recommends that you allow
at least 30 in. (76 cm) in front of the rack and 24 in. (61 cm)
behind the rack.
Figure 1: Clearance Requirements
Published: 2011-09-21