Skip to content

Support



Juniper was the first North American IP routing vendor to achieve the prestigious TL 9000 certification by the Quality of Excellence for Suppliers of Telecommunications (QuEST) Forum in the router category, for design, development, provision and service and support.



What is J-Care?

It's the world-class service and support that you expect from a company that delivers the industry's best infrastructure and security products. With J-Care, you now have the confidence knowing that Juniper will do our part to keep you on top of the world!


Calculating Power Margin for Fiber-Optic Cable for M Series, MX Series, and T Series Routers

After calculating a link's power budget you can calculate the power margin (PM), which represents the amount of power available after subtracting attenuation or link loss (LL) from the power budget (PB). A worst-case estimate of PM assumes maximum LL:

PM = PB – LL

A PM greater than zero indicates that the power budget is sufficient to operate the receiver.

Factors that can cause link loss include higher-order mode losses, modal and chromatic dispersion, connectors, splices, and fiber attenuation. Table 1 lists an estimated amount of loss for the factors used in the following sample calculations. For information about the actual amount of signal loss caused by equipment and other factors, refer to vendor documentation.

Table 1: Estimated Values for Factors Causing Link Loss  

Link-Loss Factor

Estimated Link-Loss Value

Higher-order mode losses

Single-mode—None

Multimode—0.5 dB

Modal and chromatic dispersion

Single-mode—None

Multimode—None, if product of bandwidth and distance is less than 500 MHz–km

Connector

0.5 dB

Splice

0.5 dB

Fiber attenuation

Single-mode—0.5 dB/km

Multimode—1 dB/km

The following example uses the estimated values in Table 1 to calculate link loss (LL) for a 2 km-long multimode link with a power budget (PB) of 13 dB:

  • Fiber attenuation for 2 km @ 1.0 dB/km= 2 dB
  • Loss for five connectors @ 0.5 dB per connector = 5(0.5 dB) = 2.5 dB
  • Loss for two splices @ 0.5 dB per splice =2(0.5 dB) = 1 dB
  • Higher-order loss = 0.5 dB
  • Clock recovery module = 1 dB

The power margin (PM) is calculated as follows:

PM = PB – LL

PM = 13 dB – 2 km (1.0 dB/km) – 5 (0.5 dB) – 2 (0.5 dB) – 0.5 dB [HOL] – 1 dB [CRM]

PM = 13 dB – 2 dB – 2.5 dB – 1 dB – 0.5 dB – 1 dB

PM = 6 dB

The following sample calculation for an 8 km-long single-mode link with a power budget (PB) of 13 dB uses the estimated values from Table 1 to calculate link loss (LL) as the sum of fiber attenuation (8 km @ 0.5 dB/km, or 4 dB) and loss for seven connectors (0.5 dB per connector, or 3.5 dB). The power margin (PM) is calculated as follows:

PM = PB – LL

PM = 13 dB – 8 km (0.5 dB/km) – 7 (0.5 dB)

PM = 13 dB – 4 dB – 3.5 dB

PM = 5.5 dB

In both examples, the calculated power margin is greater than zero, indicating that the link has sufficient power for transmission and does not exceed the maximum receiver input power.


Published: 2009-08-27