Clearance Requirements for Airflow and Hardware Maintenance
for a QFX3100 Director Device
When planning the site for installing a QFX3100 Director device,
you must allow sufficient clearance around the device.
- Allow at least 6 in. (15.2 cm) of clearance
on the side between devices that have fans or blowers installed. Allow
2.8 in. (7 cm) between the side of the chassis and any non-heat-producing
surface such as a wall. For the cooling system to function properly,
the airflow around the chassis must be unrestricted. Figure 1 shows the airflow through
the QFX3100 Director device.
- If you are mounting a QFX3100 Director device on a rack
or cabinet with other equipment, or if you are placing it on the desktop
or floor near other equipment, ensure that the exhaust from other
equipment does not blow into the intake vents of the chassis.
- Leave at least 24 in. (61 cm) both in front
of and behind the QFX3100 Director device. For service personnel to
remove and install hardware components, you must leave adequate space
at the front and back of the QFX3100 Director device. NEBS GR-63 recommends
that you allow at least 30 in. (76.2 cm) in front of the
rack or cabinet and 24 in. (61 cm) behind the rack or cabinet.
Figure 1: Airflow Through the
QFX3100 Director Device